The home had a kitchen update somewhere between 1999-2003.
When was it required to have a GFCI at the island? I thought I would show a few pictures of todays inspection. It seems the A/C guys like to tap in the main because there is no additional breaker. I asked the owner why the basement light was taped. He stated it shut off the microwave receptacle. The basement wiring was special. That is a light hanging from the ceiling. This house was a good example of the benifits of a pre listing inspection. As an industry we could all increase are revenue if we increased people knowledge of having an inspection before they sell. I spend at least an extra hour to help with contractor references, getting redy for the buyers inspector. |
|
#2
|
|||
|
|||
|
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#3
|
||||
|
||||
|
Quote:
|
|
#4
|
|||
|
|||
|
Quote:
Additionally, one could recommend installing GFCI's "for enhanced safety" not mentioning the code at all. ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
In the 1996 NEC, the wording was changed to include ALL kitchen counter receptacles, not just those within 6' of the sink.
|
|
#6
|
||||
|
||||
|
Quote:
This is a pre listing home that had the kitchen done between 1999-2003. The electrical was not updated. I include the GFCI chart in all my reports. |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
||||
|
||||
|
Quote:
I have a tiff but I only use when I smell the gas to locate the leak. To miss 13 leaks. Man this seems like I would of smelled something. I have a better nose than eye. Well I guess maybe NOT!! In regard to the kitchen & I just finished my own remodel & I consulted with my electrician to make sure it was all up to code. |
|
#9
|
|||
|
|||
|
Quote:
I always call out GFCI's to the latest standards in use, all of my findings are just RECCOMENDATIONS anyway. Update, don't update, fine with me. Then when I get the call from the seller and they are telling me their "tradesperson" says it is up to code, I ask them to have their "tradesperson" issue their findings in writing and sign them, to the client, like I did. "Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#10
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Kitchen island notwithstanding, all that unprotected branch wiring visible in the pics ought to be called out. Looks like the moisture problems rotted away the nice paneling that used to be covering that up. A little hydrostatic pressure, maybe????
Marc is right, as usual...1996 is the year. BTW, Marc...i'm just curious, really, and mean no offense (particularly since I get lots of good info reading your posts).....did they sometimes call you "Skunk" in HS? |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc,
I really hope I don't get something started. Curiosity got the better of me. I won't mention it again! I enjoy your posts, since I haven't been "in the field" since before my erstwhile career in the teaching profession. Eleven years is a long time, and much has taken place in the sparky world. Though I tried to keep up, I had to actually do some study to pass my ICC exam, and I gain some good insight on this board, and from your posts especially. Thanks for the contributions! Jimmy B. |
|
#13
|
|||
|
|||
|
I also have a lousy sense of smell. I tell everybody that it's because of too much horserasish and prime rib in my misspent youth. Actually, when my allergies start to kick in, I can't smell hardily anything.
Anyway, I use a TIFF gas detector too. It's a quick demo and efficient. Use the tools you need to get the job done. There isn't a home inspector who doesn't have at least 2 or 3 flashlights or outlet testers in their bag of tools. |
|
#14
|
||||
|
||||
|
Tell me if this interpretation is correct. The rule applies to kitchen countertop receptacles. If the island outlet is on the wall of the island, it would not be required to be GFCI protected unless it is also within 6 feet of the sink.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#15
|
||||
|
||||
|
Joe......if the receptacle is serving the island counter space which would be considered counter space then it would still be required to be GFCI if again it is serving the minimum allowed receptacles as defined in 210.52(C)(2) and (3) it is still a counter space in the kitchen...if this receptacle is to serve as lets say the (1) required on a 210.52(C)(2) and (3) then....
Basically.....6' is not the factor...it is a counter top and thus according to 210.8(A)(6) it would need to be GFCI protected. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |