Default Kitchen outlets

I performed an inspection in a new home in Maryland. The kitchen outlet circuits had a 20 AMP Square D breaker, 12/2 wiring and 15 AMP outlets. The circuits did have GFCI outlets within six feet of the sink area. In my report I wrote that the outlets must be 20 AMP.

The electrician stated that his installation complied with the NEC. I do not have a copy of the NEC book.

How can this be safe with the weakest link in the circuit being the outlet. I thought that NEC required 20 AMP breakers, 12/2 wiring, GFCI protection and 20 AMP outlets in new construction kitckens.
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/11/10, 5:54 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen outlets

A 15 amp duplex receptacle is permitted on a 20 amp circuit. The electrician is correct. And GFCI protection is required for all receptacles serving the countertop not just those within 6' of the sink. Look at 210.24 in the 2008 NEC.

Last edited by Robert Meier; 11/11/10 at 5:56 PM.. Reason: Added reference
Reply With Quote
  #3  
Old 11/11/10, 6:15 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen outlets

Sorry Lee, but you were incorrect on this. As RM said, the GFI protection is for all receptacles serving the countertops, not just within 6'.

A 15 amp receptacle is rated for twenty amp feed-thru. In fact the only difference is the 20 amp has the different slot configuration.

The only time the receptacle would need to be 20 amp would be if it were the only spot to plug in on the circuit. A standard duplex receptacle counts as two places.

BTW, when was the last time you saw something that had a 20 amp cordcap?
Reply With Quote
  #4  
Old 11/11/10, 6:19 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen outlets

I see that you don't have the NEC. You can view it online here:

http://www.nfpa.org/aboutthecodes/Ab...&EditionID=238
Reply With Quote
  #5  
Old 11/11/10, 6:21 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen outlets

Yes, two or more 15 amp receptacles on a 20 amp circuit is permitted. A duplex receptacle is considered two receptacles. Here's the relevant info/table from the NEC:
Quote:
210.21 Outlet Devices.
Outlet devices shall have an ampere rating that is not less than the load to be served and shall comply with 210.21(A) and (B).
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
Exception No. 1: A receptacle installed in accordance with 430.81(B).
Exception No. 2: A receptacle installed exclusively for the use of a cord-and-plug-connected arc welder shall be permitted to have an ampere rating not less than the minimum branch-circuit conductor ampacity determined by 630.11(A) for arc welders.
FPN: See the definition of receptacle in Article 100.

(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or where larger than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.
Exception No. 1: Receptacles for one or more cord-and-plug-connected arc welders shall be permitted to have ampere ratings not less than the minimum branch-circuit conductor ampacity permitted by 630.11(A) or (B) as applicable for arc welders.
Exception No. 2: The ampere rating of a receptacle installed for electric discharge lighting shall be permitted to be based on 410.62(C).

Last edited by Robert Meier; 11/12/10 at 4:58 AM.. Reason: Added Code Reference
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
The Importance of Bathroom and Kitchen Fans mkyriacou Interior Inspections 35 6/4/10 5:27 PM
kitchen outlets lprinzi Electrical Inspections 5 1/19/08 12:35 PM
kitchen outlets????? bgraham Electrical Inspections 2 4/2/07 7:09 PM
Kitchen sink & outlets lprinzi Electrical Inspections 3 6/8/06 5:52 PM


All times are GMT -4. The time now is 8:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts