Quote:
Originally Posted by Jim Port View Post
Installing NM cable in conduit is specifically allowed by the NEC. It is also required where subject to physical damage.
Then make that extension cord which is the same thing in my part of the world.

Extension cord and K& T are meant to be in open air .
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #62  
Old 1/8/12, 9:07 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Knob & Tube first

Quote:
Originally Posted by rcooke View Post
Sorry about that . This is the panel

http://www.homedepot.ca/product/30-a...-spaces/901371

I love the USA was down on Friday and bought a water softener $397;00 just looked and the same one in Canada is $598.00
Thanks Roy. When you said
Quote:
They are still manufactured and sold in Canada .I am also putting in a new FP panel For my new Generator .
I thought you were referring to Federal Pacific (Stab-Lok) panels which have a very bad history down here.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #63  
Old 1/8/12, 9:15 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Knob & Tube first

Roy
i think there is a difference between yours and the ones down here



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #64  
Old 1/8/12, 11:59 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Knob & Tube first

Quote:
Originally Posted by mlarson View Post
It simply is not my business if you choose to use your personal bias as an electrician against knob and tube.

Knob and tube can be safe and is permitted.

Some insurance companies will not insure and that is what I inform my clients about if no other problems with it exist.
The problem is that you can't see all of the wiring so it can never be known beyond a shadow of a doubt to be "safe" because it is largely concealed in walls, ceilings, and beneath floors. No electrician could say with certainly that the system was absolutely safe.

While yes, technically it is an accepted method, everything deteriorates over time and nothing can be expected to last forever. I refer it whenever I see it to an electrician and privately I tell my clients I would not let my children sleep in a home with knob and tube wiring.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #65  
Old 1/9/12, 12:01 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Knob & Tube first

Quote:
Originally Posted by mlarson View Post
FYI Knob and tube wiring was being installed in some areas into the 1960s
And back in Edison's day.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #66  
Old 1/9/12, 7:12 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Knob & Tube first

I agree with Joe on what is hidden could be the problem, K&T is outdated and should be explain as such. Problem around here most homes have been flipped and are low income. People go in paint, insulated and walk all around in the attic. Insulation over K&T .Strike one, add circuits without doing it in a proper fashion Likely taped together strike 2. .
Next problem Most electricians are not old enough to evaluated K&T.

Look at this way Model T would not be the best idea to drive down the interstate now days . was great in the day.
More loads, Uneducated People on the system loading it up .

I inform, Note it , and recommend to have a electrician evaluate it. It is up to them to make the final decision
Long story short Would i accept in my home No.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #67  
Old 1/9/12, 7:54 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Knob & Tube first

Wayne, I am not sure that I understand your post. First you say;
Quote:
Originally Posted by wwilson3 View Post
Next problem Most electricians are not old enough to evaluated K&T.
Then you make this comment;
Quote:
Originally Posted by wwilson3 View Post
I inform, Note it , and recommend to have a electrician evaluate it. It is up to them to make the final decision.
Do you also inform your client of your first statement?

Wasn’t too long ago that I looked at the electrical that a Home Inspector had written up. Although the wiring was old I found little that needed to be addressed on the electrical although there was two pages written up.
What I did notice was the HI hadn’t said a word in their report about 2x6 floor joist that spanned 12 feet nor anything about a 1 ¼ waste line on the washer.
It seems that this HI thought they knew more about the electrical than another trade although at the time the house was built everything including the electrical was code compliant.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #68  
Old 1/9/12, 7:56 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Knob & Tube first

Quote:
Originally Posted by wwilson3 View Post

Look at this way Model T would not be the best idea to drive down the interstate now days . was great in the day.
More loads, Uneducated People on the system loading it up .

...But still completely legal !!!

(Perfect comparison) Thanks.
Reply With Quote
  #69  
Old 1/9/12, 8:29 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Knob & Tube first

Quote:
Originally Posted by jfunderburk View Post
The problem is that you can't see all of the wiring so it can never be known beyond a shadow of a doubt to be "safe" because it is largely concealed in walls, ceilings, and beneath floors. No electrician could say with certainly that the system was absolutely safe.
Which is true for any wiring method.

Most knob and tube has been modified and a problem is usually evident.

My complaint is with categorically condemning Knob and tube with no evidence of a problem.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #70  
Old 1/9/12, 8:32 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Knob & Tube first

Quote:
Originally Posted by mlarson View Post
Whick is ture for any wiring method.
True Micheal how ever wiring like people when it gets older just is not the same. ever wonder why you have problems doing something now you didn't have when you were 17?



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #71  
Old 1/9/12, 8:35 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Knob & Tube first

Quote:
Originally Posted by wwilson3 View Post
True Micheal how ever wiring like people when it gets older just is not the same. ever wonder why you have problems doing something now you didn't have when you were 17?
This thread is not about your personal problems



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #72  
Old 1/9/12, 8:36 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Knob & Tube first

Quote:
Originally Posted by wwilson3

Look at this way Model T would not be the best idea to drive down the interstate now days . was great in the day.
More loads, Uneducated People on the system loading it up .





Quote:
Originally Posted by jjonas View Post
...But still completely legal !!!

(Perfect comparison) Thanks.

I think it would not be perfectly Legal on the Highway it would not be able to keep up with the traffic now 65 and most doing 70 +.

The model T was great in its day but it is not up for today's requirements
I feel like Knob and Tube it is also obsolete .
Reply With Quote
  #73  
Old 1/9/12, 8:37 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Knob & Tube first

Try to stay on topic Roy.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #74  
Old 1/9/12, 8:39 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Knob & Tube first

Quote:
Originally Posted by wwilson3 View Post
True Micheal how ever wiring like people when it gets older just is not the same. ever wonder why you have problems doing something now you didn't have when you were 17?
Wayne... (Other than the lack of a grounded conductor), What would your opinion be of a home (originally wired with K&T), having been rewired with HTTN, but still setup as K&T??? (Note: The panel was upgraded to a breaker panel, as opposed to the orig fused panel/blocks)??? Yes I have seen this once or twice. Still a defect in your eyes???
Reply With Quote
  #75  
Old 1/9/12, 9:14 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Knob & Tube first

Quote:
Originally Posted by jjonas View Post
Wayne... (Other than the lack of a grounded conductor), What would your opinion be of a home (originally wired with K&T), having been rewired with HTTN, but still setup as K&T??? (Note: The panel was upgraded to a breaker panel, as opposed to the orig fused panel/blocks)??? Yes I have seen this once or twice. Still a defect in your eyes???
If has been inspected and passed, I still inform if the K&T was still in use, In fact more chances of over loading if it has been upgraded and Modified with additional wire and a new panel .
Nothing wrong with fuses still legal lolol.
as long as no pennies have been added.
K&T makes me nervous, it is simple to replace when renovating . Most houses with it probably Balloon construction so why wouldnt you just drop a new wire down the wall?
In most cases these homes have been flipped and many short cuts have been taken . Yes the panel has been inspected but hat about the wiring? not likely in the attic or crawl space .



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buried Knob & Tube brepanshek Electrical Inspections 14 2/15/07 9:12 AM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM
Knob and tube wblakey Electrical Inspections 17 11/14/06 7:41 PM
Knob and tube: heat's the main problem? kshepard Electrical Inspections 25 6/27/06 9:51 AM


All times are GMT -4. The time now is 8:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts