Default Re: Light Switch Near Shower

I already know that 100's if not 1,000's of electricians are laughing at him anyway. So it is all good....we have come to expect as much from the source...Carrio is someone I have no respect for and it is known.....so he does not bother me.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #197  
Old 6/26/09, 1:47 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Light Switch Near Shower

All,

Plagarism means that one has impuned the reputation of the author. No reference is needed, unless the quote is used for te purpose of making money. At that point, copyright infringement comes into play. I know these things as I am a published author. Educational settings, such as colleges, have taken the term to new heights in recent years. Still doesnt change the meaning of the word, however.

Nick,

If we lived in England, your reference would be relevent to the discussion. Since we dont, it isnt
Reply With Quote
  #198  
Old 6/28/09, 9:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Switch Near Shower

Quote:
Originally Posted by jfarsetta View Post
All,

Plagarism means that one has impuned the reputation of the author. No reference is needed, unless the quote is used for te purpose of making money. At that point, copyright infringement comes into play. I know these things as I am a published author. Educational settings, such as colleges, have taken the term to new heights in recent years. Still doesnt change the meaning of the word, however.

Nick,

If we lived in England, your reference would be relevent to the discussion. Since we dont, it isnt
yeah..and we know my thousands of FREE helpful posts have made me millions...much less posting a small blurb on a non-member area to help someone.....Seems when people try to help people they get harrassed for helping...no wonder more people refuse to help.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #199  
Old 9/16/09, 10:47 PM
jmagee jmagee is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Clarksville,PA
Posts: 14
Default Re: Light Switch Near Shower

As per NEC 2008:
404.4 Damp or Wet Locations. A surface-mounted switch
or circuit breaker in a damp or wet location shall be enclosed
in a weatherproof enclosure or cabinet that shall
comply with 312.2. A flush-mounted switch or circuit
breaker in a damp or wet location shall be equipped with a
weatherproof cover. Switches shall not be installed within
wet locations in tub or shower spaces unless installed as
part of a listed tub or shower assembly.
Does the shower have a door on it, a curtin, or is the shower open. As an Commercial and Residential electrician these switches would not be located where they are in this picture. They should be mounted by the entry door to the shower room. The edge of the tile that is cloest to the switches begins the 3' rule so yes they are within the 3' area, but the 3' rule applies to lighting. (410.4 (D)) No matter how that passed inspection if it was even checked during the inspection there is a high chance of water getting into the switches, not to mention steam and water vapor.

just starting the inspection side of things here, but electric I know pretty good. Hope this helps out somewhat.

Jay Magee
Reply With Quote
  #200  
Old 9/18/09, 10:56 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Light Switch Near Shower

James,

As long as you understand that only applys to the "luminare" and not the switch....you are ok. Make sure you read all the replies...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering CFL jallingham Electrical Inspections 34 12/5/08 3:40 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical Inspections 20 1/6/08 4:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 4:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 8:22 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 10:56 AM


All times are GMT -4. The time now is 5:28 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts