Default Lightswitch In Tub Area

Gentlemen,

Today I found this dimmer control for the lights over a whirlpool tub. The dimmer is over the horizontal surface of the tile, but not directly over the tub itself. It is the right-most of the three coverplates in the picture, and is OBVIOUSLY put in that position to be reached from within the tub. The light switches for the rest of the bathroom are on the other wall, and don't control these lights. It is NOT protected by the GFCI serving the bathroom. I think it is dangerous. What do you think? At a MINIMUM, I think they should wire it to the GFCI protected outlet that is less than eighteen inches away. The third coverplate in between the two is for cable-tv and a phone.
Attached Thumbnails
lightswitch-tub-area-100_3554.jpg  
Reply With Quote
  #2  
Old 10/26/07, 5:57 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightswitch In Tub Area

It's not over the tub so it's legal. Safe is a judgement call.
IMO it is not unsafe if it is wired properly.
Reply With Quote
  #3  
Old 10/26/07, 6:52 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Lightswitch In Tub Area

Yep, looks good to me.

"Click To Enlarge"
lightswitch-tub-area-bath-switch.jpg
Reply With Quote
  #4  
Old 10/26/07, 7:05 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Lightswitch In Tub Area

Does this look like the AHJ had it removed? Why was it wrong?
Attached Thumbnails
lightswitch-tub-area-img_2436-small-.jpg.jpg
Views:	129
Size:	40.1 KB
ID:	15565  
Reply With Quote
  #5  
Old 10/26/07, 7:09 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by mlarson
Does this look like the AHJ had it removed? Why was it wrong?
It's inside the tub area. It should be located outside the tub area.
Reply With Quote
  #6  
Old 10/26/07, 7:17 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by dvalley
It's inside the tub area. It should be located outside the tub area.
Still think so?
Attached Thumbnails
lightswitch-tub-area-img_2437-small-.jpg.jpg
Views:	108
Size:	32.8 KB
ID:	15566  
Reply With Quote
  #7  
Old 10/26/07, 7:44 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by mlarson
Still think so?
Well, I wasn't on-site, but if you draw a line straight down from the outlet, it's inside the tub area.

Look for yourself...

"Click To Enlarge"
lightswitch-tub-area-img_2436-20-28small-29.jpg
Reply With Quote
  #8  
Old 10/26/07, 8:03 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by dvalley
Well, I wasn't on-site, but if you draw a line straight down from the outlet, it's inside the tub area.

Look for yourself...

"Click To Enlarge"
Attachment 15569
David, I agree with you but seems a gray area in the (word we don't use). The location in my pic is just as accessible as the one in John's original post.

Let me through in another question for thought:

How far would the wall behind the actual tub foot print in my pic have to be before the switch location became a non issue?

Last edited by mlarson; 10/26/07 at 8:06 PM..
Reply With Quote
  #9  
Old 10/26/07, 8:05 PM
John H. Cooper John H. Cooper is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Juneau, AK
Posts: 26
Default Re: Lightswitch In Tub Area

Hmm. I have to admit, the drawing is straightforward. Still, the switch is over the tile, which is part of the tub structure. The drawing shows the switch over the floor.

I guess I am stuck on the intent. If you need to install a fan/light, which is in the ceiling, on a GFCI protected circuit (per the manufacturer's instructions) why would you not need to install a 120v light switch, that was clearly installed so that the occupants of the tub can reach it, with GFCI protection at least?
Reply With Quote
  #10  
Old 10/26/07, 9:37 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by jcooper2
Gentlemen,

Today I found this dimmer control for the lights over a whirlpool tub. The dimmer is over the horizontal surface of the tile, but not directly over the tub itself. It is the right-most of the three coverplates in the picture, and is OBVIOUSLY put in that position to be reached from within the tub. The light switches for the rest of the bathroom are on the other wall, and don't control these lights. It is NOT protected by the GFCI serving the bathroom. I think it is dangerous. What do you think? At a MINIMUM, I think they should wire it to the GFCI protected outlet that is less than eighteen inches away. The third coverplate in between the two is for cable-tv and a phone.
Is that a fridge?? First I've seen that set-up in a bathroom (coffee maker and fridge)
Reply With Quote
  #11  
Old 10/26/07, 11:19 PM
John H. Cooper John H. Cooper is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Juneau, AK
Posts: 26
Default Re: Lightswitch In Tub Area

Yeah Brian, That is a fridge. It kinds of reminds me a a hotel room.

You know, stepping back a minute. There really isn't that much different here than in the kitchen or bathroom where you have your hands under the water, or holding the sprayer, and reach up to turn on the light or the garbage disposer. The current, were your hands to be wet and somehow the water got to the conductor, would run down one arm, through the heart, and out the other. You would be just as dead, or at least severely hurt, as if you reached up to that switch from the tub.

Only you wouldn't be floating around in your all in all when they found you...
Reply With Quote
  #12  
Old 10/27/07, 8:08 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by mlarson
David, I agree with you but seems a gray area in the (word we don't use). The location in my pic is just as accessible as the one in John's original post.

Let me through in another question for thought:

How far would the wall behind the actual tub foot print in my pic have to be before the switch location became a non issue?
If the Electrician simply installed this switch 4 to 5 inches to the right, like this..
lightswitch-tub-area-img_2436-20-28small-29.jpg(outside the outer rim)

then it would have been all set.
Reply With Quote
  #13  
Old 10/27/07, 8:12 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: Lightswitch In Tub Area

In John's original picture (butt ugly bathroom, imo) or Michael's I can't see a non-destructive access panel to inspect the pump motor bonding and possibly GFCI receptacle for the hydro-tub.

I call access absence all the time as well as depicted switches.

"although the hydro-tub switch location may pass past or current AHJ building standards, I advise removal and coverplate installation too avoid the potential for electrocution."

I don't need anything but common sense to report what I find and will leave the fighting to the homeowners, builders...

The rest would be up to the consumer to choose their fate.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #14  
Old 10/27/07, 8:22 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by badair
In John's original picture (butt ugly bathroom, imo) or Michael's I can't see a non-destructive access panel to inspect the pump motor bonding and possibly GFCI receptacle for the hydro-tub.
You are absolutely correct Barry and it was reported as such but that wasn't the point of the thread

When I first observed this I thought maybe acesss was through the vanity sidewall but none there either. Why the AHJs approve this type on installation is beyond me.

I still would like to see the professional opinion of some of our sparkies on the light switchbox placement. I think the NEC is a bit unclear on this issue and the diagrams I've seen never seem to show this type of situation. I guess that leaves it up to the AHJs and us poor HIs.
Reply With Quote
  #15  
Old 10/27/07, 8:31 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: Lightswitch In Tub Area

Quote:
Originally Posted by mlarson
You are absolutely correct Barry and it was reported as such but that wasn't the point of the thread

When I first observed this I thought maybe acesss was through the vanity sidewall but none there either. Why the AHJs approve this type on installation is beyond me.

I still would like to see the professional opinion of some of our sparkies on the light switchbox placement. I think the NEC is a bit unclear on this issue and the diagrams I've seen never seem to show this type of situation. I guess that leaves it up to the AHJs and us poor HIs.
Got it, but in my pea-brain if I can't verify the "other" required electrical installation features it helps to better drive my points across to my clients that the entire hydro-tub installation may be incorrect. thus they may be more apt to remove and cover as in your photo.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chicago Area Homebuilder Files for Bankruptcy ldapkus Miscellaneous Discussion for Inspectors 1 10/23/07 10:26 AM
Bay Area Prices Looking Up! whandley Miscellaneous Discussion for Inspectors 0 4/26/07 12:29 PM
Phoenix area Chapter Meeting - Jan 24th cvowell General Inspection Discussion 0 1/11/06 6:00 PM


All times are GMT -4. The time now is 10:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts