Default Light Fixture above Jacuzzi w/ Shower Spray Nozzle

The attached light fixture is 35" above the jacuzzi tub. How would you write this up? Thanks very much.
Attached Thumbnails
light-fixture-above-jacuzzi-w-shower-spray-nozzle-march-04-2008-036.jpg  
Reply With Quote
  #2  
Old 3/4/08, 7:29 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

If the fixture is listed for a damp location of wet location if it is subject to shower spray then I wouldn't worry with writing it up as anything.
Reply With Quote
  #3  
Old 3/5/08, 7:29 PM
thance thance is offline
New User
 
Join Date: Sep 2007
Location: Eastsound, WA
Posts: 92
Please Note: thance is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

Thanks Mike.
Reply With Quote
  #4  
Old 3/5/08, 10:08 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

Sorry that should have been damp location OR wet location insetad of
damp location OF wet location
Reply With Quote
  #5  
Old 3/6/08, 12:22 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

Quote:
Originally Posted by thance
The attached light fixture is 35" above the jacuzzi tub. How would you write this up? Thanks very much.
Please review this rule from the NEC:

680.43 Indoor Installations

Last edited by jtedesco1; 3/6/08 at 7:57 AM..
Reply With Quote
  #6  
Old 3/6/08, 1:08 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

Joe,
Would that installation fall under Part IV or Part VII?

Is it a spa or hot tub or is it a hydromassage bathtub?

If it is a hydromassage bathtub then this is the rule for the light fixture;
680.72 Other Electrical Equipment.
Luminaires (lighting fixtures), switches, receptacles, and other electrical equipment located in the same room, and not directly associated with a hydromassage bathtub, shall be installed in accordance with the requirements of Chapters 1 through 4 in this Code covering the installation of that equipment in bathrooms.

From the picture it looks to me like it gets drained after each use and if it does then it is a;
Hydromassage Bathtub. A permanently installed bathtub equipped with a recirculating piping system, pump, and associated equipment. It is designed so it can accept, circulate, and discharge water upon each use.

I can't say for sure which it is and you may be right. I was only assuming based on the picture.
Reply With Quote
  #7  
Old 3/6/08, 2:01 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

I'm with Mike on this one. This is not a spa
Reply With Quote
  #8  
Old 3/6/08, 2:02 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

This will make it easier for a LICENSED CERTIFIED Home Inspector to see that the installation of the fixture in the picture above is illegal!

410.4(D)
Bathtub and Shower Areas No parts of cord-connected luminaires (fixtures), chain-, cable-, or cord-suspended-luminaires (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the zone directly over the tub or shower stall. Luminaires (lighting fixtures) located in this zone shall be listed for damp locations, or listed for wet locations where subject to shower spray.

Last edited by jtedesco1; 3/6/08 at 11:34 AM..
Reply With Quote
  #9  
Old 3/6/08, 7:43 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

LOL.

Thank you for illustrating for us why we should stay away from code references and interpretations.

As stated previously and demonstrated here, code "experts" rarely agree and the many, many variables make it impractical for a home inspector to attempt to reference it in his report.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #10  
Old 3/6/08, 12:04 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

This is a hydromassage tub. It is not a spa or hot tub.

The fixture's installation appears to be unsatisfactory. Refer this for further evaluation and corrective action by a licensed electrical contractor.

It is not "illegal". No one is going to jail, and the house can still be sold "as is".

It was simply not installed in compliance with a portion of the electrical code, and is hazardous.

Nothing the inspector comments during an inspection will effect the transferrability of the dwellng in question. The client may accept that the installation is unsatisfactory. Referecing an electrical code DOES NOT help the client, other than point him to verbiage that is often confusing.

You say that it is unsatisfactory, and do so in clear, non-confusing terms that everyone can understand.

Heres the problem with referring to Joe' T's code clip:

Quote:
No parts of cord-connected luminaires (fixtures), chain-, cable-, or cord-suspended-luminaires (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold.
It aint a cord-connected fixture.
It aint a chain, cable, or cord-suspended fixture.
It aint a lighting track.
It aint a paddle fan.
Does it qualify as a pendant?

If so, the rule applies. If not, this portion of the code doesnt fit. The last sentance, with regard to properly rated fixtures does. We could add to our commentary somethng like 'It does not appear that the wall fixture is rated for damp or wet locations".

Last edited by jfarsetta; 3/6/08 at 12:11 PM..
Reply With Quote
  #11  
Old 3/6/08, 12:16 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

See the image here for the restriction.

Last edited by jtedesco1; 6/12/08 at 4:38 PM..
Reply With Quote
  #12  
Old 3/6/08, 3:29 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

Quote:
Originally Posted by jtedesco1
See the image here for the restriction.
From this illustration that clearly shows an example of the the luminary {on the right side} it seems quite clear that you are correct.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #13  
Old 3/6/08, 4:05 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

To me the illustration in post #11 is the same thing as the image in post #1.

I say code compliant, but a dumb installation.

That IS, by the way, an outdoor fixture.

Shower spray? Who knows. At this point I'd say no.
Reply With Quote
  #14  
Old 3/6/08, 4:42 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

I wouldn't do an installation like that on my own volition. If a customer asked for it to be done that way, from what I can see from the picture, I'd be hard pressed to give them a code reason why I couldn't do it that way. This is another case of "legal, but dumb".
Reply With Quote
  #15  
Old 3/6/08, 5:29 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Light Fixture above Jacuzzi w/ Shower Spray Nozzle

Quote:
Originally Posted by fcarrio
From this illustration that clearly shows an example of the the luminary {on the right side} it seems quite clear that you {Joe Tedesco} are correct.
In his original post Tim states that this light is just 35-inches above the bathtub / Jacuzzi.

The Graphic that Joe T. provided illustrates the following code that stipulates that this type of "luminary" has to be at least 8-feet above the bathtub.



Quote: Joe Tedesco
410.4(D)
Bathtub and Shower Areas:
No parts of cord-connected luminaries (fixtures), chain-, cable-, or cord-suspended-luminaries (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold.
  • This zone is all encompassing and includes the zone directly over the tub or shower stall.
Luminaries (lighting fixtures) located in this zone shall be listed for damp locations, or listed for wet locations where subject to shower spray
End Quote:
  • IMO the Code and the Graphic clearly illustrates that this installation is not code complaint.... or.... am I missing something here?
.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Trouble Shooting the Simple Light Bulb mcyr Electrical Inspections 20 1/6/08 3:47 AM
Light fixture in shower pdickerson Electrical Inspections 18 10/18/07 6:34 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 9:56 AM
Light Fixture above shower tneumann Electrical Inspections 27 3/11/06 11:03 AM


All times are GMT -4. The time now is 4:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts