#1
|
||||
|
||||
|
Today's inspection was a first for me. To date I've never came across Knob and Tube wiring which was "live". The home has a 125AMP max panel and another panel in the stairway of the basement which has four fuses I'm assuming powering the Knob and Tube. The home was built in 1929. How should I call this out. Please take a look at the pictures below and let me know what issues you see. I'm still trying to learn everything about electrical. Please be specific so I can understand exactly what your talking about. Thanks everyone I sincerly appreciate you sparky guys and everyone else.
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com Last edited by bboerner; 9/29/09 at 6:42 AM.. |
| Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Quote:
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#3
|
||||
|
||||
|
Billy,
Whenever I encounter a LIVE K&T system, I simply tell my clients that the there are a lot of insurance companies who will not insure them with this type of wiring. I then give them a link to my website...http://www.masscertifiedhomeinspections.com/?D=99 , and let them decide. |
|
#4
|
||||
|
||||
|
Excellent. Do you see any issues within the main panel?
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#5
|
||||
|
||||
|
Quote:
You can confirm this by looking for a neutral wire with the same aluminum coating. There are times where I can see the ends of the neutral wire (where it was cut) and confirm my suspicions. |
|
#6
|
||||
|
||||
|
Good to know. Anything else with the panel that you see?
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#7
|
||||
|
||||
|
Where's the disconnect? Is this LSE? |
|
#8
|
||||
|
||||
|
The forth pix shows the aluminum neutral wire. David is correct about the insurance company not insuring home with K&T. Last home that had it the client couldn't get insurance until K&T was removed.
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
|
#9
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like you have a ground an neutral wire under the same screw in the last picture
|
|
#10
|
||||
|
||||
|
Billy, here are a couple things I see.
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
|
#11
|
||||
|
||||
|
Also the wires under the 40 amp breaker look too small, compare to the rest of the wires. It is always a good idea to have the neutral wire and the ground wires on separate bussbars if you want to be choosy.
Is the 60 amp breaker going to the subpanel? Is your disconnect at the meter? |
|
#12
|
||||
|
||||
|
Here are a few more.
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
|
#13
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here in Fl, especially if they are insured with Citizens, that fuse panel would need to be replaced with a breaker panel.
FYi - fuse panels (or breaker panels) are not made to last forever. I would recommend replacement regardless |
| Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America) |
|
#14
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
||||
|
||||
|
Do I see a single pole 30 amp breaker? Paul mentioned these in his video. Are these unique? Any problems with these?
David InterNACHI #08051301 NYS Lic. #16000038229 NYS DEC Cert # T4865884 518-505-8305 HouseAbout Home Inspections HouseAbout on Facebook NY Capital Region Chapter InterNACHI |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Buried Knob & Tube | brepanshek | Electrical Inspections | 14 | 2/15/07 10:12 AM |
| K&T splice. | egarcia1 | Electrical Inspections | 13 | 2/3/07 7:36 AM |
| Insulated Knob and Tube? | scosta | Electrical Inspections | 6 | 2/3/07 7:22 AM |
| Knob and tube | wblakey | Electrical Inspections | 17 | 11/14/06 8:41 PM |