I would say more than 50% of the panels I inspect dont appear to have a bonding strap.

Am I correct to recommend a sparky to verify presence and to install.

Do the ellectricians forget to install? Is there a hidden bond that I am not seeing. If so then should the little green screw be removed?

Another question. All baths..1/2, master & 2nd floor where controlled by a GFCI outside the panel. This is an acceptable install correct?

Thanks
Attached Thumbnails
little-green-bonding-screw-87506-brunswick-019-small-.jpg.jpg
Views:	165
Size:	52.5 KB
ID:	7740   little-green-bonding-screw-87506-brunswick-020-small-.jpg.jpg
Views:	157
Size:	59.3 KB
ID:	7741   little-green-bonding-screw-87506-brunswick-021-small-.jpg.jpg
Views:	144
Size:	57.1 KB
ID:	7742  
Reply With Quote
  #2  
Old 12/12/06, 6:12 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
Send a message via MSN to cbellefontaine
Default Re: Little green bonding screw

In the first picture, the green screw in the neutral buss bar is your bond.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #3  
Old 12/12/06, 6:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Little green bonding screw

Dave,

All panels like the one you show should be bonded from the terminal grounding/grounded bar to the panel enclosure as this is a true main panel.'

Now in many cases you have either a green screw going directly through the terminal bar and screws into the panel itself.....or you could have a "Z" grounding bar which would not be green......but would serve the same purpose and also possibly you will see an actual bonding strap in many panels.

I just simply cant tell enough in these pictures....my eyes MUST be going back but in all cases if you are not able to observe the bonding of the grounding/grounded bar to the enclosure on this MAIN panel ( we are not talking a sub here )...then you most certainly should write it up....

As for the bathroom GFCI question.....yes, the GFCI can be located as a GFCI receptacle in one of the bathrooms and it can control the other recepts in the other bathrooms....perfectly fine as it does not have to be a panel installed GFCI to meet the requirement.

OH...I wanted to add.......it is important guys that if you DO have trouble finding the bonding point that get as close a picture of the buss bar as possible for us here......e-mail it to me if you wish.......but I would venture to say the screw on the left is the bond.....and yes it should be green...but again my eyes are leaving me it seems on these online images.

Also equally important to note if the system is bonded correctly to the piping enclosed in the house, important to note if you find a water pipe only GEC...that you suggest a supplimental grounding conductor as well........to aid in the lightning issues and TVSS issues that are possible in any home.

I think someone should talk NICK into having a Grounding and Bonding Session at the up coming Convention...lol.......



Paul W. Abernathy

Last edited by pabernathy; 12/12/06 at 6:20 PM..
Reply With Quote
  #4  
Old 12/12/06, 6:21 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Little green bonding screw

Chris & Paul

Thanks

As long as the green screw is in contact with the panel then this is OK? Then a strap isnt needed. The screw does look like it makes good contact. Actually I can see the light?

This would be fine.
Reply With Quote
  #5  
Old 12/12/06, 6:23 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Little green bonding screw

Yes, that is one of the methods used by the Manufacturers...some will come only with the strap...some with the "Z" bar....but the green screw you are refering to is thread into the proper opening provided by the Manufacturer and it will serve the purpose of bonding that enclosure fine.



Paul W. Abernathy
Reply With Quote
  #6  
Old 12/12/06, 6:29 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Little green bonding screw

Paul

I will be glad when I can figure this out for myself & stop asking you guys.

I learned something in regards to this. I would always look for the bonding screw but I would never look to see if it made contact. It is nice to have a clean install like this one where you can see everything.

Thanks again.
Reply With Quote
  #7  
Old 12/12/06, 7:59 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Little green bonding screw

Steve,

I think dave is refering to the connection point for the bar to the enclosure ( bonding screw or strap or "Z" strap )....sometimes they are hard to find in a cluttered panel......but should be present or it should be called out. The bar indeed connects across the back and many times the green bonding screw will go through the middle somewhere....but in this case it probably goes through the terminal points on the bar to the enclosure...



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel Bonding Screw away Electrical Inspections 24 1/9/08 2:46 PM
Steel post question sspradling Structural Inspections 42 3/2/07 8:59 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM
Is the there a 'bonding' screw that I don't see. mgault Electrical Inspections 9 10/13/06 10:31 AM


All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts