Default A little help...

Here's the main panel for a home I did yesterday. There was a lot of handyman wiring throughout the house, and I just wanted to get some opinions on the panel. Please? It's a 150A service, and there's a handyman-done 2nd panel feeding a detached shed...
Thanks for your help...
Attached Thumbnails
little-help-p1040987.jpg   little-help-p1040989.jpg   little-help-p1040990.jpg   little-help-p1040991.jpg   little-help-p1040997.jpg  




Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #2  
Old 10/11/07, 10:27 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 941
Default Re: A little help...

Also, the cover was off the panel, but the whole thing was covered by a plywood panel, painted to match the wall. Is this an acceptable replacement for the original panel cover?



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #3  
Old 10/11/07, 10:37 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,441
Default Re: A little help...

Quote:
Originally Posted by acox
Is this an acceptable replacement for the original panel cover?
Absolutely not.

There are a ton of problems with these panels. Rather than having us "pick them apart," defer the whole mess for corrections. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 10/11/07, 10:43 AM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: FL panhandle
Posts: 3,744
Default Re: A little help...

Yeah, this is a perfect example of what things "not" to do in a panel. A cornucopia of discrepancies.



Doug Edwards, CMI







Reply With Quote
  #5  
Old 10/11/07, 10:44 AM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 354
Default Re: A little help...

Quote:
Originally Posted by jpope
Absolutely not.

There are a ton of problems with these panels. Rather than having us "pick them apart," defer the whole mess for corrections. . .
I agree, usually if I find three minor electrical errors, or one big one, then I defer to an electrician. If it's for minor stuff (missing GFCI, etc), then I explain to them that if I found three errors, how many do you think a qualified electrician will find? I know it will be more then three!

BTW, what is going on with the main on this panel? Looks like they have both the supply lines and something else under those taps... Did they bypass the main for something? Those I write up as a safety hazard as well.
Reply With Quote
  #6  
Old 10/11/07, 10:50 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,412
Send a message via Yahoo to jfunderburk
Default Re: A little help...

They double-lugged the panel...the feeders at the top are apparently supplying power to the sub-panel without the benefit of overcurrent protection. Bad. Bad. Bad.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 10/11/07, 10:54 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 941
Default Re: A little help...

The subpanel is right next to the main, and they've tapped that into the mains... This feeds the "shed out back..."
Attached Thumbnails
little-help-p1050002.jpg  



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #8  
Old 10/11/07, 10:57 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 941
Default Re: A little help...

Not to mention the open boxes...
Attached Thumbnails
little-help-p1040970.jpg   little-help-p1050007.jpg  



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #9  
Old 10/11/07, 6:47 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 137
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A little help...

Let me step in here i did see more than few electrical code voilations allready

1] double tapping at main breaker that is a very serious no-no.

2] The GE breakers they are not listed for double lugged aka double wired.

3] the subfeed box used as second main breaker box IMO this is not a very safe pratice because if someone working on the subfeed box left of the main breaker box and someone turn off the main breaker and the subfeed box still alive that is very serious issue there

4] wooden panel cover that is a big no no also

5] doubled lugged at the netural bussbar

IMO the doorbell transformer should be outside of breaker box becuase the secondary side.

this breaker box should be replaced with proper breaker box with plenty breaker space in there

Merci, Marc

Let me add one more item i almost forgot but have to reedit this real quick

uncoverd repectales is a no no and the way the box mounted it sound like someone did not take the time to do this correctly
Reply With Quote
  #10  
Old 10/11/07, 8:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A little help...

You have enough info here to simply defer it......that sub panel is set up imporperly.....it is a "remoe distribution panel" and is simply wrong.

I wont go into all the little details because we have done this many times....now never ask if a combustible product will never take the place of a metal cover....lol....thats a given and should never be in question.

Defer the electrical system to a LICENSED electrical contractor and let them deal with this mess.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #11  
Old 10/11/07, 9:38 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 910
Default Re: A little help...

Quote:
Originally Posted by Marc Benz
Let me step in here i did see more than few electrical code voilations allready

1] double tapping at main breaker that is a very serious no-no.

2] The GE breakers they are not listed for double lugged aka double wired.

3] the subfeed box used as second main breaker box IMO this is not a very safe pratice because if someone working on the subfeed box left of the main breaker box and someone turn off the main breaker and the subfeed box still alive that is very serious issue there

4] wooden panel cover that is a big no no also

5] doubled lugged at the netural bussbar

IMO the doorbell transformer should be outside of breaker box becuase the secondary side.

this breaker box should be replaced with proper breaker box with plenty breaker space in there

Merci, Marc

Let me add one more item i almost forgot but have to reedit this real quick

uncoverd repectales is a no no and the way the box mounted it sound like someone did not take the time to do this correctly

Thanks for listing out the defects. I saw a few things wrong but other things I wasn't aware of. I consider this topic to be one that I need the most assistance with. It helps to be able to explain the buyer in some degree of detail just why an elec. is being called in. If I just say it's a panel with alot of issues there first question is what are the issues? I had to get into a big explanation with a buyer over the weekend as to the proble with his FPE in the master closet (69 build). Fortunately the FPE wasn't wired like this one and did not appear to have had previous defects.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #12  
Old 10/12/07, 2:57 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 941
Default Re: A little help...

Thanks for the responses - I opened the box and I think the words were, "Oh Sh...!" Marc - thanks for the list - pretty much what i have in my report...
I just talked to my client yesterday and he's going to the seller with these pictures, to start the negotiations...
Guess this is where a pre-list inspection could have saved some surprises...



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #13  
Old 10/13/07, 3:59 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 941
Default Re: A little help...

It's getting better - the buyer just called me. he apparently told the seller that if he wants to sell, he needs to replace the roof (another mess) and have an electrician look at the panel.
The seller - he's selling for the Estate of his deceased mom - said he does electrical work, and he'll take a look at it.
I told my client not to accept that. He's ready to drop the deal because of it. He has an ill wife and a mother-in-law on constant oxygen living with him.
He doesn't need these headaches...
Looking at the possibilities he could have stepped into - I'd be kind of glad to kill this deal -



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:57 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts