Would it be acceptable safe practice to join a Cu branch circuit to an Al branch at a receptacle, if you used a different receptacle screw for each wire??
John Kogel www.allsafehome.ca |
|
#2
|
|||
|
|||
|
Is this something you have come across during an inspection or something you are thinking of doing this. Alum has to have special devise's dedicated for the use with Alum wire some areas allow the pig-tailing of Cop to Alum at the outlet using approved wire nuts. If the outlet is rated for Alum wire then you could apply the copper to the outlet directly to the screw
|
|
#3
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
I don't remove cover plates so no, this is not something I've found but want an answer ready for Mr. Handy. Thanks for that.
|
|
#4
|
||||
|
||||
|
When deciding to repair or replace any electrical installation, a qualified professional should be consulted.
I'd advise removing a random number of coverplates to examine how or what connections or alterations have been made and the type of receptacles present just to improve your reporting and discussion with clients. jmo Others will advise the opposite leaning on the SOP, oh well... Upgrading aluminum-wired homes There are several "upgrades" that are commonly done to homes with pre-1974 aluminum branch circuit wiring:
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 9/17/08 at 10:51 PM.. |
|
#5
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
As far as removing a cover or two, I think we saw a case recently where pulling the receptacle out for inspection resulted in a dead short and a bit of a fire. The other factor is a couple of random, easy access outlets are inspected, they are good, now we might make a false assumption that all other outlets are similar. You still need to call for an inspection of the rest of the outlets, because you can never be sure. (I just found 2 outlets in my 30yr old living room that were never grounded, no grounding lead was ever attached.) |
|
#6
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Useally no it is not most case due the standard crimping barrel useally is either brass or steel once a while copper too also. The copalum connectors are diffrent beast they are stragiht alum connector and used specal criming device to used this item. There are few other approved items that can be used as well. Merci,Marc |
|
#7
|
||||
|
||||
|
Quote:
Merci to you also, Marc ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#8
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Fair enough.
So is it OK to use the receptacle screws to join a new Cu branch to an existing Al branch? |
|
#9
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Actually, if you're using an AL/CU rated receptacle, you can terminate AL conductors on one set of screws and CU conductors on another set of screws, and you're fine. That's a perfectly acceptable method for a conductor material change, such as a copper extension from an aluminum wired circuit. I can't say that I've ever had to do that, but it's 100% legal and safe. I will add, however, that's it's not a good idea to add any additional load to an existing aluminum wired circuit if you can do it some other way.
|
|
#10
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks Marc. And good point about keeping the load reasonable.
|
|
#11
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
And thanks Terry, I just had to hear it agin.
|
|
#12
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Look for CO/ALR rules in the NEC for devices and receptacles.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| What's This Receptacle For? | cmettel | Electrical Inspections | 7 | 5/25/07 8:35 AM |
| Panel Cover Screws | mhawley | Electrical Inspections | 17 | 4/24/07 5:23 PM |
| Online Code Check- Reference | pabernathy | Electrical Inspections | 31 | 11/9/06 4:39 PM |
| New Directors...Please join me in Congartulating Them! | hgordon | Miscellaneous Discussion for Inspectors | 0 | 3/7/06 1:02 AM |