Default K & T still in use- Hey Guru's !!!

These pics are from todays inspection. House built in 1921. Several additions and remodels later, the Knob and Tube is still in use in the attic. Not sure who did thier electrical work but someone should smack the sh*t out of him! There are open boxes, splices, wire running wild everywhere.

I do have a question though. I seem to recall that live K&T should NOT be buried with insulation. Is this a true statement? Thanks for your help fellas, Rick
Attached Thumbnails
k-and-t-still-use-hey-gurus-img_0056.jpg   k-and-t-still-use-hey-gurus-img_0057.jpg   k-and-t-still-use-hey-gurus-img_0058.jpg   k-and-t-still-use-hey-gurus-img_0060.jpg   k-and-t-still-use-hey-gurus-img_0062.jpg  




Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #2  
Old 8/11/07, 7:32 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: K & T still in use- Hey Guru's !!!

Quote:
Originally Posted by rslocum
I do have a question though. I seem to recall that live K&T should NOT be buried with insulation. Is this a true statement? Thanks for your help fellas, Rick
Correct K&T is designed to operate in free air

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 8/11/07, 7:36 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 230
Default Re: K & T still in use- Hey Guru's !!!

Thanks Gerry !



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #4  
Old 8/11/07, 7:37 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

Yup, what Gerry said.
And if anyone extended that K&T they definitely should be smacked.
Reply With Quote
  #5  
Old 8/11/07, 7:37 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: K & T still in use- Hey Guru's !!!

Quote:
Originally Posted by rslocum
These pics are from todays inspection. House built in 1921. Several additions and remodels later, the Knob and Tube is still in use in the attic. Not sure who did thier electrical work but someone should smack the sh*t out of him! There are open boxes, splices, wire running wild everywhere.

I do have a question though. I seem to recall that live K&T should NOT be buried with insulation. Is this a true statement? Thanks for your help fellas, Rick
Remember write hard talk soft miss nothing .
I write on every one of my reports to please check with your insurance company re Home insurance.
If they ask I remind them that many companies no longer will give insurance in our area for Knob and tube and also Fuse panels.

......... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 8/11/07, 7:41 PM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 230
Default Re: K & T still in use- Hey Guru's !!!

Thanks Speedy, hell they extended it, spliced into it all over the place up there.

Good advice Roy, thanks !



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #7  
Old 8/12/07, 9:56 AM
mporras mporras is offline
Active Poster
 
Join Date: Mar 2005
Location: Edmond, OK
Posts: 183
Please Note: mporras is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

I inspected a home recently, that had been beautifully remodeled, new paint, wallboard, fixtures, flooring, etc. I got into the attic, and saw a large amount of the very same electrical defects in the attic. Horrible. It was not a question of "if" the house would burn, but when! "Flip this house" my ***!
Reply With Quote
  #8  
Old 8/12/07, 1:25 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

Unfortunately this is a VERY common mentality Mike. This is the same mentality of electricians who do sloppy rough-ins.
Out of sight, out of mind.
Reply With Quote
  #9  
Old 8/13/07, 12:40 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

Quote:
Originally Posted by rslocum
These pics are from todays inspection. House built in 1921. Several additions and remodels later, the Knob and Tube is still in use in the attic. Not sure who did thier electrical work but someone should smack the sh*t out of him! There are open boxes, splices, wire running wild everywhere.

I do have a question though. I seem to recall that live K&T should NOT be buried with insulation. Is this a true statement? Thanks for your help fellas, Rick
Off topic but may be an item:

Most of the insulation in the background appears to be vermiculite. In my area, 90%+ of vermiculite here contains 1-5% asbestos. It came from the Libby, Montana mine.

Some people do not want to purchase a home with a potential environmental concern at a future re-sale and have walked from houses with this brand of vermiculite or it was removed as part of sale conditions($3,500 - $5,000+). Recently I had an electrician/trade school instructor with training about asbestos simply show no concern and buy the house.
Reply With Quote
  #10  
Old 8/17/07, 4:47 PM
dcook1's Avatar
dcook1 dcook1 is offline
Active Poster
 
Join Date: Feb 2007
Location: Stayner, On
Posts: 949
Please Note: dcook1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

Quote:
Originally Posted by Brian A. MacNeish
Off topic but may be an item:

Most of the insulation in the background appears to be vermiculite. In my area, 90%+ of vermiculite here contains 1-5% asbestos. It came from the Libby, Montana mine.

Some people do not want to purchase a home with a potential environmental concern at a future re-sale and have walked from houses with this brand of vermiculite or it was removed as part of sale conditions($3,500 - $5,000+). Recently I had an electrician/trade school instructor with training about asbestos simply show no concern and buy the house.
Brian,
Reality is, most old government buildings including most schools have asbestos or vermiculite in them. It is not a panic situation. Do not entertain your guests in the attic! As long as it is undisturbed it should not be a concern. Big trucks drive by my house all the time. As long as I do not walk in front of them, it is not a concern.
Just advise the purchaser of the situation but explain this area is separate from living quarters. If someone has to work up there they need to be advised to wear protective gear. (If it is a man, he will not listen anyway.)
When I was a mason in the early eighties, I probably poured a billion bags of this stuff in many walls in Alberta. I am not dead yet..... or am I ?

BAck to electrical...... my house was listed as "UPGRADED WIRING" When I looked at it, it looked just like the first picture. Any new wires that had been added had every ground cut. They added a 220 subpanel 2feet above the bathtub and ran a BX cable out to the water heater. And cut the ground off....... can you say... bzzzzzzzzzzt! Here is a photo of one good connection.
Attached Thumbnails
k-and-t-still-use-hey-gurus-wiring.jpg  
Reply With Quote
  #11  
Old 8/18/07, 5:51 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

Quote:
Originally Posted by dcook1
Brian,
Reality is, most old government buildings including most schools have asbestos or vermiculite in them. It is not a panic situation. Do not entertain your guests in the attic! As long as it is undisturbed it should not be a concern. Big trucks drive by my house all the time. As long as I do not walk in front of them, it is not a concern.
Just advise the purchaser of the situation but explain this area is separate from living quarters. If someone has to work up there they need to be advised to wear protective gear. (If it is a man, he will not listen anyway.)
When I was a mason in the early eighties, I probably poured a billion bags of this stuff in many walls in Alberta. I am not dead yet..... or am I ?
David:
I'm not an alarmist on this stuff! Was just giving the range of reactions that you will get when you mention asbestos here. I got booted from Mike Holme' forum for challenging the top poster's and moderator's claim that "One fiber can kill you" Alarmist or what?

Here's my website page where, in the second section, I challenge a local engineering/testing/remediation company's attempt to make big $$$$$ on mould, some very minor, in attics. They claim to kill the mould and then apply "AEGIS", a very good "physically resistant to mould/bacteria" compound to the sheathing- cost $4-5 per sq ft!......so a small bungalow costs $5-6,000!!!!!
http://www.ahi-ns.ca/Healthy.htm

Last edited by Brian A. MacNeish; 8/18/07 at 9:22 AM..
Reply With Quote
  #12  
Old 8/18/07, 7:33 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

The current consensus that K&T should not buried in insulation comes mainly from two theories;
1) It can not dissipate its own heat
2) deteriorated wire insulation and connections outside of electrical boxes pose unseen hazards to those who might be working in the space.

Lets look at the first one. "It can not dissipate its own heat."

Quote:
Originally Posted by gbeaumont
Correct K&T is designed to operate in free air


More accurately, It was not designed to operate burred in insulation. While this may seem like semantics, it is important to distinguish between the two statements. The difference is the original design and intent of use.

The statement "designed to operate in free air" suggests that it was purposely designed that way. The designers gave thought about it being buried but in the end developed a product that that either they, or though testing, decided it should not be buried. This is unlikely since insulation was not used very much back then. At least by today’s standards.

The statement "not designed to be buried in insulation" means just that. It was not considered in this application. It may work just fine who knows. My wife’s cooking was not designed to fill the kitchen garbage can but it works just fine in doing it

The load on the circuit may have changed over the years as people tapped into it for more power how ever if the over current protection device is sized accordingly there should not be any heat dissipation problems. After all, if we can bury a Romex cable (with two conductors running side by side) in insulation, why would that cause less heat than the same gauge of single K&T wire. It won't. In fact in theory it should be more because of the bundling of the two wires into a single cable. The difference comes in the wire insulation. The wire insulation used in Romex has been tested and marked that it will withstand a certain temperature. What is the temperature that the rubber wire insulation used on K&T will withstand? Is it still the same after decades of use? Unknown.

It is for this reason that I prefer to use the statement “not designed to be buried in insulation”. This, in conjunction with not being able to fully see an aging wire system for inspection on a regular basis are good enough reasons in my opinion to just replace it.
Reply With Quote
  #13  
Old 8/18/07, 8:07 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

Ontario Hydro has never condemned it, providing its in good shape. To say that all K&T has to be replaced is a misnomer unless its in poor shape, or renovations are planned anyway. The demand by insurers is not back up by any code or authority.
Reply With Quote
  #14  
Old 8/18/07, 10:58 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: K & T still in use- Hey Guru's !!!

I tell people that knob and tube is is "acceptable if done right"... but that when there is a significant quantity of K&T present, I almost never see it done right, and in any case visible K&T is often seen extending into into areas where it cannot be visually inspected, so I can't tell if it's done right.

BTW, some AHJs specifically allow the installation of loose-fill insulation over knob and tube:

http://www.waptac.org/sp.asp?id=7190


K&T and insurance:

http://www.insure.com/articles/homei...old-homes.html
http://www.wishtv.com/global/story.a...Type=Printable

K&T and the NEC:

http://www.waptac.org/doclib/openfile.asp?id=605
http://www.waptac.org/sp.asp?id=7190
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Toilet guru's kmcmahon Plumbing Inspections 5 10/12/07 12:52 AM
Knob & Tube Q. for the Electrical Gurus? pdoane Electrical Inspections 18 7/11/07 12:01 PM
Flat roof gurus.... jbreazeale Structural Inspections 0 5/17/07 11:55 PM
Calling all gurus!! dmacy Electrical Inspections 4 3/8/06 2:45 PM


All times are GMT -4. The time now is 8:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts