Default Lightning hit house

Hey folks,
I am not an inspector, but I would appreciate any information that you can provide. My house was hit by lightning 6 weeks ago. It entered the roof and exited through the siding. It fried most of the low voltage wiring as well as some of the appliances. It also damaged some minor structure in the attic, roof and all the sheetrock in the upstairs rooms.

I have been concerned about the electrical wiring and can't seem to find information about what should be inspected and how. I hired a disaster recovery company for the repairs (bad choice). one line item they had was a megameter check. I talked to the electrician who performed the check, he said he just spot-checked some of the outlets, switches and breakers to see if they were functioning. I am concerned about the safety of my wiring and can't find anybody who knows anything.

Am I overly worried? Any suggestions?
thanks
jerry
Reply With Quote
  #2  
Old 5/7/07, 12:07 PM
rcramer's Avatar
rcramer rcramer is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Belleville, IL
Posts: 128
Default Re: Lightning hit house

Hello Jerry,
About three years ago when I was doing insurance restoration work as a contractor, I was called to a home that had been struck by lightning. To make a long story short; the jolt hit an I beam in the attic that supported the roof structure and then exited the home out a side wall next to the gas meter…..very lucky. The home owner had problems from day one with the electrical system and eventually the home was almost entirely rewired. They also had other problems; as the lightning fried the heads off nails. The homeowner noticed shingles, siding and soffit pieces falling off the home. It was determined that the entire roof, siding, soffit system and gutter system needed to be replaced.
I would highly recommend that you have at least three licensed electricians evaluate your electrical system. Additionally I would recommend that you hire a structural engineer to evaluate the structural integrity of the home. Get your insurance company involved, as they should pay for all of these services.



Robert Cramer
Five Star Property Inspections
Your Best & Safest Choice
www.fivestarpi.com
1-877-378-2774
Reply With Quote
  #3  
Old 5/7/07, 1:24 PM
Jerry Maxwell Jerry Maxwell is offline
New User
 
Join Date: May 2007
Posts: 2
Please Note: Jerry Maxwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightning hit house

Thanks, Robert.

Some of the roofing and decking has been replaced. The only thing in the attic that was repaired was a horizontal 2.4 that the lightning blasted in two. The siding and soffet is being replaced right now. I will get another electrician out to look at the wiring. The disaster recovery company is an old established company, but I am surprised that the guys that I have talked to don't seem to understand what should be done for the electrical wiring.
Their software program calls for a megameter check, but no-one seems to understand what that is. I have read info about a meg ohm meter test, but I know they did not do that.

jerry
Reply With Quote
  #4  
Old 5/7/07, 4:27 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Lightning hit house

Any Master Electrician should be able to perform a meg ohm test of each circuit to verify the integrity of the insulation. If any circuit is found to have inadequate resistance, each leg of the circuit can be isolated and tested to identify the exact run(s) of wire that must be replaced.

Jim King
Reply With Quote
  #5  
Old 5/7/07, 5:00 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightning hit house

Indeed, a megohm meter check, at 500VDC MUST be performed on each and every branch circuit of a home that has taken a direct lightning strike, flood, or fire fighting effort. This is very labor intensive. It's not so much physical, but it takes an awful lot of time. When you find a non-conforming branch circuit, then you're taking apart sections of that circuit to pin down the bad piece. I've never managed to completely megger, troubleshoot, and repair a dwelling for less than 2 grand. Often, it can run into more. For a labor metric, I use 2 hours per circuit, so that will give you an idea of what sort of time is involved with a megohm check of a dwelling.

A few reasons this is so labor intensive, troubleshooting aside, is because all dimmers and GFCI's need removed and jumpered. All light bulbs need removed, and all ballasts need disconnected. All cord and plug connected loads need unplugged, and all direct wired loads need disconnected. The megohm test is performed at twice normal operating voltage, so these things need disconnected so they don't get ruined during the test.

A note to the HI's in central PA or near the Mason-Dixon; I am one of the few EC's in my area that performs such testing in dwellings, with a complete circuit by circuit report, should the need arise.
Reply With Quote
  #6  
Old 5/7/07, 5:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightning hit house

A note to the OP... since you're reasonably sure that a proper megger test was not performed, in my opinion you have two options. Insist that one is performed, and insist on a copy of the report OR insist on AFCI protection for each and every branch circuit in the home.
Reply With Quote
  #7  
Old 5/8/07, 2:15 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Lightning hit house

Marc is correct about the need to evaluate ALL of the home's branch circuit wiring. I have seen first hand what a lightning strike does to residencial wiring. I few years ago I was involved in some repair work on a home struck by lightning. About 30% of the branch circuit wiring had exposed conductors from where the strike melted the insulation. Spot checking??? I would't sleep in it
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues for Inspectors 20 1/29/08 9:05 AM
Houses for Sale Stand Vacant jburkeson1 Miscellaneous Discussion for Inspectors 2 1/21/07 8:09 PM
Family's house is infested with mold rspriggs Ancillary Inspection Services & Additional Topics 6 1/28/06 2:05 AM


All times are GMT -4. The time now is 4:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts