Please comment on this laundry room wiring...thanks.
|
| Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
I can't tell what the material is...
Did you take the pic? What is the material/conduit? How do you see it? InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
||||
|
||||
|
I might recommend GFCI.
Will let others comment on the conduit. |
|
#4
|
||||
|
||||
|
Is the conduit rated? What does the back of the box look like? Recommend GFCI.
Mid America Property Inspections, Inc. Shawnee, KS 66217 www.mapii.com NACHI # 05110992 KHIRB # 0110-0008 KS-Radon Cert.# KS-MS-0035 KS-Termite Cert. # 18933 M0-Termite Cert. # N 5033 |
|
#5
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like non-metallic flex conduit. Typically used for AC compressor wiring from the disconnect. Article 356 of the NEC covers this. I don't think it meets the uses permitted in 356.10, but also don't see it prohibited by 356.12.
Looks like the first strap is too far from the box too. If the receptacle is within 6' of a laundry tub it would require GFI under the 05 or later NEC. Last edited by Jim Port; 2/16/10 at 8:53 AM.. Reason: spelling |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Evaluating your home's wiring system | mcyr | Electrical Inspections | 0 | 12/30/09 1:31 PM |
| Duct from above furnace in laundry room..... | shand | Inspecting HVAC Systems | 6 | 7/1/09 10:58 AM |
| Common wall of garage is Laundry room / firewall ? | dnasser | Interior Inspections | 14 | 6/26/09 11:57 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |