Default Re: Larger wires at service drop

Wow this is interesting info! How does the power company know that if the conductors were feeding a 60 amp breaker/service that when they switch the panel to a 300 amp service the wires wont burn up?

I wonder how come in this area they always switch the conductors when they go to a 200 service?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #17  
Old 1/4/09, 8:23 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Yes you are right about that, when you upgrade to 200 amps going thru the proper channels TEP always brings in a new triplex. That one in the pic looks like what they use for 100 amps. Was there a 200 amp service? It is possible the POCO was not involved, some of us do have the ability to install H taps.

If you want to check on it just call Development Services, ask for the permit counter and ask for a permit history on the address. Anyone can do it and it's free. Keep in mind the City of Tucson and Pima County are in different offices. See if there was a permit for an upgrade, and most importantly, if it was finalized.
Reply With Quote
  #18  
Old 1/4/09, 8:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by mtimpani View Post
Wow this is interesting info! How does the power company know that if the conductors were feeding a 60 amp breaker/service that when they switch the panel to a 300 amp service the wires wont burn up?

I wonder how come in this area they always switch the conductors when they go to a 200 service?
They have your power bill as history. Every area does it differently. A service upgrade doesn't necessarily trigger a change of the aerial drop.
Reply With Quote
  #19  
Old 1/4/09, 9:41 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by Marc D. Shunk View Post
They have your power bill as history. Every area does it differently. A service upgrade doesn't necessarily trigger a change of the aerial drop.
The vast majority of upgrades done here are for increased capacity such as for the addition of air conditioning unit(s) or additions to the structure, which would also require additional cooling. A 5 ton AC unit would certainly increase the load, no?

I find it hard to believe that a POCO would actually review past usage to determine if a bigger drop is needed.

I work with the local POCO where the Mark's client is located and I can say without a doubt that if there is a 200 amp main under that mast then something went wrong, a bigger triplex should have been brought in.
Reply With Quote
  #20  
Old 1/5/09, 9:51 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Larger wires at service drop

This is the split buss panel.
Attached Thumbnails
larger-wires-service-drop-100_2565-800x600-.jpg  




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #21  
Old 1/5/09, 10:55 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Well Mark we can't see the bus rating from here, but if it were ME I would go with the weakest link and call it a 100 amp service due to the #2 drop.

Did you catch the 6 dissconnect violation?
Reply With Quote
  #22  
Old 1/5/09, 8:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by brian winkle View Post
Well Mark we can't see the bus rating from here, but if it were ME I would go with the weakest link and call it a 100 amp service due to the #2 drop.
...and you'd have no basis on which to make that claim.
Reply With Quote
  #23  
Old 1/5/09, 9:38 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by Marc D. Shunk View Post
...and you'd have no basis on which to make that claim.

Could you please explain? And how should he call it?
Reply With Quote
  #24  
Old 1/5/09, 10:00 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by brian winkle View Post
Could you please explain? And how should he call it?
He shouldn't. There's nothing wrong.
Reply With Quote
  #25  
Old 1/5/09, 10:54 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by Marc D. Shunk View Post
He shouldn't. There's nothing wrong.
I didn't mean to imply there was anything wrong, except for the six disco rule,
I meant what size should he/would you call the service?

Last edited by brian winkle; 1/5/09 at 10:58 PM..
Reply With Quote
  #26  
Old 1/6/09, 1:40 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by brian winkle View Post
I meant what size should he/would you call the service?
If the aerial drop is the only thing you think makes this a 100 amp (it doesn't), then this is a 200 amp service. Only consider items from the point of attachment inward. Seriously, how far back are you going to go? Check the transformer on the pole? Gauge of the primary loop feed? Substation capacity? Certainly not.

Even in the extreme example below, this is still probably a 1600 amp service:


Last edited by Marc D. Shunk; 1/6/09 at 1:49 AM..
Reply With Quote
  #27  
Old 1/6/09, 10:16 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Larger wires at service drop

The breaker that was labeled "main" and had the wires running down to the bottom breakers was 60 amp.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #28  
Old 1/7/09, 9:59 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Larger wires at service drop

How far can it go? Can it go from 60a to 300amp?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #29  
Old 1/7/09, 6:51 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Larger wires at service drop

Quote:
Originally Posted by mtimpani View Post
How far can it go? Can it go from 60a to 300amp?
They probably would never do that, but the NESC rules are so complex that you could probably get away with that easily. They take into account the span, ice and wind loading, average design temperature, demand load, insulation type, etc. They don't really have a table like the NEC has to look things up in. It's a pretty complex calculation. The power companies do have rules of thumb the linemen work by, but in not every case do they change the aerial drop, nor are they specially obligated to by any rule or law.
Reply With Quote
  #30  
Old 1/8/09, 9:41 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Larger wires at service drop

How come the wires don't burn up?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Mention voltage drop? dbucknavich Electrical Inspections 18 6/18/08 7:58 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 3:40 PM
Service Drop Was Finally Removed! jtedesco1 Electrical Inspections 1 12/1/06 3:40 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 3:49 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts