Default Larger wires at service drop

I never noticed this before. The wires from the pole look very small. Then at the mast they are bigger.

Could you please fill in the blanks for me with whats wrong here or what could happen vs the main breaker size?
Attached Thumbnails
larger-wires-service-drop-100_2563-800x600-.jpg   larger-wires-service-drop-100_2564-800x600-.jpg  




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 12/31/08, 10:27 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,700
Default Re: Larger wires at service drop

One is copper and one Alu?

Same rating?



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 12/31/08, 10:52 AM
Jeff Moore Jeff Moore is offline
New User
 
Join Date: Aug 2008
Posts: 29
Please Note: Jeff Moore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Appears that even the stranded Al wire changes sizes at the clamp. Interesting question and I wish I had an answer for you but APS or SRP own the incoming lines and maybe a call to them would help. Or one of the electrical folk on this site can shed some info on the setup.
Reply With Quote
  #4  
Old 12/31/08, 11:17 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

This is quite typical as the utilities do not use the NEC tables to size their wires.

The conductors have different insulation ratings and can radiate heat better by being in free air.

It is quite common for the overheads not even to be upgraded when a service increase is done.
Reply With Quote
  #5  
Old 12/31/08, 11:38 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Larger wires at service drop

Good answer Jim!! I actually new what you saying. (Electrical has been one of my weaker areas)

I have a question pertaining to the clamp on the stranded wire. Is this an acceptable method of attaching the 2 wires? Shouldn't a similar clamp be used like the other two wires?
Reply With Quote
  #6  
Old 12/31/08, 11:49 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: Larger wires at service drop

They are both Al wires.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #7  
Old 12/31/08, 11:55 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by dmacy View Post
Good answer Jim!! I actually new what you saying. (Electrical has been one of my weaker areas)

I have a question pertaining to the clamp on the stranded wire. Is this an acceptable method of attaching the 2 wires? Shouldn't a similar clamp be used like the other two wires?

The other two wires DO have the same H tap, you just can't see them because they are covered. The neutral does not need to be covered. It is a POCO connection, they are all done like that here (Tucson Electric Power).
Reply With Quote
  #8  
Old 12/31/08, 12:07 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

One strand inside the neutral is a steel wire. This provides the support for the triplexed cable. The clamp on the stranded wire has the steel passing thru and going to the eyebolt on the mast.

The insulated conductors do not need a clamp as the triplex construction is all supported off of the carrier strand. The cable acts as a unit.
Reply With Quote
  #9  
Old 12/31/08, 12:23 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by Jim Port View Post
One strand inside the neutral is a steel wire. This provides the support for the triplexed cable. The clamp on the stranded wire has the steel passing thru and going to the eyebolt on the mast.

The insulated conductors do not need a clamp as the triplex construction is all supported off of the carrier strand. The cable acts as a unit.
The way he said "attaching the 2 wires" I think he is referring to the H tap.
Reply With Quote
  #10  
Old 12/31/08, 7:58 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Yes, it is not necessary to put an HTap cover on the neutral. The neutral conductor is bare to begin with, so putting a cover on the HTap of the neutral is pointless and wasteful. The HTap's themselves cost about 85 or 90 cents, but the covers are 4 to 5 dollars each.
Reply With Quote
  #11  
Old 1/1/09, 2:47 PM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: Larger wires at service drop

Yes, but I am wondering about the smaller wire size coming from the pole then jumping up to a larger size into the meter and panel.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #12  
Old 1/1/09, 2:55 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Larger wires at service drop

Quote:
Originally Posted by mtimpani View Post
Yes, but I am wondering about the smaller wire size coming from the pole then jumping up to a larger size into the meter and panel.
Happy New Year Mark.

Jim answered your wondering in post #4:

http://www.nachi.org/forum/f19/large...87/#post461758



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #13  
Old 1/1/09, 8:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by mtimpani View Post
Yes, but I am wondering about the smaller wire size coming from the pole then jumping up to a larger size into the meter and panel.
Well then, quit worrying so much.


It's completely normal. The power companies size their conductors to NESC rules, and electricians size their wires to NEC rules. Two different animals. Unless the customer is having problems that can be attributed to voltage drop (lights dim severely when you turn on the disposal, etc.), it's not even worth a comment.
Reply With Quote
  #14  
Old 1/2/09, 7:00 PM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: Larger wires at service drop

Marc, I am not an electrician so bare with me.

My mother in laws house got upgraded from a 100amp to a 200 amp. The wires coming from the pole were 100amp wires and the power company changed them to a 200 - 300 amp size. Then those same size wires were brought down into the panel and a 200amp breaker was installed so the panel is a 200amp panel.

The wires in the note above look very small like 60 - 100amps. Are you saying its ok to put larger feed wires to the panel to upsize to 200amps?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #15  
Old 1/3/09, 12:54 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

As mentioned by Jim earlier in the thread, the size of the conductors from the pole to the weatherhead are sized based on the Utility codes - NESC. The size of the conductors from the overhead splice (service point - which is the load side of the utility conductors - service drop), are sized on the NEC.

The utility company will size their conductors based on the past usuage. So, if there is a service change, from 100A to 200A without a load change, the utility company will not even change their conductors from the pole.

The Utility company will size their conductors based on usuage (utility bills) and any additional calculated load(s). This conductor size will still be smaller than the NEC requirement.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Mention voltage drop? dbucknavich Electrical 18 6/18/08 7:58 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical 5 12/4/06 3:40 PM
Service Drop Was Finally Removed! jtedesco1 Electrical 1 12/1/06 3:40 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 7:17 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts