Default ITE Pushmatic neutral/ground busbar

Question(s).... I've noticed on these panels that the lugs are oversized and it appears that they're designed to be this way, with the multiple neutral/grounds bundled under the one lug. Now, is this how these were originally designed? And how much of a concern is it if it was originally designed like this and been o.k. over the years? I realize that the individual terminations on newer panels are a better way, but having these all separated and adding additional bars n such seems to be a bit much, no? Enlighten me, please...

Thanks for any help/insight in advance...
Attached Thumbnails
ite-pushmatic-neutral-ground-busbar-918-s.-lynn-st.-bryan-oh-042.jpg  
Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 11/21/09, 12:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: ITE Pushmatic neutral/ground busbar

That's really the least of your concerns with that panel. This short answer - the terminal lugs are not intended to be used like that.

I'd be way more concerned with the direct tap at the service breaker, among other things. This panel needs professional help



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/21/09, 12:19 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 767
Send a message via AIM to jfrederick
Default Re: ITE Pushmatic neutral/ground busbar

Quote:
Originally Posted by jpope View Post
the terminal lugs are not intended to be used like that.
Thats my point, since there's only a handful there, how else would you do it? or how were they intended to be used, since there so large?

Quote:
Originally Posted by jpope View Post
I'd be way more concerned with the direct tap at the service breaker
Yeah, kinda hard to miss that one
Reply With Quote
  #4  
Old 11/21/09, 2:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: ITE Pushmatic neutral/ground busbar

Those lugs were intended for larger conductors. It's obvious that many circuit have been added over the years, and this was their solution. The flat screws on that terminal bar are for the smaller conductors.

A true professional would have added additional terminal bars to accomodate the conductors, and they probably would have suggested replacing the panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 11/21/09, 3:59 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: ITE Pushmatic neutral/ground busbar

As well as the pushmatic can Have internal rust over time and not work when needed.
Mark





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #6  
Old 11/21/09, 4:39 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 767
Send a message via AIM to jfrederick
Default Re: ITE Pushmatic neutral/ground busbar

Quote:
Originally Posted by mnorthrup View Post
As well as the pushmatic can Have internal rust over time and not work when needed.
Mark
Can't any circuit breaker rust over time (if conditions exist) and not work when needed?

A majority of electricians around here say they're one of the best panels/breakers ever made.
Reply With Quote
  #7  
Old 11/21/09, 4:52 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: ITE Pushmatic neutral/ground busbar

Quote:
Originally Posted by jfrederick View Post
Can't any circuit breaker rust over time (if conditions exist) and not work when needed?

A majority of electricians around here say they're one of the best panels/breakers ever made.
The pushmatics in this area tend not to work over time unless they are tested each month. But we have alot of rain. Other areas may not be as bad. I still see alot of these panels in use and they are good panels.
but with any panel that is as old as these it might be better to upgrade to current applications especialy when they look like the one on this thread.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #8  
Old 11/21/09, 6:39 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: ITE Pushmatic neutral/ground busbar

It seems to be a west coast thing where they are having problems with rust. Never seen any rust in them, just through word of mouth on this MB. I see a lot in the Chicago suburbs. My opinion is that they are a solid panel, just may cost a little more to get the breakers.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pushmatic questions mmerino Electrical Inspections 16 6/12/09 5:44 PM
Neutral/ground bond in subpanel gkeene Electrical Inspections 2 1/23/09 11:14 PM
Neutral/Ground double taps kmalone Electrical Inspections 6 4/24/08 6:26 PM
Pushmatic and service size help cbrands Electrical Inspections 10 9/23/07 10:55 PM


All times are GMT -4. The time now is 11:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts