Default lightning protection

House has a lighting protection system and one of the connections is at the gas meter.

I would think that is not a real good place to direct lighting to.

What is the proper way to direct the lighting to ground for this type of system?

What is the correct terminology for this type of lightning protection.

Would it be a good recommendation to have the lighting system removed as I believe the electrical has been updated and ground rod(s) have been added.
Attached Thumbnails
lightning-protection-154810-032-small-.jpg.jpg
Views:	89
Size:	49.3 KB
ID:	35167   lightning-protection-154810-061-small-.jpg.jpg
Views:	99
Size:	43.1 KB
ID:	35168  
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/23/10, 4:46 PM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: lightning protection

David, I agree with you , gas meter doesn't seem like a real good spot for this to be directed to. I have these on my home, and they are directed to their own grounding rod. I am not sure how deep this rod goes into the ground though. I have one rod on each end of the house. Around here they just call them lightning rods and grounding rods. Not sure if that is the true technical term or just a common name for them, never gave it much thought.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #3  
Old 2/23/10, 5:14 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: lightning protection

I agree, and the wire shouldn't be near the gas meter at all.
Reply With Quote
  #4  
Old 2/23/10, 9:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: lightning protection

What/where was the primary grounding electrode?

The gas piping is required in most jurisdictions to be bonded to the GE, but cannot be used as the grounding electrode.

250.106 Lightning Protection Systems. The lightning protection system ground terminals shall be bonded to the
building or structure grounding electrode system.




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 2/24/10, 7:03 AM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: lightning protection

Quote:
Originally Posted by jpope View Post
What/where was the primary grounding electrode?

The gas piping is required in most jurisdictions to be bonded to the GE, but cannot be used as the grounding electrode.

250.106 Lightning Protection Systems. The lightning protection system ground terminals shall be bonded to the
building or structure grounding electrode system.

The GEC was at the exterior, ground rod(s), recently installed.
The pictured system is a separate lightning system and one of the ground terminals was the gas meter.

I was setting up a radon and was getting a jump on the inspection, going back tomorrow.
Reply With Quote
  #6  
Old 1/8/12, 7:05 AM
Corlick Mark Corlick Mark is offline
New User
 
Join Date: Jan 2012
Posts: 1
Please Note: Corlick Mark is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: lightning protection

Quote:
Originally Posted by dmacy View Post
House has a lighting protection system and one of the connections is at the gas meter.

I would think that is not a real good place to direct lighting to.

What is the proper way to direct the lighting to ground for this type of system?

What is the correct terminology for this type of lightning protection.

Would it be a good recommendation to have the lighting system removed as I believe the electrical has been updated and ground rod(s) have been added.
I am really surprised to hear that the lightning protection system is directed toward the gas meter. I suggest you to change it. In general cases, the gas meters are grounded with salt which have very low resistance. This is the same process that is followed in substation.
Reply With Quote
  #7  
Old 1/8/12, 9:54 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: lightning protection

This is an old thread, but I'll comment anyway...

These systems are typically very old (in my area approx 75+ years) and look just like the one shown, and should be on it's own ground rod. When multiple conductors are used, each usually has it's own grounding rod. From what I see in the pic's, I would bet that the grounding was moved when the metal siding was installed. This is very common, and a mistake made by siding installers that have no clue. Also, was the metal siding bonded to the system? It should be.
Reply With Quote
  #8  
Old 1/8/12, 10:07 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: lightning protection

I think someone got the bonding mixed up with what is required for GEC.
I agree with Jeffrey P.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #9  
Old 1/8/12, 10:15 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: lightning protection

Hello All,

The reason they probably connected to the gas piping is due to the proximity of of it to the system. If lightning were to strike the lightning terminal strikes and then make it's path to ground and for some reason it had an issue at that location then lightning (current) would arc off the lighting protection conductors over to the gas line since it is in contact with the earth thus providing a path and a difference of potential for that lighting. Bonding them together provides an equal potential between both of them which would lessen the chance of an arc situation and possible damage to the gas line. Seems the opposite but those are the hard facts.

While it is not typical in the example shown I would be ok with the bonding. The real risk is the potential between these two grounded points. The danger of a arc due to the potential difference is too great to not bond them together at this point. In a new NFPA780 compliant installation the layout would be much different.



Paul W. Abernathy
Reply With Quote
  #10  
Old 1/8/12, 12:10 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: lightning protection

Thanks Paul.
Reply With Quote
  #11  
Old 1/12/12, 1:55 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: lightning protection

Quote:
Originally Posted by pabernathy View Post
Hello All,

While it is not typical in the example shown I would be ok with the bonding. The real risk is the potential between these two grounded points. The danger of a arc due to the potential difference is too great to not bond them together at this point. In a new NFPA780 compliant installation the layout would be much different.
I agree with Paul's comments. A lightning protection system is a Faraday shield. An ideal lightning protection system would be a Faraday cage. Very small differences in impedance in parallel paths can cause extremely large differences in potential with a lightning strike. Putting a lightning protection system on its own ground rod could have disastrous consequences. It is much safer to terminate a lighting lead to a gas line than to a ground rod.




BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #12  
Old 1/12/12, 2:01 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: lightning protection

Quote:
Originally Posted by iniquette View Post
David, I agree with you , gas meter doesn't seem like a real good spot for this to be directed to. I have these on my home, and they are directed to their own grounding rod. I am not sure how deep this rod goes into the ground though. I have one rod on each end of the house. Around here they just call them lightning rods and grounding rods. Not sure if that is the true technical term or just a common name for them, never gave it much thought.
Ian, if your lighting protection is isolated from your house's electrical system, you could have an extremely dangerous installation. You would be much safer not to have the lightning protection at all than to have it isolated from your electrical power distribution.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Lightning Protection Systems- Do You Check It? pabernathy Electrical Inspections 20 12/29/06 9:38 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 10:43 PM


All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts