Sorry if I went off thread guys...i think we answered the original question. The things me and greg are talking about now are different and I have to admit I GAIN from these conversations so humor me please.....always learning myself to gain MORE knowledge on how others view the CODE.
Mike says it best.....Debate the CODE always helps you understand it better... Paul W. Abernathy |
|
#32
|
|||
|
|||
|
In case anyone is lost on what we are speaking about...this may help
![]() Change requires an equipotential bonding grid be installed to reduce voltage gradients in and around permanently installed pools, outdoor spas, and outdoor hot tubs. (B) Bonded Parts. The following parts of a permanently installed pool, outdoor spa, and outdoor hot tub must be bonded to a equipotential bonding grid of the type specified in 680.26(C). Paul W. Abernathy |
|
#33
|
|||
|
|||
|
greg...you are 100% correct.....but should we define a portable outdoor spa as not permanantly installed and would the GRID apply.
I dont think it applies...but the bonding referred to in 680.43(D) would apply. (b) Grid. The equipotential (stray voltage) grid must cover the contour of the permanently installed pool, outdoor spa, or outdoor hot tub, and deck extending 3 ft horizontally from the water. The equipotential (stray voltage) grid must be arranged in a 1 ft x 1 ft network of conductors in a uniformly spaced perpendicular grid pattern with a tolerance of 4 in. Paul W. Abernathy Last edited by pabernathy; 1/30/07 at 1:38 PM.. |
|
#34
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Be careful lifting rules from one article and trying to apply them somewhere else. 680.43 is "indoor"
|
|
#35
|
|||
|
|||
|
while part 1 and part 2 applies to all within the article, I think we are jumping back and forth from outside units to inside units....I was refering to the one in question but I think we agree on the outdoor units if permenantly installed...
I will continue this on the new thread as to avoid the jacking... Paul W. Abernathy |
|
#36
|
|||
|
|||
|
Craig,
Here is also come good info.... CMP-17 statement, Proposal 17-183 in the ROP leading to the 2005 NEC: Panel Statement: The need for bonding in a bathroom differs from the need for bonding in a pool area. Electrical equipment of a hydromassage bathtub is not accessible to users of the tub. Only parts that can cause a voltage gradient in the bathtub need to be bonded. Section 680.74 has been concisely reworded to require the bonding of only the parts that present a risk of creating voltage gradients in the hydromassage bathtub. Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 1:08 AM |