#1
|
|||
|
|||
|
I inspected the access under a hydromassage/Jacuzzi tub and found that the originally installed bond wire to the pump was cut near the clamp. The bond clamp and cut end of the wire were still attached to the pump.
![]() Any ideas why? Thanks for the help. BTW- This is my first post with photos. How did I do ? Craig Cooper Norwest Inspection Services, Inc. |
|
#2
|
||||
|
||||
|
Was oem or a new pumped? Some guys ripe and tare and get their money and leave, they are like ghost they can move out the door so fast.
Bungalows to Mansions Professional Inspection Services, LLC dba 1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#3
|
||||
|
||||
|
Howdy,
The interesting thing about bonding to the pump is that in many cases this takes place with the plug and cord that powers the pump itself. However, usually in the manual it will state the bonding requirement and if the LUG is present.....then in most cases it will demand it be bonded accordingly. In this case the pump does have a LUG and since the bonding conductor was run chances are it was required to be installed by the manufacturer of the pump or hot tub and should be bonded. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#4
|
||||
|
||||
|
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Don't get the equipment grounding confused with the equipotential bonding. They are two separate systems. You need both.
The green insulated 12ga or larger equipment ground is 680.21(A)(1) The 8ga solid equipotential bond wire is 680.26(B)(4) That can't be a stranded 680.26(C) |
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mike, the only way you don't need a 680.26(B)(4) 8 ga bonding wire to a pump is if it is listed/labelled as a "double insulated pool pump".
The lack of a lug may be a clue but if it isn't clearly labelled as double insulated it isn't. |
|
#7
|
||||
|
||||
|
Sorry greg....thats what I was refering to in regards to the intent of the manufacturer and their requirements. We see ALOT of them with double insulated and I even have seen MANY that say in the manual to NOT connect a seperate bonding conductor to it.....
However 680.43(E)(3) more so in regards to the bonding. Yet many newer models have a plastic outer case and will not provide a bonding point...I dont suggest the electrician FABRICATE one.....IMO We are talking about a indoor spa arn't we.....just checking What I find very interesting is the FPN under 680.26(A)..... FPN: This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode. Basically and correct me if I am wrong greg....the last few we have installed have been on set in hot tubs that have all plastic piping and so on and did not require any bonding beyond the Double Insulated cord to the GFCI protected receptacle. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 1/29/07 at 12:45 PM.. |
|
#8
|
||||
|
||||
|
OK, that sure clears that up.
So, Greg, if I understand that correctly then if I see an empty motor lug but the motor is clearly labeled Double Insulated then I do not need to write it up unless there is metallic piping? Or does, metallic piping have nothing to do with it? Quote:
Last edited by mboyett; 1/29/07 at 12:10 PM.. |
|
#9
|
||||
|
||||
|
Micheal,
The LUG is as greg stated generally to give an even potential to the metal parts around the SPA for a lack of a better description. If the spa is all plastic and their is clearly listed a double insulated plug and motor and no lug it is not needed to be bonded. However the question comes up....WHAT if they replace the motor.....but again if the motor is metal it should be bonded through the plug.....the spa would still have no metal parts....... The bonding in question is not to bring it BACK to the enclosure itself...but to equipotential all metal parts around it....just not sure how many are actually metal anymore.......the metal rings and so on lets say on jets do not require this. Now.....what if copper plumbing piping to the SPA.......the i would want the bond to take place... Edit- I called Metal ..Methal....lol Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 1/29/07 at 12:46 PM.. |
|
#10
|
||||
|
||||
|
Paul, that's exactly my point, thanks. I think HI's should be cautious and not immediately write up an empty motor lug without further investigation. Now, some may say that the further investigation should be the duty of the electrician that was called for. I don't know, I'm conflicted on this one and don't want to needlessly refer out this potential non-issue.
|
|
#11
|
||||
|
||||
|
(E) Methods of Bonding All metal parts associated with the spa or hot tub shall be bonded by any of the following methods: (1) The interconnection of threaded metal piping and fittings (2) Metal-to-metal mounting on a common frame or base (3) The provisions of a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid. Micheal I think it is WISE for the HI to learn what they are looking at when they are making sure it is GFCI protected to also go that extra mile and look for this information. I don't think it is too awful complicated. I know that in the ones we wire we hardly every bring a # 8 AWG to the pumps...probably should but we dont because it seems all the units we are dealing with that are a cord and plug these days ( assuming that mind you ) are double insulated motors and also to the GFCI receptacle . Many also that have a metal case and lug may already have the pre-installed bonding jumper to the piping system prior to shipment but I can't bank on that but it would meet the requirement because the bond is not to provide a fault path...but to supply an equipotential field and reduce voltage gradiants. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#12
|
||||
|
||||
|
Also....figured you probably already have this but figured I would post it again.
http://www.mikeholt.com/files/PDF/Pooldownload.pdf Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#13
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Craig
For your first post with pictures, you did good!!! Keep them coming. |
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
NEC 2005 680.26(C) is going to make this a lot more serious if the AHJs agree it is requiring that the paved surface within 3 feet of a spa is bonded. That would mean if you drop your Sams Wholesale Club packaged spa on a concrete patio you will be chipping up the concrete and adding a 12x12 metal bonding grid, (rebar or copper mesh) same for tile or pavers.
Florida IAEI has the longest thread in IAEI history going on this. It is 10 pages in a BB that normally only gets about 30-40 messages a month. Other things that have to be part of the "8 guage solid" bonding grid include things like screen cages, window frames, ladders, grab bars or anything else metal within 5' of the water up to 12' high. |
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You really have to determine whether this is a hydrotherapy tub or a spa. The rules are different, although I really can't see why.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 4 | 3/25/07 11:41 PM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 2:08 AM |