InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools
  #1  
Old 1/21/07, 7:52 AM
Daniel E. Giblin Daniel E. Giblin is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Hanahan, SC
Posts: 14
Please Note: dgiblin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Labels on Wiring in the Panel

What are some of your thoughts on these labels on the wiring in the panel. They used the sheathing off of the Romex for the labels. I have seen it 2x so far and have recommended the labels be removed for safetey reasons as the sheathing should be removed once the wiring enters the panel.
Attached Thumbnails
labels-wiring-panel-dsc00121.jpg  

Last edited by dgiblin; 1/21/07 at 9:32 AM..
Reply With Quote
  #2  
Old 1/21/07, 8:42 AM
Steven E. Wiegner Steven E. Wiegner is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Valrico, FL
Posts: 315
Send a message via AIM to swiegner
Default Re: Labels on Wiring in the Panel

I Have Seen It Often
I Do Not Think It Would Cause Any Concerns
Most Panels Are Not Even Labeled
Reply With Quote
  #3  
Old 1/21/07, 9:42 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

Daniel, there is NO requirement that the sheathing be removed. You can leave it as long as you want. Doing neat work tells us differently. There is also NO safety concern with these, and absolutely no need to flag IMO.

I do this myself when panels are flush and you cannot see the cables entering the box. Only I put the labels where the cables enter, not near the breaker.
That is what panel directories are for.
Reply With Quote
  #4  
Old 1/21/07, 10:32 AM
Scott A. Figert Scott A. Figert is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Cecil, Oh
Posts: 163
Default Re: Labels on Wiring in the Panel

I also do this, and I leave them near the breakers. On new construstion the cover is stored so it doesn't get damaged, drywall spray, painted, etc.. Easy way for all other subs to know what is where. I've aslo added wiring to existing boxes and label my wire this way and on the cover too. Most covers around here have miss labeled or no labeling.
Reply With Quote
  #5  
Old 1/21/07, 10:59 AM
dbush's Avatar
dbush dbush is offline
Active Poster
 
Join Date: Dec 2002
Location: Joplin, MO
Posts: 268
Send a message via MSN to dbush Send a message via Yahoo to dbush
Please Note: dbush is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

It is done often and makes it a whole lot easier when it comes time to actually label the panel covers. I see no problem with it.
Reply With Quote
  #6  
Old 1/21/07, 12:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Labels on Wiring in the Panel

Personally...and this is just MY opinion......I find it rather sloppy.

I label the lines like this when doing the rough in but when finishing out the panel I transfer these label locations to the enclosure ledger in a neat manner and remove the sleeves on the wire.

Granted the only real problem i have is IF someone put the scrap romex sleeves on and then never labeled the panel properly...via 408.4 but alas don't laugh...I have seen it and it had passed final inspection.

How as I said I do this in the early service/ rough stage..but when I go to finish the panel out...I remove them as I trasfer them to the ledger.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 1/21/07, 12:06 PM
Daniel E. Giblin Daniel E. Giblin is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Hanahan, SC
Posts: 14
Please Note: dgiblin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

I should have stated this is not new construction. The home is 2 years old and the legend for the panel is clear and accurate according to the labels on the wires when compared to the legend.
Reply With Quote
  #8  
Old 1/21/07, 12:20 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Labels on Wiring in the Panel

Daniel,

other than redundant.....it's fine. I guess some could clammer....it's combustible....but alas....I have no worries about it other than I don't like the look of it in my panels.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 1/21/07, 2:57 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

edited
Reply With Quote
  #10  
Old 1/21/07, 3:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Labels on Wiring in the Panel

lol...ok..what did you edit Marc....lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 1/21/07, 3:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

Quote:
Originally Posted by pabernathy
lol...ok..what did you edit Marc....lol
A reply to the wrong post. I had several windows up.
Reply With Quote
  #12  
Old 1/21/07, 3:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Labels on Wiring in the Panel

lol....been there fella...done that also



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 1/21/07, 11:40 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

This is strictly a personal installation situation. There is no concern for the labeling using the sheathing.
The mention that this passed inspection is not really relevant, as the cover is supposed to be installed for an inspection, and electrical inspectors are not permitted to remove equipment covers during the inspection process.
Reply With Quote
  #14  
Old 1/22/07, 9:00 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Labels on Wiring in the Panel

However, we know VERY well that if the electrician is on the job the AHJ will and can ask the electrician to remove any cover they wish to look behind.

Nope...not really an issue of any concern on the insulation labels...just don't like the looks of it myself....they are nice to identify the circuits right before you properly label the ledger...other than that I remove them afterwards.

But to each his own......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/22/07, 9:20 AM
dbush's Avatar
dbush dbush is offline
Active Poster
 
Join Date: Dec 2002
Location: Joplin, MO
Posts: 268
Send a message via MSN to dbush Send a message via Yahoo to dbush
Please Note: dbush is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Labels on Wiring in the Panel

Paul, the only reason I think it might be nice to have them still in is, if for instance, the buyer of a new construction home labels the ledger instead of the electrician, and it gets labeled with the following: "Misty's Bedroom, Joe's Bathroom, Gym", etc; instead of SW Bedroom, Hallway Bathroom and Office. Of course, I see that in quite a few houses anyway. I usually recommend they test what a breaker belongs to with the very expensive method of purchasing a portable radio. Turn the radio up and throw breakers until the radio goes out. Beats buying a breaker locator. Any other ideas?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Sub Panel Wiring tmartens Electrical 4 2/27/07 11:56 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 5:24 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts