Default Join Cu to Al at the receptacle screws?

Would it be acceptable safe practice to join a Cu branch circuit to an Al branch at a receptacle, if you used a different receptacle screw for each wire??

John Kogel
www.allsafehome.ca
Reply With Quote
  #2  
Old 9/17/08, 9:50 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 244
Default Re: Join Cu to Al at the receptacle screws?

Is this something you have come across during an inspection or something you are thinking of doing this. Alum has to have special devise's dedicated for the use with Alum wire some areas allow the pig-tailing of Cop to Alum at the outlet using approved wire nuts. If the outlet is rated for Alum wire then you could apply the copper to the outlet directly to the screw
Reply With Quote
  #3  
Old 9/17/08, 10:37 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

I don't remove cover plates so no, this is not something I've found but want an answer ready for Mr. Handy. Thanks for that.
Reply With Quote
  #4  
Old 9/17/08, 10:42 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Join Cu to Al at the receptacle screws?

When deciding to repair or replace any electrical installation, a qualified professional should be consulted.

I'd advise removing a random number of coverplates to examine how or what connections or alterations have been made and the type of receptacles present just to improve your reporting and discussion with clients. jmo Others will advise the opposite leaning on the SOP, oh well...

Upgrading aluminum-wired homes



There are several "upgrades" that are commonly done to homes with pre-1974 aluminum branch circuit wiring:
  • Ensuring that all devices are rated for use with aluminum wire. Many are not, since they do not meet the CO/ALR specification.
  • "Pigtailing", which involves splicing a short length of copper to the original aluminum wire for use with devices not CO/ALR rated.
  • COPALUM, a sophisticated crimping system that creates a cold weld between copper and aluminum wire, and is regarded to be a permanent, maintenance-free repair. These connections are sometimes too large to be installed in existing enclosures. Surface enclosures or larger enclosures may be installed to remedy this problem.
  • Alumiconn http://kinginnovation.com/products/alumiconn.html
  • Completely rewiring the house with copper instead.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/17/08 at 10:51 PM..
Reply With Quote
  #5  
Old 9/18/08, 4:32 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

Quote:
Originally Posted by badair View Post
When deciding to repair or replace any electrical installation, a qualified professional should be consulted.

I'd advise removing a random number of coverplates to examine how or what connections or alterations have been made and the type of receptacles present just to improve your reporting and discussion with clients. jmo Others will advise the opposite leaning on the SOP, oh well...

Upgrading aluminum-wired homes



There are several "upgrades" that are commonly done to homes with pre-1974 aluminum branch circuit wiring:
  • Ensuring that all devices are rated for use with aluminum wire. Many are not, since they do not meet the CO/ALR specification.
  • "Pigtailing", which involves splicing a short length of copper to the original aluminum wire for use with devices not CO/ALR rated.
  • COPALUM, a sophisticated crimping system that creates a cold weld between copper and aluminum wire, and is regarded to be a permanent, maintenance-free repair. These connections are sometimes too large to be installed in existing enclosures. Surface enclosures or larger enclosures may be installed to remedy this problem.
  • Alumiconn http://kinginnovation.com/products/alumiconn.html
  • Completely rewiring the house with copper instead.
Thanks Barry. Isn't crimping and using Copalum connectors the same thing?

As far as removing a cover or two, I think we saw a case recently where pulling the receptacle out for inspection resulted in a dead short and a bit of a fire. Oops.
The other factor is a couple of random, easy access outlets are inspected, they are good, now we might make a false assumption that all other outlets are similar. You still need to call for an inspection of the rest of the outlets, because you can never be sure. (I just found 2 outlets in my 30yr old living room that were never grounded, no grounding lead was ever attached.)
Reply With Quote
  #6  
Old 9/18/08, 7:34 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

Quote:
Originally Posted by jkogel View Post
Thanks Barry. Isn't crimping and using Copalum connectors the same thing?

Useally no it is not most case due the standard crimping barrel useally is either brass or steel once a while copper too also.

The copalum connectors are diffrent beast they are stragiht alum connector and used specal criming device to used this item.

There are few other approved items that can be used as well.

Merci,Marc
Reply With Quote
  #7  
Old 9/18/08, 9:08 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Join Cu to Al at the receptacle screws?

Quote:
Originally Posted by jkogel View Post
Thanks Barry. Isn't crimping and using Copalum connectors the same thing?

As far as removing a cover or two, I think we saw a case recently where pulling the receptacle out for inspection resulted in a dead short and a bit of a fire. Oops. I guess I'm from a different school. Better for me to find during the inspection then after closing from their attorney.
The other factor is a couple of random, easy access outlets are inspected, they are good, now we might make a false assumption that all other outlets are similar. My report verbiage covers this as well as my onsite communication with clients. You still need to call for an inspection of the rest of the outlets, switches and secured fixtures, because you can never be sure. Absolutely! (I just found 2 outlets in my 30yr old living room that were never grounded, no grounding lead was ever attached.)
hth you understand my methodology beside it's required in Texas that the inspector remove a random number of coverplates...ba-da-bing-ba-da-boom! Never have gotten an answer as to how many is in a "random'

Merci to you also, Marc



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #8  
Old 9/18/08, 9:48 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

Fair enough.

So is it OK to use the receptacle screws to join a new Cu branch to an existing Al branch?
Reply With Quote
  #9  
Old 9/18/08, 10:12 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

Actually, if you're using an AL/CU rated receptacle, you can terminate AL conductors on one set of screws and CU conductors on another set of screws, and you're fine. That's a perfectly acceptable method for a conductor material change, such as a copper extension from an aluminum wired circuit. I can't say that I've ever had to do that, but it's 100% legal and safe. I will add, however, that's it's not a good idea to add any additional load to an existing aluminum wired circuit if you can do it some other way.
Reply With Quote
  #10  
Old 9/18/08, 10:24 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

Thanks Marc. And good point about keeping the load reasonable.
Reply With Quote
  #11  
Old 9/18/08, 10:40 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

And thanks Terry, I just had to hear it agin.
Reply With Quote
  #12  
Old 9/19/08, 4:22 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Join Cu to Al at the receptacle screws?

Look for CO/ALR rules in the NEC for devices and receptacles.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
What's This Receptacle For? cmettel Electrical Inspections 7 5/25/07 8:35 AM
Panel Cover Screws mhawley Electrical Inspections 17 4/24/07 5:23 PM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 4:39 PM
New Directors...Please join me in Congartulating Them! hgordon Miscellaneous Discussion for Inspectors 0 3/7/06 1:02 AM


All times are GMT -4. The time now is 2:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts