Default Kitchen light on GFCI

Can a kitchen overhead light be on a GFCI circuit? The light wnet out when the GFCI was tripped. Can't find anything in NEC
Reply With Quote
  #2  
Old 7/13/06, 7:46 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,403
Default Re: Kitchen light on GFCI

Anything can be....
Just would not recommend it on refrigeration circuits due to failure rate of these devices.
Reply With Quote
  #3  
Old 7/13/06, 8:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

It can't be on the counter top GFCIs (AKA small appliance circuit)
Reply With Quote
  #4  
Old 7/13/06, 9:03 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,606
Default Re: Kitchen light on GFCI

Greg I have on occasion seen the bathroom light on the GFCI circuit, is that allowed?



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #5  
Old 7/13/06, 9:15 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

1st when was the home built?
2nd was a code "codified" when it was built
3rd so it is not allowed today.

Report it as not to todays standards but no BIG deal.

Sounds like nitpikky BS to me.

If anything I like it being protected by a GFCI. It is 'over' a wet location.

Again that is the chickens..t. that I get called out to say is no big deal.
Reply With Quote
  #6  
Old 7/13/06, 9:18 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

Bathroom light it depends.

Is it on the same circuit as that 'one' bathroom?

What code (cycle) are you using?
Reply With Quote
  #7  
Old 7/13/06, 9:24 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,606
Default Re: Kitchen light on GFCI

Quote:
Originally Posted by Mike Parks
Bathroom light it depends.



Is it on the same circuit as that 'one' bathroom?

What code (cycle) are you using?
Mostly 03 IRC

Hi Mike Thanx, that's kinda what I thought.

I ususlly find it on circa 1950's block home where the only outlet used to be in the light fixture over the sink. After some minor fix and flip electrical updating an outlet is added for all the new fangled gizmos.



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #8  
Old 7/13/06, 9:40 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

Brian

Use the 2005 NEC as your guide.

Unless you, everyone, know what was/is acceptable at any give time you are hanging your neck out there to be CHOPPED off.

Please watch what you say regarding electrical.

At least in Ohio you are NOT required to update anything unless the AHJ says that it is required (my opinion a safety hazard).
Reply With Quote
  #9  
Old 7/13/06, 9:52 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,606
Default Re: Kitchen light on GFCI

Quote:
Originally Posted by Mike Parks
Brian

Use the 2005 NEC as your guide.

Unless you, everyone, know what was/is acceptable at any give time you are hanging your neck out there to be CHOPPED off.

Please watch what you say regarding electrical.

At least in Ohio you are NOT required to update anything unless the AHJ says that it is required (my opinion a safety hazard).
I may consider the 05 NEC when Phoenix adopts it.



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #10  
Old 7/13/06, 9:58 PM
lprinzi lprinzi is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Jacksonville, Fl
Posts: 43
Default Re: Kitchen light on GFCI

Greg stated above that the overhead light cannot be on the counter small appliance circuits... is there a NEC section for that?
Reply With Quote
  #11  
Old 7/13/06, 10:06 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

250.52(b)(2) 2005 Nec
Reply With Quote
  #12  
Old 7/13/06, 10:12 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 384
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

The thing about receptacles and lights being on the same circuit is that if you trip the breaker while using the receptacle you might not want to be in the dark dealing with a defective appliance or whatever. Could be a safety concern in my opinion, regardless of code.
Reply With Quote
  #13  
Old 7/13/06, 10:20 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen light on GFCI

Charles

I agree that is why I put my lights and outlet on different curcuits.

It is not required.
Reply With Quote
  #14  
Old 7/13/06, 11:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Kitchen light on GFCI

Hey Guys,

Ok....my voice on this...you all know my mouth...

Ok....

1.) The light over the sink on GFCI is not big deal as long as like Greg stated it is not on the counter top circuit.....
2.) GFCI in bathrooms as mike stated CAN run lights as well as long as the circuit to that bathroom is ONLY for that bathroom and the circuit does not leave that bathroom.

Now.....for my opinions on GFCI's.....HI's should always recommend them in the report, the life you SAVE might be your client...

I came back today from a house that was just inspected by a local home inspector....and I am quite sad over it......this house was in bad shape, 30A edison fuses on 14 AWG for bedroom circuits, BX being used as the EGC and replacing the plugs with 3 hole plugs everywhere....again guys..BX is not a EGC......but I am sure everyone knows that by now.

Anyway.......I am going to need to hold a freakin LOCAL class just to make sure crap like this does not get missed again.....even the sub panel was old SE....that was worn to death.....and guess what...(10 ) no ground present plugs that were not even on the report......but had 3 hole plugs in them...

Sad to say...I was their FIXING an emergency electrical issue...not inspecting the house......dang glad of that......found extention cord wire feeding a light in the wall......yep...all this RIGHT in my face....fixing one issue and finding all this obvious other issues...so I asked the read the report....she let me....it was SAD....

OK.....I am done whining.......Where was I....oh yeah...I push GFCI's everywhere and let THEM choose to ignore my suggestions...I can sleep at night knowing I atleast told them...



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #15  
Old 7/14/06, 8:14 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 20,895
Default Re: Kitchen light on GFCI

Quote:
Originally Posted by Mike Parks
250.52(b)(2) 2005 Nec
What does this code reference for grounding electodes have to do with outlets on GFCI counter circuits??



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI light fixtures? dbook Electrical 13 9/21/07 8:28 AM
GFCI Test Light gmacandog Electrical 4 5/17/07 4:39 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical 9 4/18/07 7:22 PM
No GFCI in Kitchen rnewland Electrical 6 9/19/06 7:51 AM
How many forum members to change a light bulb? kshepard Misc. Discussion 9 8/2/06 9:56 AM


All times are GMT -4. The time now is 10:03 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts