Default Knob and tube: heat's the main problem?

Knob and tube is old by now and may be threadbare and badly spliced, but that's not something we're going to track down as inspectors if it's buried in insulation.
My understanding is that installing additional insulation to save on heating costs is now so common that knob and tube is often buried and so is unable to dissipate heat the way it was designed to.

You can call it out as an outdated but acceptable wiring system as long as it has no visible wiring defects but if you miss calling out buried K&T as a possible fire hazard you may be open to liability. Is this right?
Reply With Quote
  #2  
Old 6/24/06, 12:33 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Knob and tube: heat's the main problem?

I guess it is possible Kenton if you do not explain in your report that you can only inspect what you see. I do not do many pre 40's homes so I do not worry too much about it
Reply With Quote
  #3  
Old 6/24/06, 12:40 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Knob and tube: heat's the main problem?

Good Article posted by Paul next door about inspecting Knob and Tube but I didn't see anything about heat being a concern. There are a lot of older houses in town here and it still pops up occasionally.
Of course heat's a concern all over Phoenix

Last edited by kshepard; 6/24/06 at 12:51 AM..
Reply With Quote
  #4  
Old 6/24/06, 12:42 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Knob and tube: heat's the main problem?

Here's what I say...got it off this board somewhere. I forget who to credit.

"Knob and tube wiring is partially covered by insulation. This method of wiring was designed to be open to the air to prevent heat build-up. This wiring method should be evaluated by an electrician and certified as being safe or it should be replaced."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 6/24/06, 6:40 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Knob and tube: heat's the main problem?

394.10 Uses Permitted. Concealed knob-and-tube wiring shall be permitted to be installed in the hollow spaces of walls and ceilings or in unfinished attics and roof spaces as provided in 394.23 only as follows:

(1) For extensions of existing installations

(2) Elsewhere by special permission 394.12

Uses Not Permitted. Concealed knob-and-tube wiring shall not be used in the following:

(1) Commercial garages

(2) Theaters and similar locations

(3) Motion picture studios

(4) Hazardous (classified) locations

(5) Hollow spaces of walls, ceilings, and attics where such spaces are insulated by loose, rolled, or foamed-inplace insulating material that envelops the conductors"
Reply With Quote
  #6  
Old 6/24/06, 7:52 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

Quote:
Originally Posted by jfunderburk
"This method of wiring was designed to be open to the air to prevent heat build-up..."

This may sound on the surface like symantics but "K&T was not designed to be burried insulation" would be more accurate.

"K&T was designed to be in open air" implies that the original electrical engineers that devloped K&T had this in mind . The fact that orginal installations were in free air is inhernt from the attempts to keep it away from combustible material.

"K&T was not designed to be covered in thermal insulation" implies that although this application was probably not considered during the orginal designing of the electricla system in may or may not work fine. A re-evaluation of the system with it covered in the insulation would be needed to determind if it would provide adequate service and saftey.

Also, in general, The K&T systems were not designed to carry some of the loads that we expect today. This can also increase the temperature.

FYI: Did you know that the desiel engine was NOT originally designed to run on fossil fuel?
Reply With Quote
  #7  
Old 6/24/06, 8:23 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

Ontario Hydro has not condemned K&T. It seems to be an issue driven by insurance companies. Mind you if its exposed and damaged it would be wise to upgrade. I think that is just common sense.

As to diesels you can run them on Canola oil, french fry oil or vegetable oils.
Reply With Quote
  #8  
Old 6/24/06, 9:19 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

That's right Raymond. Peanut oil was accually the fuel the deiesel engine was oringally designed for.
Reply With Quote
  #9  
Old 6/25/06, 12:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Knob and tube: heat's the main problem?

Kenton,

I am sure others have posted this but I will elaborate.

The main problems with K&T is the following in my opinion

1.) Usually only # 14 AWG and so it has a capacity limit.
2.) As you stated it is many times embedded in insulation which defects the designed installation of the product, It needs to be FREE AIR to allow for heat removal.
3.) The rubberish style jacket tends to crack off and expose the conductor which again is a real issue since it is usually in the older insultation that is not flame-retardent.

My largest concern is the capacity to be honest with you and the effects overloading the circuit can have on the OTHER issues given, with the advent of many chances in our lifestyles the owners tend to bring in new things like computers and flour. lights and so on that create harmonics and increases the load value on the neutral which is a shared capacity neutral sometimes with many rooms....it is also usually # 14 AWG...now you have a neutral on a circuit that could be overloaded.....and add the fact it can't radiate heat from the wire because it is also now baried in insulation because the home owners wanted some storage space...yeah we have all seen this.

Now ofcourse we are not speaking of any "grounding" potential as well but that is not nearly as much of MY concern as the previously mentioned issues....a GFCI on the circuit can add protection ( having nothing to do with grounding as you all should know ) but it does not solve the problem of potential overloading.

Usually in a K&T house we see maybe 2 receptacles per room, we suggest they upgrade as it is not able to be expanded...BUT we see extention cords and power strips all around...increasing the load and demand on a conductor that was not designed for it based on it's layout....which is a huge common neutral in most cases...the poor neutral could have issues.....even WORSE if the home is a 120V service......all on the same LINE will compound the issues on the neutral......now in an older 120/240V service....IF the circuits were done right you can reduce the issue a little...BUT all depends on the layout of the panel and hope it was done by someone who KNOWS the effects.

While K&T is accepted because the code is not retroactive....BUT it should always be called out and explained it is not able to handle the demands of our generation or the next generation......so it is a PAY NOW or PAY LATER issue........I prefer to have them PAY NOW.....



Paul W. Abernathy
Reply With Quote
  #10  
Old 6/25/06, 12:37 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

I am not really sure heat is as big an issue with K&T as it would be with TW insulated paper Romex. If both were buried in the same insulation the Romex would be running hotter since the conductors are closer together and the main mechanism of failure would be failure of the TW insulation on the wire.
K&T is basically insulated by the knobs and the space between them.
I suppose at a certain point the wire could fail but that Romex would have burned up long before the copper failed. I suppose it would really come down to what type of thermal insulation was blown in the wall. If it was shreaded newspaper you have a hazard, no matter what kind of wire is there. If it was rock wool or glass, your K&T became more like MI cable.
Reply With Quote
  #11  
Old 6/25/06, 8:36 PM
sparks's Avatar
sparks sparks is offline
Spammer
 
Join Date: Apr 2006
Location: New York City
Posts: 29
Please Note: sparks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

David posts the rule from the NEC, and I wondered if he includes that information in his reports? I thought the HI was afraid of the NEC and advoids speaking to defects as violations.

Seems like some double standards here from both the US and Canadian sides. Roy?

What gives the NEC, or the SOP?

BTW, I think that the subject of the information related to K&T was covered long ago by others in the archives, and searching for that information will show that this wiring method is best left alone.

I also read where there are many issues in the attic spaces where the blown in insulation creates the problems now associated with possible fire hazards.

How many HI's really crawl into the attic to have a look see?
Reply With Quote
  #12  
Old 6/25/06, 8:54 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Knob and tube: heat's the main problem?

I am not sure why everything we post here is considered something that would be put in a report...I give alot of code but no one ever says to include it in a report......we are all adults here so we will assume HI's know what to include and what not to include....its all about education not telling someone how to write their report....

As for MY post.....you did not see one bit of NEC in my explanation and I can QUOTE NEC Code with the best of them....lol



Paul W. Abernathy
Reply With Quote
  #13  
Old 6/25/06, 8:57 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: Knob and tube: heat's the main problem?

Quote:
Originally Posted by sparks
David posts the rule from the NEC, and I wondered if he includes that information in his reports? I thought the HI was afraid of the NEC and advoids speaking to defects as violations.

Seems like some double standards here from both the US and Canadian sides. Roy?

What gives the NEC, or the SOP?

BTW, I think that the subject of the information related to K&T was covered long ago by others in the archives, and searching for that information will show that this wiring method is best left alone.

I also read where there are many issues in the attic spaces where the blown in insulation creates the problems now associated with possible fire hazards.

How many HI's really crawl into the attic to have a look see?
My openion Knob and tube has served its useful life .
Not adequate for todays home and should be upgraded immediately by a qualified person.

Roy Cooke sr ...royshomeinspection.com
Reply With Quote
  #14  
Old 6/25/06, 9:28 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

As to code, you could always state along the lines that this method or installation does not meet current code, or is against code. Just don't quote the code reference unless asked to prove otherwise post report.

If you have knowledge of code I see no reason why one would be out on a limb if stating code reference. If you are not sure don't state its not to code you could say .... this item "may not" meet code or item does "not appear" to meet code. But having said that you had better be certain you are not calling code for buildings that predate the current codes.
Reply With Quote
  #15  
Old 6/25/06, 9:55 PM
jmichalski's Avatar
jmichalski jmichalski is offline
Active Poster
 
Join Date: Aug 2004
Location: Souderton, PA
Posts: 2,532
Please Note: jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and tube: heat's the main problem?

Quote:
Originally Posted by sparks
How many HI's really crawl into the attic to have a look see?
Most HIs I know inspect all attics where access is provided, including crawling to remote points provided it does not constitute a safety hazard or present the potential for damage.

All HIs should at least view the attic and components including wiring from an entry point.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Buried Knob & Tube brepanshek Electrical Inspections 14 2/15/07 9:12 AM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM
Insulated Knob and Tube? scosta Electrical Inspections 6 2/3/07 6:22 AM
Knob and tube wblakey Electrical Inspections 17 11/14/06 7:41 PM


All times are GMT -4. The time now is 4:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts