It's my understanding the NEC is not very clear on these applications. Would you comment on this and what verbiage would you use?
Vince Santos
Owner / Certified Home Inspector StepByStep Home Services LC (734) 748-9584 http://www.stepbystepinspections.com Providing Home Inspection Services to Southeast Michigan Active Rain blog http://activerain.com/sbsinspections ITA Trained and Certified Reg104669Cc |
| Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Sure it is. There's nothing to comment about.
NEC 404.4 Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly. These switches are clearly outside of the "shower space." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff has it summed up right there. As long as you are outside the footprint, even by 1/16", you are code compliant.
|
|
#4
|
|||
|
|||
|
Since we are becoming responsible for cradle to grave service for our clients...
"Dry your hands before touching these switches lest the grave portion of our service will come sooner than you may wish".. Nothing to write up about them otherwise, as Jeff said. |
|
#5
|
||||
|
||||
|
Do they run through the GFCI?
Might be a good idea |
|
#6
|
|||
|
|||
|
I thought the switch had to be a minimum 3' from the shower. Recommend GFCI / evaluation by an electrican
|
|
#7
|
||||
|
||||
|
Tim...I believe that is in Canada but not in the US.
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
||||
|
||||
|
What is there to "evaluate?"
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Quote:
Here are some graphics on light fixtures that you might find useful. Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member |
|
#10
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Good illustration if still up to date. |
|
#11
|
||||
|
||||
|
Quote:
Your question as to whether or not this graphic was "still good" prompted me to do a lot, and I mean a lot of research.
Here's what I found and I hope it is of some use. Please feel free to add it to your "database". International Residential Code SECTION E3603 REQUIRED BRANCH CIRCUITS E3603.4 Bathroom branch circuits. A minimum of one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets. Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with Section E3602. E3605.7 Location of overcurrent devices in or on premises. Overcurrent devices shall: LOCATION, WET. Installations underground or in concrete slabs or masonry in direct contact with the earth and locations subject to saturation with water or other liquids, such as vehicle-washing areas, and locations exposed to weather. {This also includes swimming pools, Jacuzzi's, hot tubs, "regular tubs", sinks, showers and basins.} Chapter 38 Power and Lighting Distribution Section E. 3801, Receptacle Outlets E3801.6 Bathroom. At least one wall receptacle outlet shall be installed in bathrooms and such outlet shall be located within 36 inches (914 mm) of the outside edge of each lavatory basin. The receptacle outlet shall be located on a wall that is adjacent to the lavatory basin location. Receptacle outlets shall not be installed in a face-up position in the work surfaces or countertops in a bathroom basin location. Exception: The receptacle shall not be required to be mounted on the wall or partition where it is installed on the side or face of the basin cabinet not more than 12 inches (300 mm) below the countertop. SECTION E3802 GROUND-FAULT AND ARC-FAULT CIRCUIT-INTERRUPTER PROTECTION E3802.1 Bathroom receptacles. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in bathrooms shall have ground-fault circuit-interrupter protection for personnel. SECTION E3803 LIGHTING OUTLETS E3803.1 General. Lighting outlets shall be provided in accordance with Sections E3803.2 through E3803.4. E3803.2 Habitable rooms. At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom. Not be located in bathrooms. CHAPTER 39 DEVICES AND LUMINARIES SECTION E3901 SWITCHES E3901.7 Wet locations. A switch or circuit breaker located in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly. {IE manufactured "watertight/water resistant" specifically for the installed unit.} WATERTIGHT. So constructed that moisture will not enter the enclosure under specified test conditions. {NOTE: Some luminaries are "waterproof/watertight" and are constructed/manufactured specifically for the use in "wet locations" such as within 36 inches of a tub, shower, or Jacuzzi.} BATHROOM. An area, including a basin, with one or more of the following: a toilet, a tub or a shower. SECTION E3902 RECEPTACLES E3902.11 Bathtub and shower space. A receptacle shall not be installed within or directly over a bathtub or shower stall. SECTION E3903 FIXTURES E3903.8 Wet or damp locations. Luminaries installed in wet or damp locations shall be installed so that water cannot enter or accumulate in wiring compartments, lampholders or other electrical parts. All luminaries installed in wet locations shall be marked SUITABLE FOR WET LOCATIONS. All luminaries installed in damp locations shall be marked SUITABLE FOR WET LOCATIONS or SUITABLE FOR DAMP LOCATIONS. E3903.9 Lampholders in wet or damp locations. Lampholders installed in wet or damp locations shall be of the weatherproof type. E3903.10 Bathtub and shower areas. Cord-connected luminaries, chain-, cable-, or cord-suspended-luminaries, lighting track, pendants, and ceiling-suspended (paddle) fans shall not have any parts located within a zone measured 3 feet (914 mm) horizontally and 8 feet (2438 mm) vertically from the top of a bathtub rim or shower stall threshold. This zone is all encompassing and includes the zone directly over the tub or shower. Luminaries located in this zone shall be listed for damp locations and where subject to shower spray, shall be listed for wet locations. SECTION E3905 TRACK LIGHTING E3905.4 Prohibited locations. Lighting track shall not be installed in the following locations: 1. Where likely to be subjected to physical damage. 2. In wet or damp locations. Once again, I hope this information can be useful to some or all of you. ![]()
Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member |
|
#12
|
||||
|
||||
|
That's great info Frank(thanks for your research) but none of it applies to Vince's original question of a light switch near the shower bay.
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#13
|
|||
|
|||
|
The switch in Vince's picture is OK and as Jeff said there is nothing to comment about.
Bill Emelander Professional Edge Home Inspection Serving West Michigan NACHI #03111914 www.proedgehi.com |
| Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
Quote:
![]() CHAPTER 39 DEVICES AND LUMINARIES SECTION E3901 SWITCHES E3901.7 Wet locations. {IE manufactured "watertight/water resistant" specifically for the installed unit.} Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member Last edited by fcarrio; 6/11/09 at 9:15 PM.. |
|
#15
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Frank,
How would you consider that a wet location? It is outside the footprint of the drained area of the shower pan. I also scanned the code sections posted by you and did not see any mention of the 3' distance regarding switches. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Flickering CFL | jallingham | Electrical | 34 | 12/5/08 3:40 PM |
| Trouble Shooting the Simple Light Bulb | mcyr | Electrical | 20 | 1/6/08 4:47 AM |
| End of the light bulb as we know it!! | mcyr | General Inspection Discussion | 3 | 12/19/07 4:42 PM |
| Light Bulbs- All Ya Wanna Know | pabernathy | Electrical | 9 | 4/18/07 8:22 PM |
| How many forum members to change a light bulb? | kshepard | Misc. Discussion | 9 | 8/2/06 10:56 AM |