Default Lights & GFCI Outlets

What does it mean when you test the GFCI outlets and the lights go out in that particular room..

1) I hit the test button in the bathroom and the fan/light go out..
2) I hit the test button in the kitchen and the oven and overhead lights go out..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #2  
Old 2/28/07, 10:39 AM
Harvey Gordon's Avatar
Harvey Gordon Harvey Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 249
Default Re: Lights & GFCI Outlets

Those items are protected by the GFIC?

Not sure I understand what you are getting at.





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #3  
Old 2/28/07, 10:41 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Lights & GFCI Outlets

Why would the lights and the oven go out when you push the test button on the GFCI??



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #4  
Old 2/28/07, 10:43 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Lights & GFCI Outlets

Lights and fans above bathtub sunshowers are required to be GFCI protected.
Often this circuit is separate from the counter top circuits and is a GFCI device (without the plug outlet, like a Whirlpool tub GFCI).
One concern with this type of application is that the lights go off and locating the GFCI device to reset may become difficult.
It is difficult, if not impossible without ripping out the wall to rewire a GFCI circuit to remove lighting circuits from the countertop. I recommend a battery backup power failure nightlight type device if this becomes an issue.
Reply With Quote
  #5  
Old 2/28/07, 10:46 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Lights & GFCI Outlets

Ok, What about the oven, I havent seen the oven turn off when I test the GFCI...



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #6  
Old 2/28/07, 11:12 AM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lights & GFCI Outlets

If the oven is linked to the load on a GFCI receptacle then it will go off when you test the GFCI receptacle. This is how one GFCI receptacle can protect the whole circuit. I am sure it is wrong. Surely an oven appliance should be on its own circuit?

And the receptacle, lights and oven all on one circuit! Wow, that is weird. I worry about having one room in my house where one receptacle has been put on the same circuit at the light, which I am sure is not right. Perhaps someone could clarify if this is also OK for me?

I trust we are talking about GFCI receptacles here and not GFCI-protected circuits on the main panel? But even so, oven, receptacles and lights on one breaker? Very strange.

My neighbor has a big GFCI flashing light thingy that protects his entire panel. I trust we are not talking about these also?

Last edited by Ian Gills; 2/28/07 at 11:28 AM..
Reply With Quote
  #7  
Old 2/28/07, 11:30 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Lights & GFCI Outlets

Ian, I am talking about GFCI recepticles in the house..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #8  
Old 2/28/07, 11:43 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Lights & GFCI Outlets

Quote:
Originally Posted by dandersen
Lights and fans above bathtub sunshowers are required to be GFCI protected.
Only receptacle outlets are required to be GFCI protected, however, there is nothing prohibiting additional outlets (such as lighting outlets) from being protected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 2/28/07, 11:48 AM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lights & GFCI Outlets

But all these devices on the load of a single GFCI receptacle on a single circuit? An oven? The lights? Surely this CANNOT be the correct thing to do.
Reply With Quote
  #10  
Old 2/28/07, 11:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Lights & GFCI Outlets

Quote:
Originally Posted by Ian Gills
But all these devices on the load of a single GFCI receptacle on a single circuit? An oven? The lights? Surely this CANNOT be the correct thing to do.
Most likely not. Especially considering that an oven is generally on a 240v circuit.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/28/07, 11:55 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Lights & GFCI Outlets

The oven was on a 120 volt circuit, and was gas..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #12  
Old 2/28/07, 12:07 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lights & GFCI Outlets

Oh, a gas oven. Then is it OK to have lights and receptacles on one circuit? I have one room in my house like this (one receptacle, one light).

This thread is making me extremely tempted to rewire my entire house on one circuit linked to a single GFCI 100 amp main breaker. We need someone to explain the limits of individual circuits.
Reply With Quote
  #13  
Old 2/28/07, 12:33 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lights & GFCI Outlets

210.52(B)(2) ex2 specifically allows the light and igniter on a gas range/oven to be on kitchen a small appliance circuit so that one is OK. The bath depends on whether another bathroom goes off when you trip this one. If so it is wrong. All the equipment in ONE bathroom can be on the same circuit even on the GFCI. That is a bad design decision but code legal.
Reply With Quote
  #14  
Old 2/28/07, 3:11 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lights & GFCI Outlets

Jeffery you stated..Only receptacle outlets are required to be GFCI protected, however, there is nothing prohibiting additional outlets (such as lighting outlets) from being protected.

Than what your saying is that it ok to have a light on the same curcuit as the receptacle? I thought it wasn't correct because if the outlet trips the light goes out, and your in the dark (safety concern) Give me your thoughts, do I call it out or not?
Reply With Quote
  #15  
Old 2/28/07, 3:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Lights & GFCI Outlets

Quote:
Originally Posted by brepanshek
Than what your saying is that it ok to have a light on the same curcuit as the receptacle?
As Greg stated, if it's a single-bathroom circuit, it's acceptable although a poor design.

If more than one bathroom is supplied by the circuit, the receptacle outlets must be on their own circuit.

Here's the code section

210.11 (3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets.

Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Properly Testing GFCI Outlets tchristopher Electrical Inspections 17 3/17/07 11:19 AM
outlets and lights question Scott Schultz Electrical Inspections 4 1/27/07 7:59 PM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical Inspections 7 6/24/06 6:58 AM
GFCI Outlets w/ No Test Button - Dont Work! HELP PLEASE! LiveAd Electrical Inspections 4 6/20/06 10:47 AM
opinions on GFCI outlets for non grounded oputlets jmerritt1 Electrical Inspections 23 5/11/06 7:22 PM


All times are GMT -4. The time now is 4:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts