An article in our local newspaper gave the thumbs up for knob and tube...

"There appears to be a wave of fear throughout the insurance industry when it comes to knob and tube wiring," says BCAA (British Columbia Automobile Association) Insurance product manager Brooke Hanson in a news release. "Companies are asking their customers to fork out thousands of dollars in re-wiring unnecessarily, simply because they have not taken the time to learn about the real issues."

"Knob and tube wiring is not inherently hazardous as long as it's properly maintained. If the wiring has been tampered with or if wire insulation is brittle or cracked, it should be restored."

Comments?

I don't know about anyone else but if I see knob and tube I call it a major defect and refer the buyer to an electrician for further evaluation.
Reply With Quote
  #2  
Old 11/7/06, 12:08 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Knob and tube

Quote:
Originally Posted by wblakey
"Knob and tube wiring is not inherently hazardous as long as it's properly maintained. If the wiring has been tampered with or if wire insulation is brittle or cracked, it should be restored."
True statement. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/7/06, 7:34 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Knob and tube

While I concur with Jeff, I know of several insurance companies that will not provide insurance on homes with K&T wiring. Many of those who will insure homes with K&T wiring charge a higher premium. So in many cases here it is not up to the homeowner, it's up to what the insurance company wants in order to provide insurance at reasonably priced premiums. So I call it a major defect only insofar as insurance is concerned, providing that I don't see other issues (insulation on top of the K&T, improper splicing, etc.).



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #4  
Old 11/7/06, 9:42 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Knob and tube

While the K & T itself if properly maintained is generally fine......what is not fine is the design of the circuits that involve K & T which allow in many cases a fused neutral, a shared neutral and oversized fuses which do not protect the conductor size....other than that......its fine...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 11/7/06, 9:49 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: Knob and tube

Quote:
Originally Posted by pabernathy
While the K & T itself if properly maintained is generally fine......what is not fine is the design of the circuits that involve K & T which allow in many cases a fused neutral, a shared neutral and oversized fuses which do not protect the conductor size....other than that......its fine...
Any K and T I have seen should be disconnected .
How can you tell the condition inside the wall .
I have not found any I would leave and continue to use .
Roy Cooke
</IMG>



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #6  
Old 11/7/06, 9:56 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Knob and tube

Roy.......tell that to the homeowner who will not be willing to pay $ 5,000 to $ 7,000 to upgrade it.......BUT actually i was refering to the statement that was made about the jacket if maintained....I see plenty in the wall that we gut that looks fine.......the damage generally comes from the exposed K & T...not the hidden K &T.

My other statements are the factual issues with K & T, it was simply not designed to handle todays needs and it is prone to overloading....

Don't get me wrong...I dislike ANY of the K & T I see.....but again the NEC accepts it....and i work to the NEC when I am doing electrical work...but I DO make my suggestions....thehehe...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 11/7/06, 10:21 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: Knob and tube

Quote:
Originally Posted by pabernathy
Roy.......tell that to the homeowner who will not be willing to pay $ 5,000 to $ 7,000 to upgrade it.......BUT actually i was refering to the statement that was made about the jacket if maintained....I see plenty in the wall that we gut that looks fine.......the damage generally comes from the exposed K & T...not the hidden K &T.

My other statements are the factual issues with K & T, it was simply not designed to handle todays needs and it is prone to overloading....

Don't get me wrong...I dislike ANY of the K & T I see.....but again the NEC accepts it....and i work to the NEC when I am doing electrical work...but I DO make my suggestions....thehehe...
I tell them That in Most cases they will not be able to get Home owners Insurance and to please check and make sure you have insurance . I also recommend they consider immediate upgrading to moder wiring as some day when the go to seel they might have more dificulty if they do not.
In My area you can no longer get a new Insurance policy with active K&T.
I have heard of too many horror stories of a couple spending there last dime to get into a home and find out they can not get insurance Saw the tears and iy hurts me to see them cry.
Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #8  
Old 11/7/06, 11:57 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: Knob and tube

I do not agree, and really, one could say the same thing regarding Romex. I have seen many instances of stressed installations, ripped insulation, and poor connections.

A number of homes I inspect have K&T,and if I suspect an issue, I call it out. But I feel a blanket statement like that is misleading.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #9  
Old 11/7/06, 12:02 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Knob and tube

Quote:
Originally Posted by pabernathy
Roy.......tell that to the homeowner who will not be willing to pay $ 5,000 to $ 7,000 to upgrade it.......

Don't get me wrong...I dislike ANY of the K & T I see.....but again the NEC accepts it....and i work to the NEC when I am doing electrical work...but I DO make my suggestions....thehehe...
Actually, I do tell a homebuyer that wll be expensive to up-grade. And that there is reason why many insurance companies will refuse coverage. The NEC is one thing, but the insurance company isn't concerned about code--they're concern about the possilbe cash outlay.

It's true that properly maintained K&T is not unsafe, but if the insurance co. says "no", it will win that argument everytime.

Recommend contacting the insurer first and be ready to consider an upgrade.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #10  
Old 11/7/06, 12:45 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Knob and tube

BUT...you missed the POINT......I dont play Insurance Agent......and I do not try to play one on TV either....lol....

The issue is tell them about the K & T and let THEM take that information to the Insurance Company....not my PLACE to play their role....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 11/7/06, 1:01 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: Knob and tube

I did an inspection on a pristine home 800 ± sq ft home .
It had newer Gas Furnace Gas cook stove Gas dryer.
A single 40 +lady was buying it for her self.
Now this house was 30± years old and was close to perfect .
It was all Copper and had a Breaker 60 amp service .
She could not get insurance from any one .
They all said it needed to be upgraded to a 100 amp service .
As per usual the insurance companies always win.

Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #12  
Old 11/7/06, 1:23 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Knob and tube

Quote:
Originally Posted by rcooke
They all said it needed to be upgraded to a 100 amp service .
100-amp service is another deciding factor in getting insurance here in San Diego, along with K&T wiring, lead or galvanized water supply pipes, homes built prior to 1950 (premiums are higher), fuses instead of breakers, wood roof, and probably some others that I'm forgetting at the moment.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 11/7/06, 8:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Knob and tube

lets face it....the Insurance Company can demand anything they would like...I know of a fact they would not insure an apartment complex me and my brother were going to buy simply because the apartments had fuse panels......they looked fine......but they said I was bias...since I was an electrician...anyway they would not insure them......so we just walked away as it was not worth the hassle....

Long story short....still owed by the same people...5 years later....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 11/14/06, 2:07 AM
tneyedli1's Avatar
tneyedli1 tneyedli1 is offline
Active Poster
 
Join Date: Mar 2006
Location: Port Alberni, BC
Posts: 279
Please Note: tneyedli1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube

Quote:
Originally Posted by wblakey
An article in our local newspaper gave the thumbs up for knob and tube...

"There appears to be a wave of fear throughout the insurance industry when it comes to knob and tube wiring," says BCAA (British Columbia Automobile Association) Insurance product manager Brooke Hanson in a news release. "Companies are asking their customers to fork out thousands of dollars in re-wiring unnecessarily, simply because they have not taken the time to learn about the real issues."

"Knob and tube wiring is not inherently hazardous as long as it's properly maintained. If the wiring has been tampered with or if wire insulation is brittle or cracked, it should be restored."

Comments?

I don't know about anyone else but if I see knob and tube I call it a major defect and refer the buyer to an electrician for further evaluation.
Remember, knob and tube may be at least 65 years old. The cambric type of fabric may now be very frirable. Further evaluation by a qualified residential electrician familiar with knob and tube wiring may be the only true way to approach the insurance issue.
A home that old is most likely to have more than one electrical update. So be careful how it is worded, and more important understood by the prospective purchaser.
Reply With Quote
  #15  
Old 11/14/06, 2:09 AM
tneyedli1's Avatar
tneyedli1 tneyedli1 is offline
Active Poster
 
Join Date: Mar 2006
Location: Port Alberni, BC
Posts: 279
Please Note: tneyedli1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube

Quote:
Originally Posted by wblakey
An article in our local newspaper gave the thumbs up for knob and tube...

"There appears to be a wave of fear throughout the insurance industry when it comes to knob and tube wiring," says BCAA (British Columbia Automobile Association) Insurance product manager Brooke Hanson in a news release. "Companies are asking their customers to fork out thousands of dollars in re-wiring unnecessarily, simply because they have not taken the time to learn about the real issues."

"Knob and tube wiring is not inherently hazardous as long as it's properly maintained. If the wiring has been tampered with or if wire insulation is brittle or cracked, it should be restored."

Comments?

I don't know about anyone else but if I see knob and tube I call it a major defect and refer the buyer to an electrician for further evaluation.
Remember, knob and tube may be at least 65 years old. The cambric type of fabric may now be very frirable. Further evaluation by a qualified residential electrician familiar with knob and tube wiring may be the only true way to approach the insurance issue.
A home that old is most likely to have more than one electrical update. So be careful how it is worded, and more important understood by the prospective purchaser.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buried Knob & Tube brepanshek Electrical Inspections 14 2/15/07 10:12 AM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 7:36 AM
Insulated Knob and Tube? scosta Electrical Inspections 6 2/3/07 7:22 AM
Knob and tube: heat's the main problem? kshepard Electrical Inspections 21 6/27/06 10:51 AM


All times are GMT -4. The time now is 4:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts