The local bldg. inspector wants a jumper wire installed across the water meter. Apparently he does not realize that all the water pipes are plastic. (it is a double-wide home) What is the solution?
Geo |
|
#2
|
||||
|
||||
|
Ground rod
|
|
#3
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
The solution is to point out to the inspector that the piping is plastic. If he still insists on a jumper, then call his supervisor and explain it to him.
This is of course, if you are not trolling us. |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
When all the piping is plastic, you install the jumper with 1/4" polyethylene tubing for a 200 amp service, and monofilament fishing line for a 100 amp service.
|
|
#5
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#6
|
|||
|
|||
|
The plumbing main service entrance(if metal) is the main grounding electrode. That HAS to be grounded, bonding around the meter is required if the "system" is of a conductive metal. This tends to be a very touchy subject in different jurisdictions. Some electrical inspectors require bonding around the meter if there is even ten feet of copper pipe after the meter. If you want to know what the national electrical code says about it, check article 250(article 250 is very long but its in the first third of it, ill look up the exact article later).
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Neutral bus bar failed inspection | Greg Moritz | Electrical Inspections | 18 | 1/19/08 1:53 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |