Default Laundry room, wash tub receptacle

Scenario: Laundry room with washing machine and wash tub with small counter space. The washer is on one dedicated outlet but that is the only outlet in entire laundry room. Home built in 2009.

Questions: Is another receptacle required in a laundry room if a wash tub with small counter exists?

Since the washer dedicated outlet is within the 6' arc, should I assume that it should be changed to a GFCI protected duplex.?


I know NEC 210.8 states that all receptacles should be GFCI for any receptacle within 6' arc. But there is no accessible receptacle in the laundry room besides the dedicated washer outlet.

Thanks in advance!



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/28/10, 6:50 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Laundry room, wash tub receptacle

Yes, GFCI protection is required within 6' of the laundry sink. Here are the requirements for a laundry receptacle in the 2008 NEC:

Quote:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

210.8(A)(7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink
Quote:
210.52(F) Laundry Areas. In dwelling units, at least one receptacle outlet shall be installed for the laundry.
Exception No. 1: In a dwelling unit that is an apartment or living area in a multifamily building where laundry facilities are provided on the premises and are available to all building occupants, a laundry receptacle shall not be required.
Exception No. 2: In other than one-family dwellings where laundry facilities are not to be installed or permitted, a laundry receptacle shall not be required.
Quote:
210.11(C) Dwelling Units.
(1) Small-Appliance Branch Circuits. In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
(2) Laundry Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
Reply With Quote
  #3  
Old 11/10/10, 7:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Laundry room, wash tub receptacle

Now let me translate...lol......Yes if within 6' it has to be on GFCI.....No the single receptacle is all that is required .



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Laundry Room Wiring barena Electrical Inspections 4 2/15/10 10:00 PM
Duct from above furnace in laundry room..... shand Inspecting HVAC Systems 6 7/1/09 10:58 AM
Common wall of garage is Laundry room / firewall ? dnasser Interior Inspections 14 6/26/09 11:57 PM


All times are GMT -4. The time now is 8:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts