Default Re: Light Switch Near Shower

In my opinion, if you're standing in the bathtub or shower and can reach a light switch then it is not safe...period!



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #17  
Old 6/12/09, 1:38 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: Light Switch Near Shower

Quote:
Originally Posted by fcarrio View Post
Does it look like this light switch is within the 36-inch "wet zone" or within 36-inches from the outside edge of the shower?

CHAPTER 39
DEVICES AND LUMINARIES SECTION E3901 SWITCHES
E3901.7 Wet locations.
A switch .... or circuit breaker located in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet. Switches...... shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
{IE manufactured "watertight/water resistant" specifically for the installed unit.}

How did you come up with 36 inches outside of 'the wet-zone' as 'the wetzone' itself?

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #18  
Old 6/12/09, 2:44 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mgratton View Post
In my opinion, if you're standing in the bathtub or shower and can reach a light switch then it is not safe...period!
Agreed!
That was why the "36-inch" rule was devised!



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
  #19  
Old 6/12/09, 2:48 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Light Switch Near Shower

Quote:
Originally Posted by jwicklander View Post
How did you come up with 36 inches outside of 'the wet-zone' as 'the wetzone' itself?

Jeff
Look at the diagram. The “wet zone” is anything within 36-inches from either edge of the tub or… 8-feet above the tub!
These areas are considered “wet zones” because they are “subject to shower spray”.

E3903.10 Bathtub and shower areas.
Cord-connected luminaries, chain-, cable-, or cord-suspended-luminaries, lighting track, pendants, and ceiling-suspended (paddle) fans shall not have any parts located within a zone measured 3 feet (914 mm) horizontally and 8 feet (2438 mm) vertically from the top of a bathtub rim or shower stall threshold.

This zone is all encompassing and includes the zone directly over the tub or shower. Luminaries located in this zone shall be listed for damp locations and where subject to shower spray, shall be listed for wet locations.

CHAPTER 39
DEVICES AND LUMINARIES SECTION E3901 SWITCHES
E3901.7 Wet locations.
A switch .... or circuit breaker located in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet. Switches...... shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
Attached Thumbnails
light-switch-near-shower-bath-elect.jpg   light-switch-near-shower-bathroom_fixture1.jpg  



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
  #20  
Old 6/12/09, 4:00 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Light Switch Near Shower

FROM THE NATIONAL ELECTRICAL CODE.

2008 National Electrical Code
ARTICLE 404-SWITCHES
404.4 Damp or Wet Locations.
A surface mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2.
A flush mounted switchor circuit breaker in a damp or wet location shall be equipped with a weatherproof cover. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
{NOTE: According to both the NEC and the IRC a damp/wet location is in the area within 36 inches of either edge of a tub sink or basin and/or an area that is subject to "spray". The "wet/damp area also extends 8 feet vertically.}

Luminary Locations
410 10.10
{A.} Wet and Damp Locations
Luminaries installed in wet or damp locations shall be installed such that water cannot enter or accumulate in wiring compartments, lampholders, or other electrical parts. All luminaries installed in wet locations shall be marked, "suitable for wet locations". All luminaries installed in damp locations shall be marked "suitable for wet locations" or suitable for damp locations.

{D.} Bath Tub and Shower Areas.
No parts or cord connected luminaries, chain, cable, or cord suspended luminaries, lighting track, pendants, or ceiling suspended {paddle} fans shall be located within the zone measured 900 mm {3 feet} horizontally and 2.5 m {8 feet} vertically from the top of the bathtub when I'm or shower stall threshold.
This zone is all encompassing and includes a space directly over the tub or shower stall. Luminaries located within the actual outside dimension of the bathtub or shower to a height of 2.5 m {8 feet vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations were subject to shower spray.

PLEASE NOTE:
BOTH THE NEC AND THE IRC HAVE THE SAME DEFINITION FOR THE "WET ZONE".

I hope this has been of some help to my fellow NACHI members
{and guests}




Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
Reply With Quote
  #21  
Old 6/12/09, 9:17 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Light Switch Near Shower

Frank,

I now see how you derived your definition of the wet zone. However, you cannot use the zone defined for lighting fixtures and apply it to switches. There is no Code support for your opinion.

Someone, Marcel, I think said he doesn't feel safe if you can touch something while standing in the tub or shower. Heck some bathrooms would need to have everything installed outside if that were the case.

If I were to try and discern a reason for the difference it would be because the fixtures have the potential to expose you to live parts whereas a switch would not.
Reply With Quote
  #22  
Old 6/12/09, 9:20 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Quote:
NOTE: According to both the NEC and the IRC a damp/wet location is in the area within 36 inches of either edge of a tub sink or basin and/or an area that is subject to "spray". The "wet/damp area also extends 8 feet vertically.
Frank,
where is this from?

What about Mike Hot's take on this issue?

Q&A with Mike Holt

Q25. Do switches for bathroom/shower lights have to be GFCI protected? Is there any distance that the switch must be from the bathtub or shower space?

A25. No. The NEC only requires that a switch not be installed within the wet location of a tub or shower spaces, unless the switch is part of a listed tub or shower assembly

See this diagram from Mike Holt.
Attached Thumbnails
light-switch-near-shower-switch.jpg   light-switch-near-shower-tub-switch.jpg  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 6/12/09 at 9:28 AM..
Reply With Quote
  #23  
Old 6/12/09, 10:48 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Light Switch Near Shower

Quote:
Originally Posted by Jim Port View Post
Someone, Marcel, I think said he doesn't feel safe if you can touch something while standing in the tub or shower. Heck some bathrooms would need to have everything installed outside if that were the case.
I've seen light switch installed outside the bathroom exactly for that reason and a GFI receptacle beside the sink...



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #24  
Old 6/12/09, 11:38 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Light Switch Near Shower

Quote:
Originally Posted by Jim Port View Post
I also scanned the code sections posted by you and did not see any mention of the 3' distance regarding switches.
Cuz it ain't there



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #25  
Old 6/12/09, 11:59 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Light Switch Near Shower

Ontario, Canada Only

Rule 30-322(3) says the light switch must not be located within reach of a person in a shower or bathtub. Appendix B for Rule 30-322(3), page 470 in the Code, defines out of reach as 39.4in. (1m). This means that switches controlling these loads may be inside the bathroom provided they are at least 39.4in from the bathtub or shower stall.



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #26  
Old 6/12/09, 5:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mgratton View Post
Ontario, Canada Only

Rule 30-322(3) says the light switch must not be located within reach of a person in a shower or bathtub. Appendix B for Rule 30-322(3), page 470 in the Code, defines out of reach as 39.4in. (1m). This means that switches controlling these loads may be inside the bathroom provided they are at least 39.4in from the bathtub or shower stall.
That's great but Vince doesn't live in Canada.

Maybe Frank will come back and explain how he came to his conclusion which now appears to be unfounded.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #27  
Old 6/13/09, 1:28 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mlarson View Post
That's great but Vince doesn't live in Canada.
Michael and all,

Common sense should always prevail regardless of where you live me think...

Safely yours,



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #28  
Old 6/13/09, 1:37 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mgratton View Post
Michael and all,

Common sense should always prevail regardless of where you live me think...

Safely yours,
Report it however you would like but there is no code support for it in the U.S. and I prefer my face without egg.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Find an InterNACHI certified Louisiana Home Inspector (and anywhere else in North America)
  #29  
Old 6/13/09, 2:16 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mlarson View Post
Report it however you would like but there is no code support for it in the U.S. and I prefer my face without egg.
Michael,

To the best of my knowledge a home inspection is not a *code* inspection, so no code support is required. With that said, knowledge and safey should always prevail.

I sleep well at night, do you...

Cheers,



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #30  
Old 6/13/09, 2:24 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Light Switch Near Shower

Quote:
Originally Posted by mgratton View Post
Michael,

To the best of my knowledge a home inspection is not a *code* inspection, so no code support is required. With that said, knowledge and safey should always prevail.

I sleep well at night, do you...

Cheers,
I sleep fine and there is no reason to get into a p****ing match.

To say we are not "code" inspectors is true but I think you will admit that we all rely on code on a regular basis even if we don't cite chapter and verse.

The codes are about safety and I hope we all know that.

You don't need my permission to report it how ever you wish but if you are challenged, be ready to pay the unnecessary expense of the rework.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering CFL jallingham Electrical 34 12/5/08 3:40 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical 20 1/6/08 4:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 4:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical 9 4/18/07 8:22 PM
How many forum members to change a light bulb? kshepard Misc. Discussion 9 8/2/06 10:56 AM


All times are GMT -4. The time now is 12:53 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts