Hey Guys,

Just wanting another educational moment with you all.....

Have you ever been to an inspection and their was a Lightning Protection System...you know the ones with the rods on the roof and they lead down to their own ground rods......have you ever thought to yourself...are they bonding this thing correctly?

I found in a recent conversation with a few AHJ's across the country they it is nearly 30% of them do not think the lightning system should be bonded with the grounding electrode system of the house.....they say they need to be kept apart.....well.....the NEC see's it differently.

If you have your CODE books handy....check out 250.106 and give it a look see..



250.106 Lightning Protection Systems.


The lightning
protection system ground terminals shall be bonded to the
building or structure grounding electrode system.






FPN No. 1: See 250.60 for use of air terminals. For further
information, see NFPA 780-2004,



Standard for the Installation
of Lightning Protection Systems, which contains detailed
information on grounding, bonding, and spacing from
lightning protection systems.

FPN No. 2: Metal raceways, enclosures, frames, and other
non–current-carrying metal parts of electric equipment installed
on a building equipped with a lightning protection
system may require bonding or spacing from the lightning
protection conductors in accordance with NFPA 780-2004,





Standard for the Installation of Lightning Protection Systems


.
Separation from lightning protection conductors is
typically 1.8 m (6 ft) through air or 900 mm (3 ft) through
dense materials such as concrete, brick, or wood.

Also check out 250.60 as well..






250.60 Use of Air Terminals.


Air terminal conductors and
driven pipes, rods, or plate electrodes used for grounding air
terminals shall not be used in lieu of the grounding electrodes
required by 250.50 for grounding wiring systems and equipment.
This provision shall not prohibit the required bonding
together of grounding electrodes of different systems.






FPN No. 1: See 250.106 for spacing from air terminals.
See 800.100(D), 810.21(J), and 820.100(D) for bonding of
electrodes.






FPN No. 2: Bonding together of all separate grounding
electrodes will limit potential differences between them and
between their associated wiring systems.

So.....when looking at the electrical systems...and you notice a lightning protection system on the roof.....see if the lightning system is installed correctly....you may be surprised.

Does this go above and beyond your scope....yep it might....but for educational puposes figured you might like to know......

This is for Educational Purposes Only....Paulright Protected !




Paul W. Abernathy

Last edited by pabernathy; 12/28/06 at 11:46 AM..
Reply With Quote
  #2  
Old 12/28/06, 12:06 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Lightning Protection Systems- Do You Check It?

These systems are not a part of the NACHI SOP.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 12/28/06, 12:14 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Lightning Protection Systems- Do You Check It?

NEVER said it was....so you are saying you are TOO good to learn Mr. Bushart?

Are you saying...someone can't go beyond it if they wish.......?

I'm an Inspector....I check it when I see it.......are you saying I can't?

II. The inspector is not required to operate:

H. Moisture meters, gas detectors or similar equipment.

AND what about those using Thermal Imaging....hmmmmm......are you saying they CANT?

BUT how many inspectors OUT THERE use Moisture Meters...and Gas Detectors.........Your POINT IS ?


AGAIN.....this is EDUCATION only......was simply asking if anyone checked this....and if so do they want to know what the NEC says about it....nothing more.



Paul W. Abernathy

Last edited by pabernathy; 12/28/06 at 12:29 PM..
Reply With Quote
  #4  
Old 12/28/06, 12:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Lightning Protection Systems- Do You Check It?

Paul, I like you and find you very informative but James only stated a fact without and condemnation of any additional services a HI may chose to preform
Reply With Quote
  #5  
Old 12/28/06, 12:28 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Lightning Protection Systems- Do You Check It?

You obviously don't know that Mr. Bushart does not care much for me......again it was for educational purposes......explaining the bonding of lightning systems.

Many things are beyond the SOP but are done all the time....again this was for education only.

Just wanted to know clarrification on the SOP....as I do many things beyond it......so basically I was not cutting Mr. Bushart...was making a statement.......are all HI's to STOP at the SOP if they feel comfortable going furthur...thats all.



Paul W. Abernathy
Reply With Quote
  #6  
Old 12/28/06, 12:29 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Lightning Protection Systems- Do You Check It?

Quote:
Originally Posted by pabernathy
NEVER said it was....so you are saying you are TOO good to learn Mr. Bushart?

Are you saying...someone can't go beyond it if they wish.......?

I'm an Inspector....I check it when I see it.......are you saying I can't?

II. The inspector is not required to operate:

H. Moisture meters, gas detectors or similar equipment.

AND what about those using Thermal Imaging....hmmmmm......are you saying they CANT?

BUT how many inspectors OUT THERE use Moisture Meters...and Gas Detectors.........Your POINT IS ?


If you do not LIKE me Mr. Bushart.......thats fine but do NOT destroy the ability of other inspectors who MAY want to learn things other than what is SOP.....They just might have wanted to know about this information for future knowledge and education.....
You need to go back on your meds, Paul.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #7  
Old 12/28/06, 12:33 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Lightning Protection Systems- Do You Check It?

nope.........but seriously since you are on the SOP committee...are you saying people can't go beyond the SOP.....honestly I am confused now and would like your take on it.....but please.....I edited it ...as I believe your motives were genuine.....so please explain to me the stance of the SOP and IF someone goes beyond it...( please leave out the legal issues involved....I dont see a concern with it in some areas )



Paul W. Abernathy
Reply With Quote
  #8  
Old 12/28/06, 12:38 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: Lightning Protection Systems- Do You Check It?

Quote:
Originally Posted by pabernathy
You obviously don't know that Mr. Bushart does not care much for me......again it was for educational purposes......explaining the bonding of lightning systems.

Many things are beyond the SOP but are done all the time....again this was for education only.

Just wanted to know clarrification on the SOP....as I do many things beyond it......so basically I was not cutting Mr. Bushart...was making a statement.......are all HI's to STOP at the SOP if they feel comfortable going furthur...thats all.
I guess I need to go back on my meds too .
James seems to have much knowledge I wish he would share more of it .
I have been ignoring most of his posts as it looks to me like he is only trying to destroy what ever has been said or posted .
He seems to disagree with many things that are posted and not adding much on how things could be improved .
I guess I just need to keep him on my ignore List .
This is to bad as he could add much info if he tried .
Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #9  
Old 12/28/06, 12:40 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Lightning Protection Systems- Do You Check It?

Quote:
Originally Posted by pabernathy
Hey Guys,

Just wanting another educational moment with you all.....

Have you ever been to an inspection and their was a Lightning Protection System...you know the ones with the rods on the roof and they lead down to their own ground rods......have you ever thought to yourself...are they bonding this thing correctly?

I found in a recent conversation with a few AHJ's across the country they it is nearly 30% of them do not think the lightning system should be bonded with the grounding electrode system of the house.....they say they need to be kept apart.....well.....the NEC see's it differently.

If you have your CODE books handy....check out 250.106 and give it a look see.
For the record...I never said that you SHOULD check it...I asked DO you check it...and then as you see above simply made an attempt to explain it.

Has nothing to do with the SOP......you can clearly go beyond it if you feel qualified to do so....I was only making an attempt to help qualify you by proxy of education about the subject.

Most HI's will not......I accept that and not trying to suggest they all do...but found it interesting that many AHJ's do not understand the NEC on it so I figured what better thing to do than explain the NEC's view on it and if anyone learned anything from it..so be it.

Anyway...hope it was helpful.....not bashing you JB....simply wanted to educate......are I for one am never to educated to learn more...I learn daily...

Sorry if anyone did not find this educational or helpful....accept my appologies



Paul W. Abernathy
Reply With Quote
  #10  
Old 12/28/06, 12:46 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Lightning Protection Systems- Do You Check It?

Quote:
Originally Posted by pabernathy
For the record...I never said that you SHOULD check it...I asked DO you check it...and then as you see above simply made an attempt to explain it.

Has nothing to do with the SOP......you can clearly go beyond it if you feel qualified to do so....I was only making an attempt to help qualify you by proxy of education about the subject.

Most HI's will not......I accept that and not trying to suggest they all do...but found it interesting that many AHJ's do not understand the NEC on it so I figured what better thing to do than explain the NEC's view on it and if anyone learned anything from it..so be it.

Anyway...hope it was helpful.....not bashing you JB....simply wanted to educate......are I for one am never to educated to learn more...I learn daily...

Sorry if anyone did not find this educational or helpful....accept my appologies
I for one found it very helpful and thank you Paul!

I do not find many of these systems installed and may make a comment on them if they are severely in disrepair. Now I may pay a little closer attention to them.

Thanks again Paul! I have always found you a great asset to this BB unlike certain other members.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #11  
Old 12/28/06, 12:47 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Lightning Protection Systems- Do You Check It?

Quote:
Originally Posted by pabernathy
nope.........but seriously since you are on the SOP committee...are you saying people can't go beyond the SOP
People make their own business decisions.

For people who inspect in accordance with the SOP, the SOP provides protection for them. It is the standard that they apply in all of their inspections and it is the standard that they can expect their client to hold them accountable for.

When a person decides to inspect outside of the SOP, he steps outside of the boundaries of that protection.

I simply pointed out, in response to your choice of topic, that such an observation would place an inspector outside of the protection offered him by the SOP.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #12  
Old 12/28/06, 12:54 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Lightning Protection Systems- Do You Check It?

Quote:
Originally Posted by jbushart
People make their own business decisions.

For people who inspect in accordance with the SOP, the SOP provides protection for them. It is the standard that they apply in all of their inspections and it is the standard that they can expect their client to hold them accountable for.

When a person decides to inspect outside of the SOP, he steps outside of the boundaries of that protection.

I simply pointed out, in response to your choice of topic, that such an observation would place an inspector outside of the protection offered him by the SOP.
Thank you James......I thank you for your position on the subject.



Paul W. Abernathy
Reply With Quote
  #13  
Old 12/29/06, 12:33 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightning Protection Systems- Do You Check It?

Most electrical inspectors don't really know that much about lightning systems either, even here in lightning country. They just look for fat wire, no sharp turns and good regular bonding practices. Real lightning systems will use braided fine strand conductors since the leading edge of a lightning strike acts like RF and skin effect is a factor. It is a very short duration event and by the time it could saturate a thick conductor it is gone. It just rides on the skin.
In the computer biz we looked at lightning and other short duration transients as a race. You shunt it before it can hurt you. You slow down the shot on signal lines with iron and let it go as fast as you can on the bond (short braided wire). Hopefully it is gone before it hits the circuitry.
In a lightning rod system you want to shunt the shot to ground before it can burn down the house by taking a more resistive path. Resistance is heat. There will always be a spike on everything electrical but if it all rides the spike up and rides it back down nobody gets hurt. In that respect you want it connected to your star wired grounding electrode system, where your protectors get connected.
Reply With Quote
  #14  
Old 12/29/06, 12:39 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Lightning Protection Systems- Do You Check It?

Hey Greg........I do have a question for you.....since most places DO NOT truly understand the installation of the lightning systems...they are getting more popular up here....

What is YOUR take on the companies that are installing the lightning rod systems within the attic space...then running the conductors down the wall cavity to the basement....and out the wall....

I have inspected a few ( on the electrical side ) and they have always been outside the dwelling......but recently we have a company in the area who are running them through the attic....poking the rods out the attic space and then all of the braids are within the attic and down the finished wall in the insulation...

What is your opinion of that......?



Paul W. Abernathy
Reply With Quote
  #15  
Old 12/29/06, 12:56 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Lightning Protection Systems- Do You Check It?

Paul

When I see a lightning protection system I will inspect and report on same but remember I have some knowledge in that area

At this point in time it is not a HI issue because very few homes have a system -- Sort of like solar electrical systems

Times might change

Maybe we could start a thread on LPS - chokes - and building halos -- lot of fun -- and yes I am name dropping to impress (my kids just take me for granite and I need someone to think I know something)

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 10:43 PM


All times are GMT -4. The time now is 4:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts