  #1  
Old 2/22/07, 2:17 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Isolation

Are the grounds & nuetrals properly isolated in the photo below. They are on seperate parts of the bar but the bar is connected.

This is a Auxilary panel and not the main distribution panel.



Thanks
Attached Thumbnails
isolation-91607-034-small-.jpg.jpg
Views:	110
Size:	70.2 KB
ID:	9373   isolation-91607-035-small-.jpg.jpg
Views:	84
Size:	49.8 KB
ID:	9374  
Reply With Quote
  #2  
Old 2/22/07, 2:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Isolation

Quote:
Originally Posted by dmacy
They are on seperate parts of the bar but the bar is connected.
You answered your own question - NO.

The neutrals must be isolated from the enclosure. The grounds must be bonded to the enclosure.

You cannot meet these requirements if the "bar is connected."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 2/22/07, 2:24 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

Bump
Reply With Quote
  #4  
Old 2/22/07, 2:37 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Isolation

Quote:
Originally Posted by jpope
You answered your own question - NO.

The neutrals must be isolated from the enclosure. The grounds must be bonded to the enclosure.

You cannot meet these requirements if the "bar is connected."
Thanks

I usually know the answer but I like to make sure before I submit the report.

This was a pre list & I want to make sure there is no second guessing on my end.

Thanks Jeff I value you expert opinion.
Reply With Quote
  #5  
Old 2/22/07, 2:49 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Isolation

Reply With Quote
  #6  
Old 2/22/07, 3:01 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Isolation

What is the hazard of bonding the grounds & nuetrals?
Reply With Quote
  #7  
Old 2/22/07, 3:11 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

Q. Given the physical and electrical nature of the connection between those two panels, what is the difference between this and a "split bus" service panel where with the lighting section's bus is fed via a breaker? Is the second panel in this set up considered a "distribution" panel, or part of the service panel?
Reply With Quote
  #8  
Old 2/22/07, 5:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Isolation

Quote:
Originally Posted by dmacy
What is the hazard of bonding the grounds & nuetrals?
A parallel path of current which may energize panel boxes, conduit, etc. etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 2/22/07, 5:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Isolation

Quote:
Originally Posted by mthomas2
Q. Given the physical and electrical nature of the connection between those two panels, what is the difference between this and a "split bus" service panel where with the lighting section's bus is fed via a breaker? Is the second panel in this set up considered a "distribution" panel, or part of the service panel?
The split bus would be considered within, or part of, the service equipment. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 2/22/07, 10:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

The operative language is "Objectionable Current over Grounding Conductors". You don't ever want circuit current flowing in any grounding conductor, including the main bonding jumper.
That means that even if this is the main panel, you don't want white wires on supplimental buses that are screwed directly to the enclosure. Their path to the transformer X0 is through the bonding jumper or green screw
Reply With Quote
  #11  
Old 2/23/07, 9:27 AM
Michael Martin Michael Martin is offline
New User
 
Join Date: May 2005
Location: Cleveland, Ohio
Posts: 24
Please Note: Michael Martin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

Quote:
Originally Posted by Greg Fretwell
The operative language is "Objectionable Current over Grounding Conductors". You don't ever want circuit current flowing in any grounding conductor, including the main bonding jumper.
That means that even if this is the main panel, you don't want white wires on supplimental buses that are screwed directly to the enclosure. Their path to the transformer X0 is through the bonding jumper or green screw
I thought that in a main panel, if you happen to have two bonded grounding/neutral buses, it doesn't matter where the grounded and grounding conductors go (i.e., that you could mix them on the two buses).
Reply With Quote
  #12  
Old 2/23/07, 12:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

If the grounding bus is simply screwed to the can you are sending circuit current through the enclosure. That in not correct.
Reply With Quote
  #13  
Old 2/23/07, 4:11 PM
Michael Martin Michael Martin is offline
New User
 
Join Date: May 2005
Location: Cleveland, Ohio
Posts: 24
Please Note: Michael Martin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

Okay, I'm trying to understand. Assume that there is only one bus in the main panel, and that both grounded and grounding conductors are attached to that bus. Isn't that bus bonded to the enclosure? If so, doesn't that mean that return current, even though it is flowing back through the neutral line to the center tap on the transformer secondary, is also present on the panel? Or rather does the fact that it is flowing back to the tap mean that there is no current on the panel?

Doesn't the green screw bond the bus to the enclosure?
Reply With Quote
  #14  
Old 2/23/07, 4:37 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

Quote:
Originally Posted by Michael Martin
.......
............
Doesn't the green screw bond the bus to the enclosure?
I think maybe you're confusing "main panel" and "sub panel"
Reply With Quote
  #15  
Old 2/24/07, 11:11 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Isolation

The point is you are never supposed to impose circuit current on the enclosure ... period. If this is not part of the neutral bus(s) it should not have white wires on it. The main bonding jumper (green screw) is not listed as a circuit conductor.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wooden Isolation Joints gloughman Exterior Inspections 3 7/12/07 12:47 PM
Sub question about isolation again!! dmacy Electrical Inspections 7 2/4/06 12:03 AM


All times are GMT -4. The time now is 8:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts