House has a lighting protection system and one of the connections is at the gas meter.
I would think that is not a real good place to direct lighting to. What is the proper way to direct the lighting to ground for this type of system? What is the correct terminology for this type of lightning protection. Would it be a good recommendation to have the lighting system removed as I believe the electrical has been updated and ground rod(s) have been added. |
| Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
David, I agree with you , gas meter doesn't seem like a real good spot for this to be directed to. I have these on my home, and they are directed to their own grounding rod. I am not sure how deep this rod goes into the ground though. I have one rod on each end of the house. Around here they just call them lightning rods and grounding rods. Not sure if that is the true technical term or just a common name for them, never gave it much thought.
Ian Niquette Square One Home Inspection Markesan WI 53946 www.squareonehomeinspection.com Active Rain Network INACHI Awards Portal Want To Exchange Links? What we've got here is......failure......to communicate.....
|
|
#3
|
||||
|
||||
|
I agree, and the wire shouldn't be near the gas meter at all.
|
|
#4
|
||||
|
||||
|
What/where was the primary grounding electrode?
The gas piping is required in most jurisdictions to be bonded to the GE, but cannot be used as the grounding electrode. 250.106 Lightning Protection Systems. The lightning protection system ground terminals shall be bonded to the building or structure grounding electrode system. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Quote:
The pictured system is a separate lightning system and one of the ground terminals was the gas meter. I was setting up a radon and was getting a jump on the inspection, going back tomorrow. |
|
#6
|
|||
|
|||
|
Please Note:
Corlick Mark is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
||||
|
||||
|
This is an old thread, but I'll comment anyway...
These systems are typically very old (in my area approx 75+ years) and look just like the one shown, and should be on it's own ground rod. When multiple conductors are used, each usually has it's own grounding rod. From what I see in the pic's, I would bet that the grounding was moved when the metal siding was installed. This is very common, and a mistake made by siding installers that have no clue. Also, was the metal siding bonded to the system? It should be. Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#8
|
||||
|
||||
|
I think someone got the bonding mixed up with what is required for GEC.
I agree with Jeffrey P. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#9
|
|||
|
|||
|
Hello All,
The reason they probably connected to the gas piping is due to the proximity of of it to the system. If lightning were to strike the lightning terminal strikes and then make it's path to ground and for some reason it had an issue at that location then lightning (current) would arc off the lighting protection conductors over to the gas line since it is in contact with the earth thus providing a path and a difference of potential for that lighting. Bonding them together provides an equal potential between both of them which would lessen the chance of an arc situation and possible damage to the gas line. Seems the opposite but those are the hard facts. While it is not typical in the example shown I would be ok with the bonding. The real risk is the potential between these two grounded points. The danger of a arc due to the potential difference is too great to not bond them together at this point. In a new NFPA780 compliant installation the layout would be much different. Paul W. Abernathy |
|
#10
|
||||
|
||||
|
Thanks Paul.
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#11
|
||||
|
||||
|
Quote:
BestInspectors.Net
& Real Estate Training Academy Inspection Report Software for Windows - iOS - Mac - Android Continuing Education Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921 http://www.bestinspectors.net est. 1992 |
|
#12
|
||||
|
||||
|
Quote:
BestInspectors.Net
& Real Estate Training Academy Inspection Report Software for Windows - iOS - Mac - Android Continuing Education Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921 http://www.bestinspectors.net est. 1992 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Lightning Protection Systems- Do You Check It? | pabernathy | Electrical Inspections | 20 | 12/29/06 9:38 PM |
| Electrical Inspection Training for Home Inspectors | jtedesco1 | Inspection Education & Training | 6 | 4/27/06 10:43 PM |