Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 272
Default Knob & Tube first

I've not run across this before - Any issues? thanks TG

Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/7/12, 12:51 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Knob & Tube first

Yes, heat buildup. K&T relies on free moving air to stay cool. Wrte it up, Danno!
Reply With Quote
  #3  
Old 1/7/12, 12:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Knob & Tube first

http://www.nachi.org/knob-and-tube.htm



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #4  
Old 1/7/12, 1:46 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 272
Default Re: Knob & Tube first

Thanks Guys, I knew it wasn't correct, but a local electrician found nothing wrong with plastic over the K&T.

TG
Reply With Quote
  #5  
Old 1/7/12, 4:13 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob & Tube first

I don't see an issue either. The plastic will not retain that much heat.
Reply With Quote
  #6  
Old 1/7/12, 4:38 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Knob & Tube first

Quote:
Originally Posted by Jim Port View Post
I don't see an issue either. The plastic will not retain that much heat.
Okay... then write it up for the barrier being installed improperly! Either way, it's wrong!!!
Reply With Quote
  #7  
Old 1/7/12, 5:03 PM
Kathleen Luuk's Avatar
Kathleen Luuk Kathleen Luuk is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: Richmond Hill, ON
Posts: 377
Default Re: Knob & Tube first

I don't think it's that the plastic will build up heat, but that the plastic prevents free movement of air around the K&T, that will cause the wires to heat up, no? I have never seen knob and tube, but I hear there is still some places around here with it.



when you have eliminated the impossible, whatever remains, however improbable, must be the truth.

Sir Arthur Conan Doyle.

If you have ten thousand regulations you destroy all respect for the law.
Winston Churchill
Reply With Quote
  #8  
Old 1/7/12, 5:33 PM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,246
Default Re: Knob & Tube first

You should also have your client check with their insurance company. Some companies around here won't insure a house with knob and tube.



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #9  
Old 1/7/12, 5:36 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Knob & Tube first

State Farm is one of them. My Son-In-Law is an Agent.
Reply With Quote
  #10  
Old 1/7/12, 7:17 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Knob & Tube first

Quote:
Originally Posted by kluuk View Post
I don't think it's that the plastic will build up heat, but that the plastic prevents free movement of air around the K&T, that will cause the wires to heat up, no? I have never seen knob and tube, but I hear there is still some places around here with it.
You are correct Kathleen.
Reply With Quote
  #11  
Old 1/7/12, 9:14 PM
Kathleen Luuk's Avatar
Kathleen Luuk Kathleen Luuk is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: Richmond Hill, ON
Posts: 377
Default Re: Knob & Tube first

Thanks Jeffrey, just wanted to check, never having seen or dealt with it I am only going by what I have read. Good to know I remembered something



when you have eliminated the impossible, whatever remains, however improbable, must be the truth.

Sir Arthur Conan Doyle.

If you have ten thousand regulations you destroy all respect for the law.
Winston Churchill
Reply With Quote
  #12  
Old 1/7/12, 9:21 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Knob & Tube first

Quote:
Originally Posted by bhamilton View Post
You should also have your client check with their insurance company. Some companies around here won't insure a house with knob and tube.
Exactly.
Knob and tube was installed Before 1950 . It is an obsolete Type of wiring that is not suited for today's equipment and should be immediately upgraded
Reply With Quote
  #13  
Old 1/7/12, 9:39 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob & Tube first

Quote:
Originally Posted by rcooke View Post
Exactly.
Knob and tube was installed Before 1950 . It is an obsolete Type of wiring that is not suited for today's equipment and should be immediately upgraded
Roy,
I'm not disagreeing with you but would you actually put that wording into an inspection report?
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/7/12, 9:45 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Knob & Tube first

Quote:
Originally Posted by Robert Meier View Post
Roy,
I'm not disagreeing with you but would you actually put that wording into an inspection report?
Yes .
I expect I am one of a very few left who took Knob and Tube at Trade school .
Proper method of soldering with a Blow torch to heat the dip pot and the big old Copper Soldering iron .
Reply With Quote
  #15  
Old 1/7/12, 10:12 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Knob & Tube first

LOL I doubt many are qualified to solder it properly.
Side note is nobody mentioned double insulating conductors as a no no.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buried Knob & Tube brepanshek Electrical Inspections 14 2/15/07 9:12 AM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM
Knob and tube wblakey Electrical Inspections 17 11/14/06 7:41 PM
Knob and tube: heat's the main problem? kshepard Electrical Inspections 25 6/27/06 9:51 AM