Saw this today, during a draw inspection.
The previous owner (this was a tear down McMansion) installed flood lights high (about 17 feet up) in a tree next to a deck. They ran conduit up the tree (waterproof connections) and had the two waterproof boxes on opposite sides to the tree. The drilled a hole directly through the tree and inserted the EMT through the hole. So, everything was properly sealed and in the (locally) required EMT conduit. Problem? Comments? They seemed to go through much work to do this. NEC complient? (I can't wait!!! Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#2
|
||||
|
||||
|
I would find it hard to believe that this spotlight was installed in accordance with the manufacturer's directions.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Another one that's dumb, but legal:
ARTICLE 410 Luminaires (Lighting Fixtures), Lampholders, and Lamps 410.16 Means of Support. (H) Trees. Outdoor luminaires (lighting fixtures) and associated equipment shall be permitted to be supported by trees. The violation, from a code standpoint, is 110.3(B), which requires that manufacturers instructions be followed. The lampholder pointing up is the violation. PAR holders must point at least 15 degrees below horizontal according to most manufacturers. Straight up like that one is a genuine problem on many fronts. Last edited by Marc D. Shunk; 4/21/08 at 9:54 PM.. |
|
#4
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
See 225.26 also and EMT is Electrical Metallic Tubing "Thinwall"
Were the EMT fittings raintight? |
|
#5
|
||||
|
||||
|
Quote:
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#6
|
|||
|
|||
|
What they gonna do when the tree gets bigger around? And it will, you know.
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#7
|
||||
|
||||
|
Quote:
Agree with the upward orientation, Marc. What about the drilling through the tree and inserting the EMT? All connections were rain tight. Exterior boxes. All EMT with the proper fittings and unions. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I think it would be a good idea for someone to propose that the word "thermal" be stricken any place in the NEC that it precedes "expansion" and put the word "any" in its place. |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree drilling the tree was the main flaw. They could have looped "wet" MC cable or one of the liquidtight flexible raceways between the boxes with a little slack for growing room.
Joe, if this has been in the tree for more than a couple years I guarantee the connectors are not "raintight". That is fairly a new invention. |
|
#10
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
UL offers Listing service for "raintight" compression type EMT fittings under the product category Electrical Metallic Tubing (EMT) Fittings (FKAV) located on page 33 of the 2005 General Information Directory for Electrical Equipment (White Book). UL recently conducted a study to determine the reliability of "raintight" compression fittings to consistently comply with the wet location test criteria. Based on the results, UL initiated a more stringent follow-up test program to assure these products consistently exclude water to maintain their "raintight" marking. As of March 2002, manufacturers of UL Listed "raintight" (wet location) compression type EMT fittings were required to comply with the more stringent follow-up test requirements. If they did not comply, they were no longer authorized to mark their UL Listed fittings with the "Raintight" marking. Several manufacturers presently have Listing up to 2 inch and some up to 3 inch trade size. As of June 2005, several manufacturers are authorized to mark their Listed compression type EMT fittings with the "Raintight" marking up to 2 inch trade size. At least one manufacturer has up to 3 inch trade size fittings Listed for "Rain Tight" or "Wet Locations". These fittings are typically provided with additional gaskets, sealing or "O" rings or additional assembly instructions that must be followed to exclude water. The installation instructions on the carton must be followed for proper installation. Look for the "Raintight" or "Wet Locations" marking on the container and the UL Mark on the fitting. The availability of "raintight" fittings may change as manufacturers redesign their fittings to comply with UL's new follow-up "raintight" testing. It is imperative to always look for the proper marking on the product and container. If the product is not marked with the UL Listing Mark and the container is not marked "Raintight" or "Wet Locations", then the fittings have not been Listed for raintight or wet location applications. As new "Raintight" Listings are promulgated, this page will be updated. Contact Us If you have an immediate question or need assistance, please contact Regulatory Services. |
|
#11
|
||||
|
||||
|
Would have been no problem if they used Liquid tight around the outside.
|
|
#12
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#13
|
||||
|
||||
|
In higher-end neighborhoods, with the $2m+ homes, this is quite common. Floodlights are usually pointed upward, even when mounted up in the tree. It creates an interesting lighting effect. I've even seen low wattage lights tilted downward from WAY up, to try and emulate moonlight. A little weird, but can look cool.
|
|
#14
|
||||
|
||||
|
The boring won't hurt the tree, but don't ever try that with a Popular Tree, they are Nature's own Lighting Rod. P.S. Not a good choice for a Deer Stand either.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Lights Flickering while appliances start-up and while running. | Jeff Nunz | Electrical Inspections | 15 | 11/27/07 4:04 PM |
| Fan type and recessed can lights | dmacy | Interior Inspections | 7 | 7/23/07 10:39 PM |
| Trees are nice but...... | gbrasseur | General Inspection Discussion | 7 | 3/2/07 11:02 PM |
| Lights & GFCI Outlets | thejnicki | Electrical Inspections | 14 | 2/28/07 3:48 PM |