Is this a version of knob and tube?
The wires are insulated. |
|
#2
|
||||
|
||||
|
Yep. That would be an "open-conductor support."
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Jeff,
How much of an issue is the insulation packed around it? I would think it would contribute to conductor overheating. |
|
#4
|
||||
|
||||
|
It's not allowed. I would say that it's a "substantial" issue which should be corrected.
394.12 Uses Not Permitted. Concealed knob-and-tube wiring shall not be used in the following: (5) Hollow spaces of walls, ceilings, and attics where such spaces are insulated by loose, rolled, or foamed-inplace insulating material that envelops the conductors -- IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |