  #1  
Old 4/12/07, 8:45 PM
Kenneth E. Sitzes's Avatar
Kenneth E. Sitzes Kenneth E. Sitzes is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Waterloo, Il
Posts: 423
Send a message via Skype™ to ksitzes
Default Junction box

The house I inspected to had a sub panel under the kitchen sink. When I open it was junction box. Is there a height requirement on junction boxes?

jse_DSC02133.jpg
Attached Thumbnails
junction-box-jse_dsc02133.jpg  



Kenneth Sitzes
NACHI #04122492
Eagle Inspection of Illinois
618-830-8283
Waterloo, Illinois 62298
ghinspector@yahoo.com
InterNACHI State of Illinois Continuing Education Administrator
Reply With Quote
  #2  
Old 4/12/07, 8:50 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

No height requirement on junction boxes. They are only required to be accessible. The definition of accessible in the code does not include words like "easy" or "fun". There are a couple of apparent violations in that picture, such as the 2" connector is not okayed for 12 romexes, the cable do not appear to be fastened within 12" of the box, and the box does not appear to be bonded with the largest equipment grounding conductor that enters the box. The equipment grounding conductors only appear to be twisted, with no mechanical splicing means.
Reply With Quote
  #3  
Old 4/12/07, 8:52 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Junction box

Quote:
Originally Posted by ksitzes
Is there a height requirement on junction boxes?
Just so it's accessible.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 4/12/07, 10:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

You could point out the missing KO seals and the sloppy way the Romex is coming in the box. (not stapled within 12", the big "cludge" in one connector etc).
Reply With Quote
  #5  
Old 4/12/07, 10:42 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

That is pretty common with the old fuse boxes. Most of the time the electricains just removed the bars, spliced the wires and closed up the old box.
Reply With Quote
  #6  
Old 4/13/07, 8:45 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: Junction box

Old service equipment (from the picture) under a kitchen sink, now used as a junction box.

My first question. Why the heck did they put a panel under the kitchen sink?


"Oh, I just had an old panel around and didn't feel like running down to Home Depot and paying $3 for new junction box, so I used the old one.

Under a kitchen sink is a "wet location". If anyone disagrees, I would suggest that you spend some time down there.

I guess that it is just a matter of how much danger the client wants to accept.

"Gee, Mom. I just went to put something under the sink, but I got shocked."

Question? Did the panel have a dead front or was it just open?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #7  
Old 4/13/07, 10:18 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

Quote:
Originally Posted by wdecker
Under a kitchen sink is a "wet location". If anyone disagrees, I would suggest that you spend some time down there.
That's screwball talk. Under the kitchen sink is not a wet location. If it's wet under there, it's a leaky location. Have the leak repaired.
Reply With Quote
  #8  
Old 4/14/07, 1:15 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: Junction box

Quote:
Originally Posted by Marc D. Shunk
That's screwball talk. Under the kitchen sink is not a wet location. If it's wet under there, it's a leaky location. Have the leak repaired.
With all due respect, how many kitchen faucets have you changed out?

How many P traps have you changed? How many grease clogs have you rodded? How many dishwasher drains have you replaced? How many backsplashes have you caulked?

You just do electric. How many panels (which is what this is, even though it is only being used as a "junction box") have you found under a kitchen sink?

Under the kitchen sink is a wet location.

Trust me.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 4/14/07, 2:12 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

By your definition any receptacle near a window is a wet location.
Reply With Quote
  #10  
Old 4/14/07, 9:52 AM
jvogan's Avatar
jvogan jvogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: Junction box

I agree with William. Doesn't seem to be the safest location for an electrical junction box. Sometimes, sooner or later, most sinks will leak. I wouldn't want my child messing around under there, and I would certainly call it out for any client paying me to inspect their home, regardless of what code says. Marc, what is the difference between a "wet" location and a "leaky" location. Under "redundant" in the dictionary is says "see redundant"!
Reply With Quote
  #11  
Old 4/14/07, 12:02 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

It may be a poor choice but that is a design problem, not a "wet location" problem.
Reply With Quote
  #12  
Old 4/14/07, 1:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

It's a dumb location for a junction box, but certainly not a prohibited location.
Reply With Quote
  #13  
Old 4/14/07, 2:57 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: Junction box

Quote:
Originally Posted by Marc D. Shunk
It's a dumb location for a junction box, but certainly not a prohibited location.
Again, we have to note a big difference. Home Inspectors are not Code inspectors.

Electricians only have to follow code.

Home Inspectors have a much greater liability. We have to inspect to standards of common sense. If somecan get hurt, they probably will get hurt, and then they will sue us.

Electricians can just point to "code" and they get off the hook.

Different job, different standards, different liability.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #14  
Old 4/14/07, 3:09 PM
jvogan's Avatar
jvogan jvogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: Junction box

I would simply call it out as a safety concern, and recommend moving the box, regardless of what "code" had to say. Too many bad things can happen (ie. children getting into the box, water, etc.). That covers me and the homeowner is made aware of the concern. Then the monkey is on their back to fix it or not.
Reply With Quote
  #15  
Old 4/14/07, 3:14 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Junction box

Quote:
Originally Posted by wdecker
Different job, different standards, different liability.
Yeah, it would be nice for you guys if you had an SOP that had the rule of law. It makes me wonder why anyone would want to be a home inspector? Is there any money in it? I don't think I've ever seen any palacial homes occupied by home inspectors. I guess it's a calling?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Unsecured Junction box to Furnace lsheehy Electrical Inspections 4 4/20/07 10:02 AM
Wires and Junction at tub mlong Electrical Inspections 8 11/18/06 1:29 PM
Overloaded Junction Boxes and Fill pbennett1 Electrical Inspections 6 11/6/06 5:13 PM
Service Panel Used As Junction Box mbazzo Electrical Inspections 20 8/12/06 1:09 PM


All times are GMT -4. The time now is 3:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts