#166
|
||||
|
||||
|
Quote:
I am done with this topic.....mixing luminaries with non-metallic snap switches and non-metallic cover plates are insane but HI's are free to call them out....just be ready for any backlash they may take. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
| Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America) |
|
#167
|
||||
|
||||
|
Ooh Paul.
Better look out. THE COLORS ARE COMING... THE COLORS ARE COMING Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#168
|
||||
|
||||
|
Quote:
Secondly, I would read 404.9 (B) Grounding. Snap switches, including dimmer and similar control switches, shall be connected to an equipment grounding conductor and shall provide a means to connect metal faceplates to the equipment grounding conductor, whether or not a metal faceplate is installed. Snap switches shall be considered to be part of an effective ground-fault current path if either of the following conditions is met: (1) The switch is mounted with metal screws to a metal box or metal cover that is connected to an equipment grounding conductor or to a nonmetallic box with integral means for connecting to an equipment grounding conductor. (2) An equipment grounding conductor or equipment bonding jumper is connected to an equipment grounding termination of the snap switch. Exception to (B): Where no means exists within the snapswitch enclosure for connecting to the equipment grounding conductor or where the wiring method does not include or provide an equipment grounding conductor, a snap switch without a connection to an equipment grounding conductor shall be permitted for replacement purposes only. A snap switch wired under the provisions of this exception and located within reach of earth, grade, conducting floors, or other conducting surfaces shall be provided with a faceplate of nonconducting, noncombustible material or shall be protected by a ground-fault circuit interrupter. So with that said.......and what I suggested to you in Colorado is to recommend protection of the circuit on GFCI......rather than tell a person they have to change it, move it when clearly it is not a violation.....but again and I will said it LOUD so frank can hear it.....if you feel a GFCI is needed then suggest it by all means.......but make seller move it and possibly lose a sale because of it then i am sur we might see you in court.....THATS what a home seller will say in this kinda market. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#169
|
||||
|
||||
|
Quote:
So Paul, How far away would you say that metal cover plate should be from the tub / shower area? Would you not agree that it should be situated out of reach from anyone in the tub / shower for safety reasons ??? Cheers,
Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
|
#170
|
||||
|
||||
|
Nope.....none of my posts maintain it should be outside of reach from anyone. No one will change my mind on it....suggest GFCI if you wish but no way in heck would I flag someone for a switch near the shower as long as it is not within it.
But please feel free to do what you wish.......that goes for anyone here. Just dont look for me to support the choice....lol As for how far away with a metal cover...i did not give a distance....chances nothing as long as it complies with 404.9. Remember...Canada is Canada.....the NEC is used in more countries than just one unlike canada's code. I understand it is within canadian requirements. Does no make them right or wrong but it does say they made a choice which is not the same choice made in the USA or other countries that use the NEC. BTW- the NEC is a minimum safety standard so AGAIN for about the 20th time....if someone wishes to suggest GFCI I support that with no question because I agree on a potential issue that is in the interest of HI's safety concerns. However, I do not support telling a client they need to move it.........the risk does not outway the cost and compliance is compliance. I suggest members go with their own feelings, far be it for me to sway anyone. I can paint alot of what ever situations that could kill people but reality is...this is not something ANYONE can produce a real death concern anywhere. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 6/24/09 at 12:43 AM.. |
|
#171
|
||||
|
||||
|
Quote:
Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
|
#172
|
||||
|
||||
|
AskNACHI.org ForumQuestions posted to AskNACHI.org are displayed here for responses from InterNACHI members.
http://www.nachi.org/forum/f54/copper-bar-40777/#post529586 Quote:
Quote:
Hey "cut and paste" champion! YOU SHOULD BE ASHAMED OF YOURSELF! If you were going to do a "cut and paste" you should at least be honest enough to give credit to the author and or website where you took the material from! http://jchemed.chem.wisc.edu/JCESoft...OXCU/PAGE1.HTM Oxidation and Reduction of Copper A piece of copper metal is oxidized to black copper oxide by air when heated in a flame. The oxidized copper is reduced when placed in a hydrogen atmosphere. When removed from the hydrogen atmosphere, the metal is again oxidized. The equation for the reaction is included. (30 ) Keywords applications - practical/real-life, combination reaction, copper, descriptive chemistry, evidence of chemical reaction, hydrogen, oxygen, redox reaction, single exchange/replacement reaction Multimedia Play movie (QuickTime 3.0 Sorenson, duration 63 seconds, size 4.4 MB) A piece of copper is supported over a burner and is heated. The copper begins to react more rapidly with oxygen from the air and a darker color can be seen on the surface of the copper. This is similar to the color that forms on copper cookware when it is used in a kitchen. A few seconds later the copper has become dark. It has reacted with oxygen in the air. The burner flame is turned out and an inverted funnel with hydrogen gas blowing out of it is placed over the copper. The hydrogen gas is a reducing agent. It reduces the copper oxide on the surface of the copper and causes pure copper to be formed again. The dark color disappears leaving a pure copper color. Oxidation and reduction of the copper can be repeated several times by removing and replacing the funnel until the metal cools and the reactions slow down. The copper reacts with oxygen from the air. Hydrogen gas ... ... reduces the copper oxide. Discussion Copied by Paul Abernathy and pasted on the NACHI bulletin board without giving credit to this website! Copper oxidizes slowly in air, corroding to produce a brown or green patina. At higher temperatures the process is much faster and produces mainly black copper oxide. The oxide can be reduced by hydrogen gas, which is a moderately strong reducing agent, producing a shiny, clean copper surface. This provides a striking illustration of oxidation and reduction of a metal. Equations for the reactions are 2 Cu(s ) + O2(g ) --> 2 CuO(s ) CuO(s ) + H2(g ) --> Cu(s ) + H2O(g ) Demonstration Notes, Warnings, Safety Information, etc. Exam and Quiz Questions 1. When heated in air, copper changes color. Based on the color change, is the copper being oxidized or reduced? 2. In the presence of hydrogen gas, the copper turns color. Based on the color that the copper turns, is the hydrogen causing oxidation or reduction? Would the hydrogen be clasified as an oxidizing agent or a reducing agent? 3. What observable evidence indicates that a reaction is taking place when the copper is being heated? What are the reactants in this reaction? 4. Classify the reactions shown in the video as combination, decomposition, exchange, acid-base, combustion, or redox. (There is more than one reaction, and each reaction may fall within more than one of these categories.) Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 Last edited by fcarrio; 6/24/09 at 2:53 AM.. |
|
#173
|
||||
|
||||
|
Originally Posted by fcarrio
More FATAL mistakes from "Instructors" An experienced electrician in the U.S. mine was showing other workers how to use a cable fault tester. This device, also known as a "thumper," is capable of producing a high-energy pulse at voltages up to 10,000 V. During his demonstration, the man inadvertently touched a part of the test unit that was energized. Unfortunately, he was not wearing safety gloves suitable for high voltages.
Quote:
electrical guru/codeoligst who needs to get over himselfThe bottom line ..... is to keep me out of your posts and I will keep you out of mine! Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
|
#174
|
||||
|
||||
|
Hey Boys & Girls!
Here is some interesting information for ya! http://www.osha.gov/SLTC/etools/construction/electrical_incidents/eleccurrent.html How Electrical Current Affects the Human Body Three primary factors affect the severity of the shock a person receives when he or she is a part of an electrical circuit:Amount of current flowing through the body (measured in amperes). Path of the current through the body. Length of time the body is in the circuit. Other factors that may affect the severity of the shock are:
Effects can range from a barely perceptible tingle to severe burns and immediate cardiac arrest. Although it is not known the exact injuries that result from any given amperage, the following table demonstrates this general relationship for a 60-cycle, hand-to-foot shock of one second's duration: Current level (in milliamperes) Probable effect on human body 1 mA Perception level. Slight tingling sensation. Still dangerous under certain conditions. 5 mA Slight shock felt; not painful but disturbing. Average individual can let go. However, strong involuntary reactions to shocks in this range may lead to injuries. 6-30 mA Painful shock, muscular control is lost. This is called the freezing current or "let-go" range. 50-150 mA Extreme pain, respiratory arrest, severe muscular contractions. Individual cannot let go. Death is possible. 1000-4300 mA Ventricular fibrillation (the rhythmic pumping action of the heart ceases.) Muscular contraction and nerve damage occur. Death is most likely. 10,000 mA Cardiac arrest, severe burns and probable death.
Under dry conditions, human skin is very resistant. {Maybe that is why Paul keep a dry hand on a dry switch while he tried to fool Nick Wet skin dramatically drops the body's resistance. {Duh..... "The Darwin Award"..... Like being soaking wet and standing in a shower flipping an electrical switch off & on} Dry Conditions: Current = Volts/Ohms = 120/100,000 = 1mA a barely perceptible level of current
If the extensor muscles are excited by the shock, the person may be thrown away from the circuit. Often, this can result in a fall from elevation that kills a victim even when electrocution does not. When muscular contraction caused by stimulation does not allow the victim to free himself from the circuit, even relatively low voltages can be extremely dangerous, because the degree of injury increases with the length of time the body is in the circuit.
Note that a difference of less than 100 milliamperes exists between a current that is barely perceptible and one that can kill. High voltage electrical energy greatly reduces the body's resistance by quickly breaking down human skin. Once the skin is punctured, the lowered resistance results in massive current flow. Ohm's law is used to demonstrate the action. At 1,000 volts, Current = Volts/Ohms = 1,000/500 = 2 Amps which can cause cardiac arrest and serious damage to internal organs So..... Any so called "Electrical Guru / Codeoligist who tells you to stand in a shower and "flip a light switch off and on or...... sit on a toilet with one hand in a sink filled with water like he did" is IRRESPONSIBLE and or NUTS!Like I said.... There are Instructors and then there is... Paul! PS: Paul.... Earlier this year you said that you were quitting and becoming a " Dog Groomer"! Now would be a good time! Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
|
#175
|
||||
|
||||
|
Quote:
This sounds like one of your students! 20th March 2009, 04:12 PM Shaolin Wahnam Student Join Date: Feb 2006 Location: Beijing, China Posts: 269 Getting Electrocuted Dear All, I would like to relate a very interesting experience. Today when I was trying to find the source for an electrical problem I was electrocuted. I could feel the electricity hit my internal organs, and its pathway. Wow! As a carpenters apprentice I have worked with electricity before, but have never been 'hit'. Needless to say that, It Freaked me out!!! Not to mention that here in China the voltage is 240volts, quite a bit more than in the US. Anyways, after being zapped and letting loose a loud scream. I heard my training calling me. {Pauls Training! And that's when it happened, I felt as I had been electrocuted again, but this time in reverse. All of the original electric shock that my body had recieved, was literally shot out from my hand, with all the intensity of the original receiving of the electrical shock. Interesting experience, it freaked my roommate out! ![]() Anyways, dont try this at home .(thats what my face looked like)Still Living, Adam
Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
|
#176
|
||||
|
||||
|
Frank,
Are you OK? He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#177
|
|||
|
|||
|
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#178
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
I wonder how a person that was electrocuted wrote that story. Electrocution is death from an electric shock. So how could a dead person write that? Did they go through a medium?
|
| Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America) |
|
#179
|
||||
|
||||
|
This thread has turned to bull$h*t.
The ghost of JT haunts it. Boys and girls, please learn to play in the sandbox. I happen to agree with Paul. There is nothing to prohibit it, but personally I would recommend GFCI protection for this switch. There's a clear distinction from flagging something as a true defect, and making a recommended improvement. All defects are repairable. The art comes from the Client's impression of how manageable the problem is. The configuration in question, from whatever side of the argument you are on, is simple; install a GFCO and move on. Some inspectors talk for the sake of talking. And, Mike L was correct with regard to luminaires in the vicinty of a tub. As I recall, this was an old debate on this board, where there was an associated photo showing a hot tub with metal wall fixtures above the ledge. Tedesco and others debated it for days. In the end, the code interpretation was limited to protection from filaments. Problem with code references is that our opinions really do not count. The ONLY opinion that counts is that of the AHJ. Actually, Jim Bushart is the AHJ for his city. Why not ask Jim for his spin? Last edited by jfarsetta; 6/24/09 at 11:49 PM.. |
|
#180
|
||||
|
||||
|
Quote:
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Flickering CFL | jallingham | Electrical Inspections | 34 | 12/5/08 3:40 PM |
| Trouble Shooting the Simple Light Bulb | mcyr | Electrical Inspections | 20 | 1/6/08 4:47 AM |
| End of the light bulb as we know it!! | mcyr | General Inspection Discussion | 3 | 12/19/07 4:42 PM |
| Light Bulbs- All Ya Wanna Know | pabernathy | Electrical Inspections | 9 | 4/18/07 8:22 PM |
| How many forum members to change a light bulb? | kshepard | Miscellaneous Discussion for Inspectors | 9 | 8/2/06 10:56 AM |