Default Island GFCI requirments

The home had a kitchen update somewhere between 1999-2003.

When was it required to have a GFCI at the island?

I thought I would show a few pictures of todays inspection.

It seems the A/C guys like to tap in the main because there is no additional breaker.

I asked the owner why the basement light was taped. He stated it shut off the microwave receptacle.

The basement wiring was special. That is a light hanging from the ceiling.

This house was a good example of the benifits of a pre listing inspection. As an industry we could all increase are revenue if we increased people knowledge of having an inspection before they sell.

I spend at least an extra hour to help with contractor references, getting redy for the buyers inspector.
Attached Thumbnails
island-gfci-requirments-93207-070-small-.jpg.jpg
Views:	96
Size:	58.7 KB
ID:	9941   island-gfci-requirments-93207-056-small-.jpg.jpg
Views:	87
Size:	43.2 KB
ID:	9942   island-gfci-requirments-93207-057-small-.jpg.jpg
Views:	92
Size:	48.4 KB
ID:	9943  
Reply With Quote
  #2  
Old 3/12/07, 7:51 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Island GFCI requirments

http://www.mikeholt.com/documents/ne...ment_page2.pdf
Reply With Quote
  #3  
Old 3/12/07, 7:54 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Island GFCI requirments

Quote:
Originally Posted by bkelly2
Were on there does it say anything about island receptacles?
Reply With Quote
  #4  
Old 3/12/07, 7:59 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Island GFCI requirments

Quote:
Originally Posted by dmacy
Were on there does it say anything about island receptacles?
The island is in the kitchen, no?

Additionally, one could recommend installing GFCI's "for enhanced safety" not mentioning the code at all.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 3/12/07, 7:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Island GFCI requirments

In the 1996 NEC, the wording was changed to include ALL kitchen counter receptacles, not just those within 6' of the sink.
Reply With Quote
  #6  
Old 3/12/07, 8:03 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Island GFCI requirments

Quote:
Originally Posted by Marc D. Shunk
In the 1996 NEC, the wording was changed to include ALL kitchen counter receptacles, not just those within 6' of the sink.
Thanks Marc.

This is a pre listing home that had the kitchen done between 1999-2003.
The electrical was not updated.

I include the GFCI chart in all my reports.
Reply With Quote
  #7  
Old 3/12/07, 8:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Island GFCI requirments

Quote:
Originally Posted by dmacy
This is a pre listing home that had the kitchen done between 1999-2003.
The electrical was not updated.
It may be a defect from a HI standpoint, but maybe not a violation. I can be years before a jurisdiction legally adopts a certain code revision. You have a good eye, just the same.
Reply With Quote
  #8  
Old 3/12/07, 8:18 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Island GFCI requirments

Quote:
Originally Posted by Marc D. Shunk
It may be a defect from a HI standpoint, but maybe not a violation. I can be years before a jurisdiction legally adopts a certain code revision. You have a good eye, just the same.
I dont know about the good eye. I just had a call back that said they had 13 gas leaks There was no gas odor. It was discovered when the gas company read the meter. They shut it down and said get it fixed.

I have a tiff but I only use when I smell the gas to locate the leak.
To miss 13 leaks. Man this seems like I would of smelled something. I have a better nose than eye. Well I guess maybe NOT!!

In regard to the kitchen & I just finished my own remodel & I consulted with my electrician to make sure it was all up to code.
Reply With Quote
  #9  
Old 3/12/07, 8:21 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Island GFCI requirments

Quote:
Originally Posted by dmacy
Were on there does it say anything about island receptacles?
Where it says KITCHEN.

I always call out GFCI's to the latest standards in use, all of my findings are just RECCOMENDATIONS anyway. Update, don't update, fine with me.

Then when I get the call from the seller and they are telling me their "tradesperson" says it is up to code, I ask them to have their "tradesperson" issue their findings in writing and sign them, to the client, like I did.
Reply With Quote
  #10  
Old 3/13/07, 2:26 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Island GFCI requirments

Kitchen island notwithstanding, all that unprotected branch wiring visible in the pics ought to be called out. Looks like the moisture problems rotted away the nice paneling that used to be covering that up. A little hydrostatic pressure, maybe????

Marc is right, as usual...1996 is the year. BTW, Marc...i'm just curious, really, and mean no offense (particularly since I get lots of good info reading your posts).....did they sometimes call you "Skunk" in HS?
Reply With Quote
  #11  
Old 3/13/07, 5:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Island GFCI requirments

Quote:
Originally Posted by jbreazeale
BTW, Marc...i'm just curious, really, and mean no offense (particularly since I get lots of good info reading your posts).....did they sometimes call you "Skunk" in HS?
No, I went to a private high school, where such nonsense wasn't really a custom. I did hear it quite a bit in grammar school. Some people on this site in particular have taken to calling me Skunk when I rub them the wrong way. The fact that I havn't heard that since grammar school tells a story of its own. It doesn't really bother me, though. When I'm ordering something over the phone, and they ask me to repeat my last name, I often interject, "sort of like skunk, only shunk". My name is reasonably well known locally, as my uncle is the weather guy at a local TV station and my great grandfather was governor of my state.
Reply With Quote
  #12  
Old 3/14/07, 5:48 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Island GFCI requirments

Marc,

I really hope I don't get something started. Curiosity got the better of me. I won't mention it again! I enjoy your posts, since I haven't been "in the field" since before my erstwhile career in the teaching profession. Eleven years is a long time, and much has taken place in the sparky world. Though I tried to keep up, I had to actually do some study to pass my ICC exam, and I gain some good insight on this board, and from your posts especially.

Thanks for the contributions!

Jimmy B.
Reply With Quote
  #13  
Old 3/18/07, 12:25 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Island GFCI requirments

I also have a lousy sense of smell. I tell everybody that it's because of too much horserasish and prime rib in my misspent youth. Actually, when my allergies start to kick in, I can't smell hardily anything.

Anyway, I use a TIFF gas detector too. It's a quick demo and efficient. Use the tools you need to get the job done. There isn't a home inspector who doesn't have at least 2 or 3 flashlights or outlet testers in their bag of tools.
Reply With Quote
  #14  
Old 3/19/07, 9:59 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Island GFCI requirments

Tell me if this interpretation is correct. The rule applies to kitchen countertop receptacles. If the island outlet is on the wall of the island, it would not be required to be GFCI protected unless it is also within 6 feet of the sink.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 3/19/07, 10:30 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Island GFCI requirments

Joe......if the receptacle is serving the island counter space which would be considered counter space then it would still be required to be GFCI if again it is serving the minimum allowed receptacles as defined in 210.52(C)(2) and (3) it is still a counter space in the kitchen...if this receptacle is to serve as lets say the (1) required on a 210.52(C)(2) and (3) then....

Basically.....6' is not the factor...it is a counter top and thus according to 210.8(A)(6) it would need to be GFCI protected.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Looking for BOCA 1996 combustion air requirments jmerritt1 Inspecting HVAC Systems 3 3/6/07 2:40 PM


All times are GMT -4. The time now is 4:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts