Default Jacuzzi Bond wire was cut. Why ?

I inspected the access under a hydromassage/Jacuzzi tub and found that the originally installed bond wire to the pump was cut near the clamp. The bond clamp and cut end of the wire were still attached to the pump.

jacuzzi-bond-wire-cut-why-inspection-photos-048.jpg jacuzzi-bond-wire-cut-why-inspection-photos-049.jpg

Any ideas why? Thanks for the help.

BTW- This is my first post with photos. How did I do ?

Craig Cooper
Norwest Inspection Services, Inc.
Reply With Quote
  #2  
Old 1/29/07, 8:00 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Jacuzzi Bond wire was cut. Why ?

Was oem or a new pumped? Some guys ripe and tare and get their money and leave, they are like ghost they can move out the door so fast.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 1/29/07, 10:21 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Jacuzzi Bond wire was cut. Why ?

Howdy,
The interesting thing about bonding to the pump is that in many cases this takes place with the plug and cord that powers the pump itself. However, usually in the manual it will state the bonding requirement and if the LUG is present.....then in most cases it will demand it be bonded accordingly.

In this case the pump does have a LUG and since the bonding conductor was run chances are it was required to be installed by the manufacturer of the pump or hot tub and should be bonded.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 1/29/07, 11:33 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Jacuzzi Bond wire was cut. Why ?

Quote:
Originally Posted by pabernathy
The interesting thing about bonding to the pump is that in many cases this takes place with the plug and cord that powers the pump itself. However, usually in the manual it will state the bonding requirement and if the LUG is present.....then in most cases it will demand it be bonded accordingly.
We've had this discussion before on the board. The last time we did I came to the conclusion that the boding wire was for the benefit of any metallic piping at the tub and not for the pump motor itself. It's already bonded as you stated. In the case shown here I would think the bonding wire is not needed since the visible plumbing is PVC. Is that incorrect?
Reply With Quote
  #5  
Old 1/29/07, 11:46 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Jacuzzi Bond wire was cut. Why ?

Don't get the equipment grounding confused with the equipotential bonding. They are two separate systems. You need both.
The green insulated 12ga or larger equipment ground is 680.21(A)(1)
The 8ga solid equipotential bond wire is 680.26(B)(4) That can't be a stranded 680.26(C)
Reply With Quote
  #6  
Old 1/29/07, 11:53 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Jacuzzi Bond wire was cut. Why ?

Mike, the only way you don't need a 680.26(B)(4) 8 ga bonding wire to a pump is if it is listed/labelled as a "double insulated pool pump".
The lack of a lug may be a clue but if it isn't clearly labelled as double insulated it isn't.
Reply With Quote
  #7  
Old 1/29/07, 11:59 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Jacuzzi Bond wire was cut. Why ?

Sorry greg....thats what I was refering to in regards to the intent of the manufacturer and their requirements. We see ALOT of them with double insulated and I even have seen MANY that say in the manual to NOT connect a seperate bonding conductor to it.....

However 680.43(E)(3) more so in regards to the bonding. Yet many newer models have a plastic outer case and will not provide a bonding point...I dont suggest the electrician FABRICATE one.....IMO

We are talking about a indoor spa arn't we.....just checking

What I find very interesting is the FPN under 680.26(A).....


FPN: This section does not require that the 8 AWG or
larger solid copper bonding conductor be extended or attached
to any remote panelboard, service equipment, or any
electrode.

Basically and correct me if I am wrong greg....the last few we have installed have been on set in hot tubs that have all plastic piping and so on and did not require any bonding beyond the Double Insulated cord to the GFCI protected receptacle.




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 1/29/07 at 12:45 PM..
Reply With Quote
  #8  
Old 1/29/07, 12:05 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Jacuzzi Bond wire was cut. Why ?

OK, that sure clears that up. My point is that, as HI's, we are encouraged to write up every jucuzzi pump motor we see that has an empty bonding lug and yet, I'm still confused as to whether that is the correct thing to do or not.

So, Greg, if I understand that correctly then if I see an empty motor lug but the motor is clearly labeled Double Insulated then I do not need to write it up unless there is metallic piping? Or does, metallic piping have nothing to do with it?

Quote:
The 8ga solid equipotential bond wire is 680.26(B)(4) That can't be a stranded 680.26(C)
Is that what the lug is for?

Last edited by mboyett; 1/29/07 at 12:10 PM..
Reply With Quote
  #9  
Old 1/29/07, 12:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Jacuzzi Bond wire was cut. Why ?

Micheal,

The LUG is as greg stated generally to give an even potential to the metal parts around the SPA for a lack of a better description. If the spa is all plastic and their is clearly listed a double insulated plug and motor and no lug it is not needed to be bonded.

However the question comes up....WHAT if they replace the motor.....but again if the motor is metal it should be bonded through the plug.....the spa would still have no metal parts.......

The bonding in question is not to bring it BACK to the enclosure itself...but to equipotential all metal parts around it....just not sure how many are actually metal anymore.......the metal rings and so on lets say on jets do not require this.

Now.....what if copper plumbing piping to the SPA.......the i would want the bond to take place...

Edit- I called Metal ..Methal....lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 1/29/07 at 12:46 PM..
Reply With Quote
  #10  
Old 1/29/07, 12:31 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Jacuzzi Bond wire was cut. Why ?

Paul, that's exactly my point, thanks. I think HI's should be cautious and not immediately write up an empty motor lug without further investigation. Now, some may say that the further investigation should be the duty of the electrician that was called for. I don't know, I'm conflicted on this one and don't want to needlessly refer out this potential non-issue.
Reply With Quote
  #11  
Old 1/29/07, 12:41 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Jacuzzi Bond wire was cut. Why ?

(E) Methods of Bonding
All metal parts associated with the spa or hot tub shall be bonded by any of the following methods:

(1) The interconnection of threaded metal piping and fittings
(2) Metal-to-metal mounting on a common frame or base
(3) The provisions of a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid.

Micheal I think it is WISE for the HI to learn what they are looking at when they are making sure it is GFCI protected to also go that extra mile and look for this information. I don't think it is too awful complicated.

I know that in the ones we wire we hardly every bring a # 8 AWG to the pumps...probably should but we dont because it seems all the units we are dealing with that are a cord and plug these days ( assuming that mind you ) are double insulated motors and also to the GFCI receptacle .

Many also that have a metal case and lug may already have the pre-installed bonding jumper to the piping system prior to shipment but I can't bank on that but it would meet the requirement because the bond is not to provide a fault path...but to supply an equipotential field and reduce voltage gradiants.




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 1/29/07, 1:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Jacuzzi Bond wire was cut. Why ?

Also....figured you probably already have this but figured I would post it again.

http://www.mikeholt.com/files/PDF/Pooldownload.pdf



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 1/29/07, 5:58 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Jacuzzi Bond wire was cut. Why ?

Craig
For your first post with pictures, you did good!!! Keep them coming.
Reply With Quote
  #14  
Old 1/29/07, 6:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Jacuzzi Bond wire was cut. Why ?

NEC 2005 680.26(C) is going to make this a lot more serious if the AHJs agree it is requiring that the paved surface within 3 feet of a spa is bonded. That would mean if you drop your Sams Wholesale Club packaged spa on a concrete patio you will be chipping up the concrete and adding a 12x12 metal bonding grid, (rebar or copper mesh) same for tile or pavers.
Florida IAEI has the longest thread in IAEI history going on this. It is 10 pages in a BB that normally only gets about 30-40 messages a month.

Other things that have to be part of the "8 guage solid" bonding grid include things like screen cages, window frames, ladders, grab bars or anything else metal within 5' of the water up to 12' high.
Reply With Quote
  #15  
Old 1/29/07, 6:07 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Jacuzzi Bond wire was cut. Why ?

You really have to determine whether this is a hydrotherapy tub or a spa. The rules are different, although I really can't see why.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 2:08 AM


All times are GMT -4. The time now is 8:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts