Default Lack of circuits

The main panel was replaced in this 1930 home.

It appears to be lacking the proper amount of circuits.

I was looking at the code check book and is there anything that states the minumum amount of circuits at a main panel.

These 1st time buyers are being led to believe they have an updated service.

The home lacks receptacles in the bedroom. (1 in each room was observed)
Knob & tube was present
The kitchen is outdated and had only 1 receptacle that was installed in the door.
The main panel has only 3or 4 breakers for the entire house. Excluding the air.
No GFCI protection.
Fixtures wear rusted, dated.

Any thoughts on this upgated service?



Thanks

Last edited by dmacy; 6/26/07 at 8:44 PM..
Reply With Quote
  #2  
Old 5/14/07, 1:59 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Lack of circuits

Wow! I wonder how anyone is not Amish can survive with only one receptacle in the kitchen. Do the owners have a refrigerator or an ice box? How is a receptacle installed in a door?

The porcelain knobs and tubes in the 2nd photo look dark like they have soot on them. Has this house had a fire?

Jim King
Reply With Quote
  #3  
Old 5/14/07, 2:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

Current code probably means nothing since this is an existing house but the general rule is you should be able to reach a receptacle from anywhere in a room at the wall with a 6 foot cord and not string it across a doorway or fireplace. That was not the standard as recently as the early 60s so it is not unusual to see places where this is not true. One receptacle in a room is not uncommon in old houses. The other place where it shows up is a lack of 20a receptacle circuits serving countertops in the kitchen (2) and bath (1).
They would also require GFCI protection. My guess is this old house needs a serious electrical upgrate.
Reply With Quote
  #4  
Old 5/14/07, 2:06 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Lack of circuits

What bothers me is this is a typical type house were the first time buyres are told that this house has been upgraded as they installed a new panel.

I told them that they need an electrician to update the branch circuitry and I opened there eyes as they were misled by the agents.

They have a new born on the way. I don't want the responsability of a infant being electrocuted due to extension cord wiring and other potential concerns of an older system.
Reply With Quote
  #5  
Old 5/14/07, 3:22 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

In the UK, 3 or 4 breakers for the entire house is perfectly normal. But then we use fuses in each and every plug, so a device can blow a fuse without tripping the whole circuit. Come on America. Catch up!
Reply With Quote
  #6  
Old 5/14/07, 5:14 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

Ian, it would not be a case of catching up as much as totally changing our wiring philosophy. You folks have 230v ring circuits and we use radial circuits at half the voltage. You also have fewer transformers serving more homes each. I doubt most of your homes have 48 kva services either but that is pretty much standard here with bigger homes being twice that. The differences go on like this quite a bit.
Reply With Quote
  #7  
Old 5/14/07, 5:50 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

Quote:
Originally Posted by dmacy
Any thoughts on this upgated service?
Sounds like the service was, indeed, updated. You apparently are confused on what the term "service" means. The branch circuits, however, do not appear to have been updated.
Reply With Quote
  #8  
Old 5/14/07, 8:41 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Lack of circuits

Quote:
Originally Posted by Marc D. Shunk
Sounds like the service was, indeed, updated. You apparently are confused on what the term "service" means. The branch circuits, however, do not appear to have been updated.
That's how I read it, too.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 5/14/07, 11:08 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

Quote:
Originally Posted by dmacy
They have a new born on the way. I don't want the responsability of a infant being electrocuted due to extension cord wiring and other potential concerns of an older system.
I truly understand your concern, but how could you EVER be considered "responsible" for such a thing????

You just report the lack of "modern" circuits; quantity and otherwise.
Because the house is old is not your fault. Because previous owners never added circuits is not their fault either. It is simply fact. Obviously the previous owners never needed to add circuits. It is not mandatory that they do.

As Marc stated, the service and branch circuits are totally different things. Many folks are mistaken in their belief that when they are told the "Service has been updated", they think the house was re-wired.
Reply With Quote
  #10  
Old 5/15/07, 12:29 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Lack of circuits

Most local codes in our area hold that if the 'service' (generally taken to mean raising the service amps or replacing the service equipment) is upgraded, then ALL the house's electrical equipment (breakers, wires, conduit (read: take out knob and tube), receptacles (read: current standards with regards to GFCI and AFCI and receptacle placement, distance and number) must also be upgraded.

In other words, if a licensed electrician changes out the SE panel, everything downstream must also be upgraded to current local code standards.

Must be a union thing .



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 5/15/07, 12:51 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

William, if that is in fact true, it is an absolutely absurd requirement IMO.
I bet it could also be proven illegal to enforce.
Reply With Quote
  #12  
Old 5/15/07, 1:28 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

Quote:
Originally Posted by wdecker
Most local codes in our area hold that if the 'service' (generally taken to mean raising the service amps or replacing the service equipment) is upgraded, then ALL the house's electrical equipment (breakers, wires, conduit (read: take out knob and tube), receptacles (read: current standards with regards to GFCI and AFCI and receptacle placement, distance and number) must also be upgraded. .
Got a link? Not calling BS, because I can believe anything from the Chicago area. I'd just like to read more about it, is all.
Reply With Quote
  #13  
Old 5/15/07, 5:54 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Lack of circuits

I would, too. That would make some interesting reading.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 5/15/07, 10:44 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lack of circuits

At those connections to the K&T running into the panel at top center secured to the box in any way, or just routed through the knock-out? Around here (assuming that it was allowed to stay) most AHJs would require that the K&T terminate at junction boxe(s), with modern (NM or wire in conduit) run from the junction box to the panel in an approved manner.
Reply With Quote
  #15  
Old 5/15/07, 11:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Lack of circuits

"There are not as many outlets as would be required by current standards, and you may wish to consult an electrician about the possibility of adding more."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM
Multi-Branch circuits Matthew Hopkins Electrical Inspections 3 6/28/07 8:18 PM
Article 240 : Overcurrent Protection Article pabernathy Electrical Inspections 0 5/23/07 12:40 PM
Preemptive Spark Helps Find Electrical Short Circuits In Airplanes mbledsoe Electrical Inspections 0 6/21/06 3:30 PM


All times are GMT -4. The time now is 4:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts