Default K & T and GFCI

Yesterdays house is mostly K & T, it is a 2 family, and the owner just recently installed GFCI outlets in several rooms.

When testing the device with the buttons, it tests properly, when using a tester, it obviousally shows no ground and will not test. I remember reading back at some point that a 2-prong system can have a GFCI and be wired to operate properly and will not trip if a tester is used. That appears to be the case here.

What I am trying to figure out is, if a normal 2-prong system has a 3-prong device installed without grounding it would be considered defective. Why would it not be the same case with a GFCI?

The owner (seller) indicated it was his understanding that in using the GFCI device (again which does properly test by the devices buttons) satisfied the code for a 3-prong non-grounded system.

Input please.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 1/6/08, 7:10 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: K & T and GFCI

Quote:
Originally Posted by sfalvey
What I am trying to figure out is, if a normal 2-prong system has a 3-prong device installed without grounding it would be considered defective. Why would it not be the same case with a GFCI?


Input please.
The GFCI receptacle should be labeled no equipment ground. The three prong receptacle should be labeled GFCI protected and no equipment ground.

An ungrounded Outlet.When three prong receptacles with open grounds are identified and a two-wire system is present, the NEC® currently allows the following methods to be used to resolve the problem:
  • Install an equipment ground. (recommended for high end equipment)
  • Provide GFCI protection for the receptacle (either at the receptacle or upstream of the receptacle) the receptacles are to be marked “no equipment ground”. This method does not provide an equipment ground.
  • Replace the existing three-hole receptacle with a two-hole non-grounded receptacle.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER

Last edited by lkage; 1/6/08 at 9:10 PM..
Reply With Quote
  #3  
Old 1/6/08, 3:39 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T and GFCI

Filling the ground holes with a hot glue gun or similar method is recogizied up here as an acceptable method.
Reply With Quote
  #4  
Old 1/6/08, 3:50 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: K & T and GFCI

One thing I mention to my clients is that when using GFCI's without a ground conductor, a surge protector will no longer offer much surge protection.

A surge protector sinks the majority of the surge to the ground conductor. So I alway recommend computer equipment to be grounded.

Also, do not use a GFCI on a refrigerator or freezer because they tend to trip the day after you leave on a two-week vacation.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
More GFCI info from U/L Greg Fretwell Electrical 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 6:13 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts