Default Light Fixture above shower

Hate to start this debate again...and I don't care too much about code...but I do care about safety

This doesn't seem safe to me....the angle of the pic could have been better, but this fixture is directly above the shower.....granted the actual light fixture is not...but the ceiling box is...and no caulk or waterproofing of any kind.....

I am going to write it up as a safety issue...and help on the wording would be appreciated.

Thanks
Attached Thumbnails
light-fixture-above-shower-1413sanderson-066.jpg  
Reply With Quote
  #2  
Old 3/9/06, 7:03 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,091
Default Re: Light Fixture above shower

Tony,
You won't get any debate from me. That's got to go.
Reply With Quote
  #3  
Old 3/9/06, 7:58 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above shower

Doesn't look like a light fixture for a bathroom.
Reply With Quote
  #4  
Old 3/9/06, 8:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Light Fixture above shower

Unlisted electrical outlet within the plane of the shower enclosure is a potential safety hazard. Recommend correction by qualified electrician.

Then you can explain the difference between outlets and receptacles.

Last edited by lkage; 3/9/06 at 8:36 PM..
Reply With Quote
  #5  
Old 3/9/06, 9:14 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Light Fixture above shower

"Unlisted electrical outlet within the plane of the shower enclosure is a potential safety hazard. Recommend correction by qualified electrician."

What I would say. Pass off the liability to an electrician. Let them explain to a judge that it was no problem. "But you honor, it was code."

Take upon yourself your client's liability and pass it back to those who deserve it.

My motto.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 3/9/06, 9:22 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Light Fixture above shower

Quote:
Originally Posted by wdecker
Take upon yourself your client's liability and pass it back to those who deserve it.

My motto.
I like that...simple.
Reply With Quote
  #7  
Old 3/9/06, 10:58 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Fixture above shower

Yeppers. Not allowed but just in case you DO want code...lol...view Art 410.4(D).....anyway does not matter Tony if it is off to the side or not as it is within the 3' area of the tub and not allowed and yes is a safety issue you can write up.



Part II. Luminaire Locations


The text was modified to clarify the types of luminaires not permitted within 3 ft horizontally and 8 ft vertically from the top of the bathtub rim or shower stall. And new rule requires luminaires in bathtub or shower zone to be listed for damp locations, or listed for wet locations where subject to shower spray.
(D) Above Bathtubs. No part of chain-, cable-, or cord luminaires, track lighting, or ceiling paddle fans is permitted to be located within 3 ft horizontally and 8 ft vertically from the top of the bathtub rim or shower stall threshold (bathtub/shower luminaire zone).

Author’s Comment: The 3 ft by 8 ft bathtub/shower luminaire zone does not apply to recessed or surface mounted luminaires, switches, or receptacles. See 404.4 for switch requirements and 406.8(C) for receptacle requirements.

Luminaires located in bathtub and shower zone must be listed for damp locations, or listed for wet locations where subject to shower spray.

Courtesy Mike Holt Enterprises




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 3/9/06, 11:07 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above shower

All the above and it looks as though that is a detachable shower head that can be inadvertently pointed up and spray the fixture.

Steve
Reply With Quote
  #9  
Old 3/9/06, 11:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Fixture above shower

Damn I have no idea why so many people are anti-Code.....good lord people...the CODE is about safety even at a minimum.

Stop fighting it and embrace it...GESSSHHH...Hell I do BOTH and I have no problem embracing it.....

The reason some of us post CODE is to not just say WHY it is not allowed...you need SOME FORM OF RECOGNITION to understand why and the code simply BACKS YOU UP on your safety call.....GESSSHHHH

I mean...My Lord......just because someone posts CODE to explain something does not mean you dont have enough common sense to NOT quote it in your report.....thats not OUR fault if you can't define the two.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 3/9/06, 11:17 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Light Fixture above shower

I embrace code. I even read it to put myself to sleep after too many margaritas. However, I don't cite code in my reports because my E&O insurance does not cover me for citing code.
Reply With Quote
  #11  
Old 3/9/06, 11:20 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Fixture above shower

Thats what I am saying.....Just because Electricians and Others like myself explain some issues using code examples....does not mean a HI is supposed to quote it...it is for the LEARNING experience only......GESSSHHH...

I think some people on here think just because we use it as a teaching tool that it has to be quoted in a report...hell you can sign your reports with the name Jimmy Hoffa for all I care......we only use code here sometimes to show examples of safety issues the NFPA and NEC have already uncovered and why the code book was written...

Anyway.......I don't care.......I do home inspections as well and I never quote any code......but I also do Code Inspections where I HAVE to quote code.....either way...I know how to turn either one on and off.....I am guessing some others do not......which is why some members have Code-Phobia



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 3/9/06, 11:49 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Light Fixture above shower

And that's why I don't mind at all reading the technical posts by the Abernathys and Tedescos of the world. I learn, yet I'm intelligent enough to know what to use and what to keep in my head as the basis for my business.
Reply With Quote
  #13  
Old 3/9/06, 11:54 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Fixture above shower

I don't mind you guys quoting code either....BUT...because I did a search of this topic prior to posting it....I was privvy to the pissing match that ensued another time when this was brought up....and wanted to avoid it if I could....don't stop what you do Paul.....!
Reply With Quote
  #14  
Old 3/10/06, 12:00 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Light Fixture above shower

Deal killers.
Reply With Quote
  #15  
Old 3/10/06, 12:09 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Fixture above shower

lol...Oh Brian.....lol.......tehhehe

Naw.......when I teach seminars to home inspectors I do not bring up code hardly at all...the only time It is used here on the boards is to try and define a point...I will never just post code and RUN......I always try to give a personal slant or view on the subject so that HI's can relate....thats important to me.......I just think CODE happens to be an important part of my foundation as an HI....

If you ask 90% of the HI clients out their what your job is I can almost guarantee they say to enforce the codes or something like that.....they are wrong...BUT if the HI does not spend a little time in their profession learning some of them....why do it at all.....we learn something NEW everyday.

People just have to learn to take with them what they can use and leave what they can't where it was learned...here on the boards....again just because every now and then code is posted....thats for educational purposes to explain a point...not to tell you to quote code....thats all....

I'm done with my little rant on the subject now..unless it just can't rest...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light fixture in shower pdickerson Electrical Inspections 18 10/18/07 7:34 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 8:22 PM
Shower Light mmasney Electrical Inspections 9 2/11/07 12:00 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 10:56 AM
Outdoor light fixture bsmith Electrical Inspections 4 3/22/06 10:48 PM


All times are GMT -4. The time now is 8:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts