Default Light Switch Near Shower

It's my understanding the NEC is not very clear on these applications. Would you comment on this and what verbiage would you use?
Attached Thumbnails
light-switch-near-shower-100_5272.jpg  



Vince Santos
StepByStep Home Services LC
(734) 748-9584
Providing Home Inspection Services to Southeast Michigan
facebook
ITA Trained and Certified

Reply With Quote
Find an InterNACHI certified Missouri Home Inspector (and anywhere else in North America)
  #2  
Old 6/9/09, 3:47 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Light Switch Near Shower

Sure it is. There's nothing to comment about.

NEC 404.4 Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

These switches are clearly outside of the "shower space."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/9/09, 3:57 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Switch Near Shower

Jeff has it summed up right there. As long as you are outside the footprint, even by 1/16", you are code compliant.
Reply With Quote
  #4  
Old 6/9/09, 3:58 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Light Switch Near Shower

Since we are becoming responsible for cradle to grave service for our clients...

"Dry your hands before touching these switches lest the grave portion of our service will come sooner than you may wish"..

Nothing to write up about them otherwise, as Jeff said.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #5  
Old 6/9/09, 5:34 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Light Switch Near Shower

Do they run through the GFCI?
Might be a good idea
Reply With Quote
  #6  
Old 6/9/09, 8:29 PM
Tim C. Howell Tim C. Howell is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: New Liberty, IA
Posts: 85
Default Re: Light Switch Near Shower

I thought the switch had to be a minimum 3' from the shower. Recommend GFCI / evaluation by an electrican
Reply With Quote
  #7  
Old 6/9/09, 9:30 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Switch Near Shower

Tim...I believe that is in Canada but not in the US.



Paul W. Abernathy
Reply With Quote
  #8  
Old 6/9/09, 9:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Light Switch Near Shower

Quote:
Originally Posted by thowell View Post
I thought the switch had to be a minimum 3' from the shower. Recommend GFCI / evaluation by an electrican
What is there to "evaluate?"



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 6/10/09, 2:26 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Light Switch Near Shower

Quote:
Originally Posted by vsantos View Post
It's my understanding the NEC is not very clear on these applications. Would you comment on this and what verbiage would you use?
Vincent,
Here are some graphics on light fixtures that you might find useful.
Attached Thumbnails
light-switch-near-shower-bath-elect.jpg   light-switch-near-shower-bathroom_fixture1.jpg  



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #10  
Old 6/10/09, 9:27 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Light Switch Near Shower

Quote:
Originally Posted by fcarrio View Post
Vincent,
Here are some graphics on light fixtures that you might find useful.
Never knew the 8 foot rule.
Good illustration if still up to date.
Reply With Quote
  #11  
Old 6/11/09, 2:47 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Light Switch Near Shower

Quote:
Originally Posted by relliott View Post
Never knew the 8 foot rule.
Good illustration if still up to date.
Hi Robert,


Your question as to whether or not this graphic was "still good" prompted me to do a lot, and I mean a lot of research.
  • I have found that information still valid.
I've gone out of my way to research the "electrical section" of the International Residential Code to look for "switches, receptacles, and luminaries" in damp/wet locations.

Here's what I found and I hope it is of some use.

Please feel free to add it to your "database".

International Residential Code

SECTION E3603
REQUIRED BRANCH CIRCUITS
E3603.4 Bathroom branch circuits.
A minimum of one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception:
Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with Section E3602.

E3605.7 Location of overcurrent devices in or on premises.
Overcurrent devices shall:

LOCATION, WET.
Installations underground or in concrete slabs or masonry in direct contact with the earth and locations subject to saturation with water or other liquids, such as vehicle-washing areas, and locations exposed to weather.
{This also includes swimming pools, Jacuzzi's, hot tubs, "regular tubs", sinks, showers and basins.}

Chapter 38 Power and Lighting Distribution
Section E. 3801, Receptacle Outlets

E3801.6 Bathroom.
At least one wall receptacle outlet shall be installed in bathrooms and such outlet shall be located within 36 inches (914 mm) of the outside edge of each lavatory basin. The receptacle outlet shall be located on a wall that is adjacent to the lavatory basin location.
Receptacle outlets shall not be installed in a face-up position in the work surfaces or countertops in a bathroom basin location.
Exception:
The receptacle shall not be required to be mounted on the wall or partition where it is installed on the side or face of the basin cabinet not more than 12 inches (300 mm) below the countertop.

SECTION E3802
GROUND-FAULT AND ARC-FAULT
CIRCUIT-INTERRUPTER PROTECTION
E3802.1 Bathroom receptacles.
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in bathrooms shall have ground-fault circuit-interrupter protection for personnel.

SECTION E3803
LIGHTING OUTLETS
E3803.1 General.
Lighting outlets shall be provided in accordance with Sections E3803.2 through E3803.4.

E3803.2 Habitable rooms.
At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.

Not be located in bathrooms.

CHAPTER 39
DEVICES AND LUMINARIES SECTION E3901 SWITCHES
E3901.7 Wet locations.
A switch or circuit breaker located in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly. {IE manufactured "watertight/water resistant" specifically for the installed unit.}

WATERTIGHT.
So constructed that moisture will not enter the enclosure under specified test conditions.
{NOTE:
Some luminaries are "waterproof/watertight" and are constructed/manufactured specifically for the use in "wet locations" such as within 36 inches of a tub, shower, or Jacuzzi.}

BATHROOM.
An area, including a basin, with one or more of the following: a toilet, a tub or a shower.

SECTION E3902
RECEPTACLES
E3902.11 Bathtub and shower space.
A receptacle shall not be installed within or directly over a bathtub or shower stall.

SECTION E3903
FIXTURES
E3903.8 Wet or damp locations.
Luminaries installed in wet or damp locations shall be installed so that water cannot enter or accumulate in wiring compartments, lampholders or other electrical parts. All luminaries installed in wet locations shall be marked SUITABLE FOR WET LOCATIONS. All luminaries installed in damp locations shall be marked SUITABLE FOR WET LOCATIONS or SUITABLE FOR DAMP LOCATIONS.

E3903.9 Lampholders in wet or damp locations.
Lampholders installed in wet or damp locations shall be of the weatherproof type.

E3903.10 Bathtub and shower areas.
Cord-connected luminaries, chain-, cable-, or cord-suspended-luminaries, lighting track, pendants, and ceiling-suspended (paddle) fans shall not have any parts located within a zone measured 3 feet (914 mm) horizontally and 8 feet (2438 mm) vertically from the top of a bathtub rim or shower stall threshold.
This zone is all encompassing and includes the zone directly over the tub or shower. Luminaries located in this zone shall be listed for damp locations and where subject to shower spray, shall be listed for wet locations.

SECTION E3905
TRACK LIGHTING
E3905.4 Prohibited locations.
Lighting track shall not be installed in the following locations:
1. Where likely to be subjected to physical damage.
2. In wet or damp locations.

Once again, I hope this information can be useful to some or all of you.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #12  
Old 6/11/09, 6:00 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Light Switch Near Shower

That's great info Frank(thanks for your research) but none of it applies to Vince's original question of a light switch near the shower bay.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #13  
Old 6/11/09, 7:00 AM
bemelander bemelander is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Grand Rapids, MI
Posts: 341
Default Re: Light Switch Near Shower

The switch in Vince's picture is OK and as Jeff said there is nothing to comment about.



Bill Emelander
Professional Edge Home Inspection
Grand Rapids and all of West Michigan
NACHI #03111914
www.proedgehi.com
Reply With Quote
Find an InterNACHI certified Missouri Home Inspector (and anywhere else in North America)
  #14  
Old 6/11/09, 8:07 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mlarson View Post
That's great info Frank(thanks for your research) but none of it applies to Vince's original question of a light switch near the shower bay.
Does it look like this light switch is within the 36-inch "wet zone" or within 36-inches from the outside edge of the shower?

CHAPTER 39
DEVICES AND LUMINARIES SECTION E3901 SWITCHES
E3901.7 Wet locations.
A switch .... or circuit breaker located in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet. Switches...... shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
{IE manufactured "watertight/water resistant" specifically for the installed unit.}



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096

Last edited by fcarrio; 6/11/09 at 8:15 PM..
Reply With Quote
  #15  
Old 6/11/09, 9:06 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Switch Near Shower

Frank,

How would you consider that a wet location? It is outside the footprint of the drained area of the shower pan. I also scanned the code sections posted by you and did not see any mention of the 3' distance regarding switches.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering CFL jallingham Electrical Inspections 34 12/5/08 2:40 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical Inspections 20 1/6/08 3:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 3:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 9:56 AM


All times are GMT -4. The time now is 4:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts