Default Just use a jumper

to energize the other side of the sub panel..
Attached Thumbnails
just-use-jumper-138-127.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/20/12, 9:38 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Just use a jumper

Curious and seriously... did you call out that missing knockout?
Reply With Quote
  #3  
Old 1/20/12, 9:48 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Just use a jumper

Quote:
Originally Posted by jjonas View Post
Curious and seriously... did you call out that missing knockout?
Yes along with the rest of the panel as well.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 1/20/12, 9:55 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Just use a jumper

Quote:
Originally Posted by sfogarty View Post
Yes along with the rest of the panel as well.
Thank you. I always wondered if others do as well, irregardless of the other issues.
Reply With Quote
  #5  
Old 1/20/12, 10:42 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Just use a jumper

Is the pic sideways or is that the way it was mounted?

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #6  
Old 1/21/12, 8:10 AM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: Just use a jumper

Is that lamp wire coming out of the bottom left breaker?



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
  #7  
Old 1/21/12, 11:13 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Just use a jumper

It does look a lot like lamp or zip cord.
Reply With Quote
  #8  
Old 1/21/12, 12:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Just use a jumper

I see this crap all too often, and usually recommend removal or replacement in lieu of "corrections."

It's apparently being back-fed by a single-pole breaker, and the jumper is being used to supply power to (what should be ) the opposite leg of 120V. In addition, it appears to be a sub panel, in which case the neutrals should be isolated from the enclosure. This is most certainly a "home owner" installation.

I always call out missing KO's.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 1/21/12, 2:18 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Just use a jumper

Quote:
Originally Posted by jpope View Post

I always call out missing KO's.
As do I, but this one would be for a different reason that the typical missing knockout, would it not?
Reply With Quote
  #10  
Old 1/21/12, 3:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Just use a jumper

Quote:
Originally Posted by jjonas View Post
As do I, but this one would be for a different reason that the typical missing knockout, would it not?
I'm not sure I understand what you mean. The missing KO is insignificant compared to the rest of the issues, if that's where you're going...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 1/21/12, 4:19 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Just use a jumper

Quote:
Originally Posted by jpope View Post
I'm not sure I understand what you mean. The missing KO is insignificant compared to the rest of the issues, if that's where you're going...
The fact that the missing knock out was against wood also will prevent entry of forgien debris and animals. Like you said the knockout is the minimal.

The whole garage was wired by the previous owner and it showed.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #12  
Old 1/21/12, 6:04 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Just use a jumper

Quote:
Originally Posted by sfogarty View Post
The fact that the missing knock out was against wood also will prevent entry of forgien debris and animals. Like you said the knockout is the minimal.

The whole garage was wired by the previous owner and it showed.
Exactly, and I agree it is a lesser issue, but it is still an issue.
Reply With Quote
  #13  
Old 1/21/12, 7:25 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Just use a jumper

Quote:
Originally Posted by jjonas View Post
Exactly, and I agree it is a lesser issue, but it is still an issue.
Sadly unless I can find nothing else to gripe about the knock outs usually go undocumented. Many times the panels with missing knock outs have far more issues to focus on.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/22/12, 2:59 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Just use a jumper

Although the wood does keep stuff out of the KO it doesn't satisfy the NEC requirement where the seal has to be a material equivalent to the enclosure.

Quote:
110.12 Mechanical Execution of Work.
Electrical equipment shall be installed in a neat and workmanlike manner.
FPN: Accepted industry practices are described in ANSI/NECA 1-2006, Standard Practices for Good Workmanship in Electrical Contracting, and other ANSI-approved installation standards.
(A) Unused Openings. Unused openings, other than those intended for the operation of equipment, those intended for mounting purposes, or those permitted as part of the design for listed equipment, shall be closed to afford protection substantially equivalent to the wall of the equipment. Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6 mm (¼ in.) from the outer surface of the enclosure.
Reply With Quote
  #15  
Old 1/22/12, 3:19 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Just use a jumper

Exposed wood can catch on fire. The purpose of the enclosure is to contain the fire.

I would call out a missing ko quicker than I would two neutrals under one screw.



Mike Whitt
Contractor/Instructor
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Spanish version of Grounding Jumper added to Inspection Graphics Library. gromicko General Inspection Discussion 0 9/18/11 11:45 PM
Bonding Jumper Size??? bsmith Electrical Inspections 3 10/28/09 12:19 PM
jumper wire gmartin2 Electrical Inspections 5 1/23/09 12:45 AM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM


All times are GMT -4. The time now is 8:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts