Default Lightning arrestor and surge protector wiring

I went to Home Depot and Lowe's today to buy these items just so I can have the manufactures directions on how to install them. I see many of them wired directly to the main lugs. I do not think that is proper. Can anyone direct me to the place where I can find the wiring directions to these items. I used search engines and could not find the wiring diagram or instructions. Thanks in advance for the help.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/3/11, 10:07 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Lightning arrestor and surge protector wiring

Leviton 51120-x whole house surge protector:

http://www.smarthome.com/manuals/4860.pdf




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #3  
Old 1/3/11, 10:43 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Lightning arrestor and surge protector wiring

Delta lightning arrestors...
http://www.deltala.com/installa.htm




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #4  
Old 1/3/11, 10:54 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Lightning arrestor and surge protector wiring

From what I can see surge protectors cannot be attached to the main lugs and the lighting arrestor is to be attached to the main lugs.

I guess I will have to look up on a case by case basis. Thanks for the info, it was very kind of you.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #5  
Old 1/4/11, 4:59 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightning arrestor and surge protector wiring

This section, from the 2008 NEC, would prohibit double tapping the mains in most cases since those lugs are typically rated for only one conductor.

Quote:
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
FPN: Many terminations and equipment are marked with a tightening torque.
(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
Reply With Quote
  #6  
Old 1/6/11, 3:39 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 373
Default Re: Lightning arrestor and surge protector wiring

It used to be common around here that the arrestor was attached to the lugs on the main disconnect. In all new installations they are now connecting them to a circuit breaker.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #7  
Old 2/12/12, 10:12 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Lightning arrestor and surge protector wiring

I ran across this yesterday. Sorry the writing on the device is not very legible. I can't imagine this thing even working. A plastic device on the outside of the service panel with 3 conductors tapped directly to a 200 amp main breaker. Are you kidding me? Please tell me why I should be convinced this works.
Attached Thumbnails
lightning-arrestor-and-surge-protector-wiring-img_20120211_160252.jpg   lightning-arrestor-and-surge-protector-wiring-sam_1675.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #8  
Old 2/12/12, 1:46 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Lightning arrestor and surge protector wiring

This does NOT address you question but around here, the local power company will install these devices on your home to provide those protections for $4.95 a month. The other good thing is they will then put you into their system for the lowest rates...all the time. It will installed correctly and you get off the highest rates and into a lower cost per kilowatt rate. I would surprised they did not have something like that across the State as energy conscience as FL is. They will also do a FREE energy audit, install a new thermostat and some other energy saving features. They do all kinds of wacky things here....buy any old refrigerators, freezers to keep them out of the land fills, will pay for a new water heater if you currently have gas and will convert over....to name a few. There may be a similar program in your area.
Attached Thumbnails
lightning-arrestor-and-surge-protector-wiring-govt-st-027.jpg   lightning-arrestor-and-surge-protector-wiring-govt-st-029.jpg  



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts