Old 2/12/06, 4:51 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
Default Light switch where entering a room.
The only switch when you walk into this room (from outside) operates the breezeway light. I told the builder that lights within the room should be operable when entering the room from outside (not walk across to the opposite wall to do so)
I anticipate a request for some "code" type reference... anyone? Bueller?
- Mike
Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com
(843) 442-9755
Charleston Home Inspector
Old 2/12/06, 5:15 PM
Joseph Hagarty,  CMI's Avatar
Default Re: Light switch where entering a room.
NEC 2002
210.70 Lighting Outlets Required.
Lighting outlets shall be installed where specified in 210.70(A), (B), and (C).
(A) Dwelling Units.
In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (2), and (3).
(1) Habitable Rooms.
At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Exception No. 2: Lighting outlets shall be permitted to be controlled by occupancy sensors that are (1) in addition to wall switches or (2) located at a customary wall switch location and equipped with a manual override that will allow the sensor to function as a wall switch.
(2) Additional Locations.
Additional lighting outlets shall be installed in accordance with (a), (b), and (c).
(a) At least one wall switch-controlled lighting outlet shall be installed in hallways, stairways, attached garages, and detached garages with electric power.
(b) For dwelling units, attached garages, and detached garages with electric power, at least one wall switch
controlled lighting outlet shall be installed to provide illumination on the exterior side of outdoor entrances or exits with grade level access. A vehicle door in a garage shall not be considered as an outdoor entrance or exit.
(c) Where one or more lighting outlet(s) are installed for interior stairways, there shall be a wall switch at each
floor level, and landing level that includes an entry way, to control the lighting outlet(s) where the stairway between floor levels has six risers or more.
Exception to (a), (b), and (c): In hallways, stairways, and at outdoor entrances, remote, central, or automatic control of lighting shall be permitted.
FYI: I am not aware of a NEC requirement as to where the switch is located.
Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net
Old 2/12/06, 5:16 PM
Joe Funderburk, CMI's Avatar
I generally don't make definitive statements on the job site about something I'm not sure about. As Samuel Clemmons said, "better to keep quite and look stupid than open your mouth and remove all doubt." I go home and research it first--that's why I don't do onsite reports. I like the time to think things over and research things I'm not sure about; nobody knows all the various codes.
Personally, unless it's a brand new house or there is some safety hazard, I wouldn't give your situation second thought--we aren't code enforcers anyway.
As to the specifics of your question, let's see. I don't know either.
Theodore Roosevelt
Joe Funderburk, CMI
NACHI ID: NACHI05120170
www.aohomeinspection.com
Old 2/12/06, 5:36 PM
It is brand new.
Won't close till the end of the month.
When I say the 'Builder' I mean the "in charge" guy there on Sunday morning overseeing the other two guys there (actual "Builder" site rep will be there tomorrow).
No report given yet, this was a walk through for a neighbor...
I've just never seen a door from which you can enter a room from outside and not have a wall switch to that rooms interior lights readily accessible...
In this particular room, you enter, walk across a 14.5 foot room to the opposite wall to access the light switch...
Mayhap I'm just naive
- Mike
NACHI05040682
(843) 442-9755
Old 2/12/06, 5:38 PM
Originally Posted by jhagarty
NEC 2002
Maybe "at outdoor entrances" is inferred here?
- Mike
NACHI05040682
(843) 442-9755
Old 2/12/06, 5:41 PM
[/left]
Nope.
Phone: 610-399-3675
Old 2/12/06, 6:29 PM
Michael R. Boyett's Avatar
This was discussed several times last year on the old board. You might do a search there but, if memory serves, then you'll not find any 'code' references to support the idea of a switch by the door. I had one last year in a utility room that was actually behind the door, i.e. you had to close the door in the dark to get to the switch.
Old 2/12/06, 6:41 PM
Paul W. Abernathy's Avatar
Actually this is correct.....the NEC does not mandate that the switch MUST be on the doorknob side of the swinging door per se.....just that a switched outlet ( ie : Light or Recept. ) has to be present in certain locations....
The CODE contains the requirement for the location of the lighting outlet, but does no specify the location for the switch. Naturally, you would not want to isntall a switch behind a door or other inconvient location, but the CODE does not require you to relocate the switch to suit the swing of the door. When in doubt as to the best location to place a light switch...if you do not know where the best location is.....make a friend..ask the AHJ...
Paul W. Abernathy,CMI,CPI,CME
Old 2/12/06, 9:03 PM
Robert J. OConnor's Avatar
This topic has been kicked around before on the boards, and I believe the end result was there is no code requirement for a switch to be in a room it services. However, codes are concerned with minimal safety, and not convenience or functionality.
As an HI there is no reason you can't write that issue up as a concern (or defect, but thats a little strong in my book), as HI's are not limited to commenting on strictly code related issues.
JMO & 2-nickels ...
Robert O'Connor, PE
LIU CW Post Adjunct Professor
www.reporthost.com/-rjo
Old 2/12/06, 11:01 PM
I'll just say it's stupid (a concern, an inconvienience, or the like) and if the HO want's to let it stay, oh well...
I'd certainly holler to get a switch there...
- Mike
NACHI05040682
(843) 442-9755
Old 2/12/06, 11:09 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
JMO & 2-nickels ...
same as if the tread and rise of stairs varies in the same flight, but stays within the min-max. it's not any violation, but might be erginomicly uncomfortable and note worthy.
Old 11/15/07, 2:07 PM
Scott C. LeMarr Scott C. LeMarr is offline
While we are on the subject of light switches, I have seen two bathrooms with the light switch is on the outside of the room. I can't find any information where this is restricted but seems like it could be a safety hazard if someone were to turn the switch off while someone was in the bathroom.
Comments?
Old 11/15/07, 6:03 PM
Barry Adair's Avatar
Michael,
option #2 if all else fails
Scott,
only when shaving the jewels
ADAIR INSPECTION
972-487-5634
TREC # 4563
EDI: EIFS-MA TX # 39
2008 US Member of the Year
Old 11/15/07, 7:09 PM
gbeaumont's Avatar
Originally Posted by badair
Scott,
way to much information there, you just ruined my supper
Regards
Gerry
(Mark B Adams)
NACHI cell 484-429-5466
NACHI02121106
Old 11/15/07, 7:15 PM
Regards
Gerry
Sorry mate, I'll save my bits for pre-tea
ADAIR INSPECTION
972-487-5634
TREC # 4563
Bathroom light switch question Jim White, #3 Electrical Inspections 2 10/16/07 4:21 PM
Need help.What type of light switch is this ? dnasser Electrical Inspections 3 10/7/07 3:41 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 8:22 PM
Warm Light Switch Cover cpennick General Inspection Discussion 11 11/23/06 12:05 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 10:56 AM