is it ok to splice from breaker to solid wire (solid wire was not long enough to get to braeker) with12awg stranded wire. this is a 30 amp breaker. I would put a couple of pics but havnt figured it out yet and kinda need an answer quickly. I dont believe it is ok
Reply With Quote
  #2  
Old 2/8/06, 3:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: a little help

Richard,

Since you are in a hurry I will leave out the code references......1.) If the wire to the breaker is too short and it is in existing work go ahead and splice a wire via WIRENUT to the wire and run a new one to the breaker....HOWEVER...if it is a 30A breaker...you cant use # 12 AWG wire...it needs to be # 10 AWG wire......

So while splicing is fine and in some cases the only thing you can do...it is not ok to splice a # 12 AWG to a 30 A breaker......the breaker must be sized to protect the wire at its smallest size so to speak...in this case it would not be...so it is a big NO to the 12 AWG.........and I wont go into the places that you CAN do it....just based on the info you provided it is incorrect to do it.

Hope this helps



Paul W. Abernathy
Reply With Quote
  #3  
Old 2/8/06, 3:04 PM
rcantrell rcantrell is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Anderson, SC
Posts: 43
Default Re: a little help

Thank you I also thought the wire was too small
Reply With Quote
  #4  
Old 2/8/06, 3:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: a little help

Yep.....and you will get those clients who have a 20A CKT in 12 AWG run to a 30A breaker because the 20A one tripped all the time.......a serious NO-NO.....unless in a specific application where it is allowed...and we wont go their right now..thehehe....WE will keep it simple...tell them to buy some # 10 AWG wire and be done with it....UNLESS the wire that is too short is # 12 AWG as well.....then they need to buy a NEW breaker that is 20A.....



Paul W. Abernathy
Reply With Quote
  #5  
Old 2/8/06, 3:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: a little help

Quote:
Originally Posted by pabernathy
12 AWG run to a 30A breaker ......a serious NO-NO.....unless in a specific application where it is allowed...
Common in many condenser units. Check the panel labeling (if it exists). Otherwise, defer it. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/8/06, 6:14 PM
Robert Wade Robert Wade is offline
New User
 
Join Date: Sep 2005
Posts: 7
Please Note: Robert Wade is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: a little help

I have been told that under no circumstances are wire nuts acceptable in a breaker panel and that the condition should be called out as a defect, just like double lugging. Or is this a different situation?
Reply With Quote
  #7  
Old 2/8/06, 6:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: a little help

I believe you have been misinformed. Although panel boards are not technically "junction boxes," wire nuts are not specifically disallowed.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 2/8/06, 7:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: a little help

Dang Jeff....Did you not read my post...lol...I said I did not want to go their...lol



Paul W. Abernathy
Reply With Quote
  #9  
Old 2/8/06, 7:24 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: a little help

The only limitation to the panel is in space and how much you take up of it....nothing against wirenuts in the panel itself so calling that out is incorrect.

In fact the simple solution sometimes to a client that has double taps and no space left in the panel is to tell them to remove the wires from the breaker.....wirenut them together and take a pigtail to the breaker so only one is on the breaker.....NOW....make sure they size the pigtail to match the wire sizes that were on the breaker...and make sure the wires are all the same AWG........but this removes the double tap issue.....

NOw I am not saying homeowners need to do this...BUT you know they will try anything once...might be the last time they try it but it will remove the issue of double tapping.....not to take the place of doing actual load calculations which the HI should not attempt...



Paul W. Abernathy
Reply With Quote
  #10  
Old 2/8/06, 7:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: a little help

I went there for you Paul



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/8/06, 8:49 PM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: a little help

good info




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #12  
Old 2/9/06, 12:00 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: a little help

lol...I feel the love Jeff.....I truly feel the love...NOT..lol



Paul W. Abernathy
Reply With Quote
  #13  
Old 2/9/06, 10:47 AM
Robert Wade Robert Wade is offline
New User
 
Join Date: Sep 2005
Posts: 7
Please Note: Robert Wade is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: a little help

Jeff and Paul, Thank you for your help.
Reply With Quote
  #14  
Old 2/9/06, 11:09 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: a little help

Also...just in case you would like some light reading....

NEC Art 312.8 - Defines it quite well.....in laymans terms the splices ( ie: wirenuts ) SHALL NOT fill the wiring space at any cross section to more than 75% of the cross sectional area of that space....

Now......dont even bother with trying to solve that math.....when you see a overly crowded panel with NO room at all within it...you can BET it breaches that requirement as well as 312.7.....but figured you should know....

also important to note that a Service Enclosure is not a junction box...by any means...as Jeff stated...while you can splice to extend as in the explanation above....you cant use it to junction to other OCPD enclosures per say....Unless space is provided in the enclosure for this purpose....yada...yada..yada......you get the point.



Paul W. Abernathy
Reply With Quote
  #15  
Old 2/9/06, 1:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: a little help

I think, if someone did challenge you to do the math, it would be hard to show >75% fill.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:57 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts