Default ITE Panel / Split Main

ITE Split Main Panel



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 4:34 PM..
Reply With Quote
  #2  
Old 1/20/07, 5:14 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

Joseph,

Are my EYE's starting to play tricks on me.......does not look like a split main panel to me......just looks like a normal ITE panel.

Maybe I just can't see it real well.....

As well as the Grounded Conductor not identified.....double taps..and so on....

AH wait...I see the jump loops............NOW I gotcha



Paul W. Abernathy

Last edited by pabernathy; 1/20/07 at 5:29 PM..
Reply With Quote
  #3  
Old 1/20/07, 5:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ITE Panel / Split Main

What I think I see there is a regular ITE main lug panel, which should be a subpanel. It appears to be fed with 3 wire, and the grounds and neutrals are not segregated for the branch circuits. The breaker on the upper left appears to have a loose connection, and has heated up a bit over the years. The panel has problems, but it mostly stems from being improperly wired for use as a subpanel. Like Paul, I don't really see a split buss setup here.
Reply With Quote
  #4  
Old 1/20/07, 5:30 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

Marc.....check out those loops about half way down the left side running down and under......interesting.........would ya say



Paul W. Abernathy
Reply With Quote
  #5  
Old 1/20/07, 5:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

DAMN I just hate pictures.........I would WANT to get my EYES in this one and SNOOP around...lol.......Can't say I have seen one do the jumpers like that before......Joseph can I HAVE this picture......

GUess based on the position of the breaker doing the JUMPING to the lower part of the panel...FROM the bottom no doubt...this could be a main panel.......6 throw rule in effect....based on the location of the breaker "ASSUMED" is doing the jumping so not a Sub-Panel then......interesting



Paul W. Abernathy
Reply With Quote
  #6  
Old 1/20/07, 5:33 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ITE Panel / Split Main

Quote:
Originally Posted by pabernathy
Marc.....check out those loops about half way down the left side running down and under......interesting.........would ya say
Looks like a double tap (probably baseboard heaters, if I was forced to guess) and an improper handle tie on those two single pole breakers that they're terminated to. I don't know enough about ITE brand breakers to know if double taps are okay on them or not. I suspect not.
Reply With Quote
  #7  
Old 1/20/07, 5:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

Yeah Boy...on that second picture a CLASSIC case of corrosion and causing a hot spot on that conductor.......GOOD catch...and a GOOD reason why HI's are looking in the panels......



Paul W. Abernathy
Reply With Quote
  #8  
Old 1/20/07, 5:37 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

Marc,

I am talking about the wires JUST above those double taps...NO they are not allowed in ITE panels.

if you follow the ones on the 3rd set down to the left...they appear to go down and UNDER the bottom of the panelboard itself.....now I would LOVE a shot from below that bottom level of breakers...lol.......ahhhh......wish I could be at every inspection these guys do.....and I am am SUCH a freakin NERD !



Paul W. Abernathy
Reply With Quote
  #9  
Old 1/20/07, 5:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: ITE Panel / Split Main

These going under:
Attached Thumbnails
ite-panel-split-main-panel1small-.jpg.jpg
Views:	143
Size:	59.8 KB
ID:	8535  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 1/20/07, 5:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ITE Panel / Split Main

Ah, yes. I see now. It is, indeed, a split-buss panel. Never knew ITE made those. I see very, very little of that brand in my area.
Reply With Quote
  #11  
Old 1/20/07, 5:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: ITE Panel / Split Main

On the extreme upper right, there appears to be a knockout lodged sideways, with a single white conductor passing through. Not sure what that's all about. Might be a telco ground.
Reply With Quote
  #12  
Old 1/20/07, 5:45 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

Quote:
Originally Posted by lkage
These going under:
lol....ahhh...yep we saw those and corrected it in my original post...lol......read my posts fella....lol......just teasing ya



Paul W. Abernathy
Reply With Quote
  #13  
Old 1/20/07, 5:46 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

lol....I want that corrosion picture.......very nice and the GREEN show up SO nice as well....



Paul W. Abernathy
Reply With Quote
  #14  
Old 1/20/07, 5:48 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: ITE Panel / Split Main

Quote:
Originally Posted by pabernathy
lol....ahhh...yep we saw those and corrected it in my original post...lol......read my posts fella....lol......just teasing ya
Just trying to help Mark out...see his post #6...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #15  
Old 1/20/07, 5:48 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: ITE Panel / Split Main

lol.........well you know us electricians and pictures...lol

I will say however Larry...those are some MIGHTY pretty arrows you got there....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Murray Split Main Panel jhagarty Electrical Inspections 15 2/18/07 3:26 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM