  #151  
Old 6/19/09, 5:01 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Light Switch Near Shower

Quote:
Originally Posted by jfarsetta View Post
No.

Absolutely the single most horrifying photo to ever disgrace this message board was a former electrical contributor and self-appointed authority on all things electrical, wearing an electric blue sequened evening dress, complete with high heels, nylon stockings, wig, false eyelashes, lipstic, and make-up.

I still have nightmares...

Who remembers what I speak of? How long have you all been InterNACHI members?
Joe,

You have E-mail.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #152  
Old 6/20/09, 1:48 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Light Switch Near Shower

Quote:
Originally Posted by gromicko View Post
If it was my shower stall and I had kids, I'd install a GFCI on the switch circuit before I installed a Water-Pik. Call me nuts.
Ok....your NUTS...lol

Actually as I told you at dinner the other night. If an HI is concerned over this situation they can always recommend the circuit to be protected by GFCI , Clearly, everyone has different opinions of it but rather than FLAME it as a defect that could come back to haunt an HI....recommend a positive solution at a reasonable cost and tell them they may want to protect it with GFCI....and it will help some sleep at night but again NO ONE has found any documentation of the condition causing an electrical hazard.

Look......as you remember today.....I sat on your toilet, dangled my hands in the sink while the water was running and with the other hand flicked your bathroom lights on and off........over and over again and you notice I was not shocked.....fact is you have a better chance at winning the lotto than it really being a problem.

But to each his own....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #153  
Old 6/22/09, 10:56 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: Light Switch Near Shower

Quote:
Originally Posted by jfarsetta View Post

Who remembers what I speak of? How long have you all been InterNACHI members?
I had that picture out of my head until today, thanks for the awful memory. I think he was mixed up and posted the pic on the wrong website. InterNACHI.org and trollingforguys.com could easily be mixed up as the spelling is similiar???



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #154  
Old 6/22/09, 4:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Light Switch Near Shower

I kinda liked that image of me in a pink speedo....I shed like 150 pounds in a click of a shutter....lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #155  
Old 6/22/09, 4:41 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,826
Send a message via AIM to sstanczyk
Default Re: Light Switch Near Shower

Quote:
Originally Posted by pabernathy View Post
I kinda liked that image of me in a pink speedo....I shed like 150 pounds in a click of a shutter....lol
In order to keep this thread from drifting too far, the question is:

When this photo was taken, were you really testing switches?

light-switch-near-shower-paul-testing-switches.jpg




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #156  
Old 6/23/09, 12:49 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,588
Default Re: Light Switch Near Shower

Paul writes:
Quote:
I sat on your toilet, dangled my hands in the sink while the water was running and with the other hand flicked your bathroom lights on and off........over and over again and you notice I was not shocked.
But you were touching a plastic switch cover with a dry hand while sitting on porcelain toilet.

Would you be willing to get soak and wet, stand barefoot in a bathtub full of water, and touch a decorative metal or chrome switch plate cover with a wet hand, with no hesitation? If so, what method would have used to confirm the plate cover isn't energized? Or do you do it without hesitation based solely on the unlikeliness that the switch plate cover is energized?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"

Last edited by gromicko; 6/23/09 at 12:54 AM..
Reply With Quote
  #157  
Old 6/23/09, 12:52 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

I think Nick must live in a bubble.

How else could he feel "safe" ?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #158  
Old 6/23/09, 1:18 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,588
Default Re: Light Switch Near Shower

http://www.nachi.org/gallery/electri...sunken-tub.jpg Light fixtures are not permitted to hang within 3 foot of the perimeter of the tub (in part) for fear that the metal housing of the fixture might be energized and in part because of these: http://doitbest.com/Cord+sockets-Lev...sku-520243.dib. But how is an energized metal switch plate cover any different?



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"

Last edited by gromicko; 6/23/09 at 1:22 AM..
Reply With Quote
  #159  
Old 6/23/09, 4:40 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Light Switch Near Shower

Quote:
Originally Posted by pabernathy View Post
I sat on your toilet, dangled my hands in the sink while the water was running and with the other hand flicked your bathroom lights on and off........over and over again and you notice I was not shocked

Quote:
Originally Posted by gromicko View Post
Paul writes: But you were touching a plastic switch cover with a dry hand while sitting on porcelain toilet.
So he "flipped the switch" with a dry hand!

Man oh man that really takes the cake!
Talk about being disingenuous! He might as well have had one hand in the sink, both feet in a tub of water, while wearing a big red rubber nose an orange colored Afro wig and an insulated glove on!
Would you be willing to get soak and wet, stand barefoot in a bathtub full of water, and touch a decorative metal or chrome switch plate cover with a wet hand, with no hesitation?
Here in the Northeast we inspect homes that were built in the 1700s 1800s and early 1900s that still have "knob and tube wiring"! Many of these homes have been renovated to have expensive tile with decorative brass plates/fixtures but have neglected to ensure that the electrical system is bonded/grounded properly!
I have found many faceplates in both kitchens and bathrooms that have been energized!

I would love to see this clown take a shower and while dripping wet flip a brass/metallic light switch on and off with-a-hand-that-is-dripping-with water!

If so, what method would have used to confirm the plate cover isn't energized? Or do you do it without hesitation based solely on the unlikeliness that the switch plate cover is energized?
There are Instructors and then there are "instructors".

Paul reminds me of the Naval electrical instructor that was demonstrating "what not to do" and killed himself in front of this class!



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
  #160  
Old 6/23/09, 8:36 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Quote:
Originally Posted by gromicko View Post
http://www.nachi.org/gallery/electri...sunken-tub.jpg Light fixtures are not permitted to hang within 3 foot of the perimeter of the tub (in part) for fear that the metal housing of the fixture might be energized and in part because of these: http://doitbest.com/Cord+sockets-Lev...sku-520243.dib. But how is an energized metal switch plate cover any different?
You're making it up Nick. sorry.

Have you considered that the exclusion zone for LUMINAIRS may have has more to do with water contacting a hot bulb, breaking it and exposing the filament than the use of an antiquated adapter.

A metal switch plate cover in a properly installed switch plate is bonded to the grounding system and presents no hazard.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #161  
Old 6/23/09, 8:38 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Quote:
Originally Posted by fcarrio View Post

There are Instructors and then there are "instructors".

Just as there are code inspectors and "code inspectors".

Paul reminds me of the Naval electrical instructor that was demonstrating "what not to do" and killed himself in front of this class!
You remind me of the "code inspector" that has to find something to justify his time, so he makes it up to be a pain in someone's backside.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #162  
Old 6/23/09, 4:43 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Light Switch Near Shower

More FATAL mistakes from "Instructors"

An experienced electrician in the U.S. mine was showing other workers how to use a cable fault tester. This device, also known as a "thumper," is capable of producing a high-energy pulse at voltages up to 10,000 V. During his demonstration, the man inadvertently touched a part of the test unit that was energized. Unfortunately, he was not wearing safety gloves suitable for high voltages.
  • The man received a fatal electrical shock.
Another incident was reported in Alberta, where a young, healthy worker was seriously injured when his co-workers, in an act of horseplay, applied the leads of a megohmeter to his hands. Workers in the electrical industry sometimes use this method of "zapping" the hands of a worker - usually a first-year apprentice - as an initiation joke.
  • This dangerous act is not worth the risk.
A megohmeter or "meggar" is an instrument used to measure the resistance of electrical insulation. It generates high voltages with a small current. During this incident, the electricity travelled from one hand of the worker to the other, passing through his heart.
  • The worker was hospitalized and treated for symptoms similar to those of a heart attack victim.
He was discharged from the hospital, but continued to have cardiac problems and was later re-admitted. His doctor confirmed that the condition was the result of the small electric current that had travelled through his heart.
  • Follow-up with a cardiologist confirmed that a small current of a high voltage can result in heart problems.
Under occupational health and safety law, employers have a legal responsibility to ensure the health and safety of all workers, and workers are equally accountable for their own safety, and for the safety of their co-workers.
  • This means taking all necessary precautions against workplace hazards.
For anyone working with electrical devices, the US Department of Labour's Mine Safety and Health Administration recommends these best practices:
  • No one should operate a high-voltage testing device except a qualified electrician, thoroughly trained in the use of that specific model of tester.
  • The operator must follow the manufacturer's instructions and keep the owner's manual with the device at all times.
  • When operating an electrical testing device such as a "thumper," always wear suitable high-voltage electrical gloves.
  • Before turning on an electrical testing unit, connect the provided frame-grounding cord/connectors to a proper grounding medium.
  • All workers should be informed that instruments that test and measure electricity are capable of storing and delivering a lethal electrical charge.
  • Store such devices in a secured location, accessible only to qualified, trained electricians.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
  #163  
Old 6/23/09, 5:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Does anyone think think "code inspectors" are smarter than "electrical instructors"

I don't.


FBI: Jersey City building inspector took bribes to look the other way

Electrocution Prompts Home Builder Lawsuit



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 6/23/09 at 5:54 PM..
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #164  
Old 6/23/09, 10:35 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Light Switch Near Shower

Quote:
Originally Posted by fcarrio View Post

There are Instructors and then there are "instructors".

Paul reminds me of the Naval electrical instructor that was demonstrating "what not to do" and killed himself in front of this class!
Your insane.......but I already KNEW this. Firstly, if you would READ the post you would understand what nick was saying...the hands were dry on the ONE end. besides I know where your heart lies...lol.

Secondly, if your intent is to build a mountain out of a mole hill and recommend plastic switches, with plastic covers be moved from clearly outside the shower and tub space....Now you would be wrong but thats your choice.

How about showing me (1) death from what you can a problem? And lets not use canada's codes because they are only for Canada.....the NEC is world wide.

Also your statements have no merit......got another agenda again Frank?



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #165  
Old 6/23/09, 10:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Light Switch Near Shower

Quote:
Originally Posted by fcarrio View Post
More FATAL mistakes from "Instructors"



An experienced electrician in the U.S. mine was showing other workers how to use a cable fault tester. This device, also known as a "thumper," is capable of producing a high-energy pulse at voltages up to 10,000 V. During his demonstration, the man inadvertently touched a part of the test unit that was energized. Unfortunately, he was not wearing safety gloves suitable for high voltages.
  • The man received a fatal electrical shock.
Another incident was reported in Alberta, where a young, healthy worker was seriously injured when his co-workers, in an act of horseplay, applied the leads of a megohmeter to his hands. Workers in the electrical industry sometimes use this method of "zapping" the hands of a worker - usually a first-year apprentice - as an initiation joke.
  • This dangerous act is not worth the risk.
A megohmeter or "meggar" is an instrument used to measure the resistance of electrical insulation. It generates high voltages with a small current. During this incident, the electricity travelled from one hand of the worker to the other, passing through his heart.
  • The worker was hospitalized and treated for symptoms similar to those of a heart attack victim.
He was discharged from the hospital, but continued to have cardiac problems and was later re-admitted. His doctor confirmed that the condition was the result of the small electric current that had travelled through his heart.
  • Follow-up with a cardiologist confirmed that a small current of a high voltage can result in heart problems.
Under occupational health and safety law, employers have a legal responsibility to ensure the health and safety of all workers, and workers are equally accountable for their own safety, and for the safety of their co-workers.
  • This means taking all necessary precautions against workplace hazards.
For anyone working with electrical devices, the US Department of Labour's Mine Safety and Health Administration recommends these best practices:
  • No one should operate a high-voltage testing device except a qualified electrician, thoroughly trained in the use of that specific model of tester.
  • The operator must follow the manufacturer's instructions and keep the owner's manual with the device at all times.
  • When operating an electrical testing device such as a "thumper," always wear suitable high-voltage electrical gloves.
  • Before turning on an electrical testing unit, connect the provided frame-grounding cord/connectors to a proper grounding medium.
  • All workers should be informed that instruments that test and measure electricity are capable of storing and delivering a lethal electrical charge.
  • Store such devices in a secured location, accessible only to qualified, trained electricians.
You really MUST have a hard on for me Frank........I sat on the toilet, turned on the sink and put my hand in the water while I turned on the light....get real...it was not on video and was a joke ( mainly about your statements to be honest with you )....while taking a break from shooting...get over yourself.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering CFL jallingham Electrical 34 12/5/08 3:40 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical 20 1/6/08 4:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 4:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical 9 4/18/07 8:22 PM
How many forum members to change a light bulb? kshepard Misc. Discussion 9 8/2/06 10:56 AM


All times are GMT -4. The time now is 5:01 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts