Default Live weather cover

Does anyone have any idea why an outdoor weather cover would set off a voltage sniffer and continue to do so even after I trip the GFCI upstream and cut power to the receptacle? The three-light tester reads OK and I have touched the cover without a shock.
Reply With Quote
  #2  
Old 10/19/06, 8:31 PM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

I should add... this is my own home. It's a new receptacle on old wiring, some of it UF buried in conduit. The voltage disappears when I throw the breaker, but not when I trip the GFCI at an upstream receptacle. Based on this, I'm thinking the ground might be compromised by a live wire upstream of the GFCI. Does that make sense? I'm trying to figure out what to look for. If this were an inspection, I would just say, "consult a licensed electrician"...
Reply With Quote
  #3  
Old 10/19/06, 8:44 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

You say the three light tester reads "OK". What does this mean?
Does it read ok as in live and wired correctly even when the GFI is tripped?
Or ok as in dead, no lights?

Also, what is a "sniffer"? Do you mean a non-contact voltage tester? Like a volt-tick?
Reply With Quote
  #4  
Old 10/19/06, 8:47 PM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Yes, the tester has the correct two-light display when the circuit is powered. When the GFCI is tripped, the tester is dark. And yes, I'm talking about a non-contact pen-type voltage detector.
Reply With Quote
  #5  
Old 10/20/06, 10:38 AM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

I realized this morning after I'd turned the breaker off that two old ungrounded indoor receptacles are on the same circuit. I'm thinking that a previous homeowner must have spliced into an ungrounded circuit and created some sort of bootleg ground that is carrying a small amount of current. Maybe they even tied it into a neutral? Looks like a project...
Reply With Quote
  #6  
Old 10/21/06, 9:10 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Live weather cover

Jeff,

If you do not figure it out...let me know...I am only about 35 minutes from you and will look at it for you if needed.

It also sounds to me off hand like the receptacle was added to the old circuit and is not actually downstream of the GFCI....otherwise the GFCI being tripped ahead of it would kill it....

Check to see if they did not tap the old circuit and connect to the LINE side of the circuit...rather than the load side of the GFCI protected portion of the circuit.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 10/21/06, 12:10 PM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Thanks, Paul. I'll keep you posted.
Reply With Quote
  #8  
Old 10/21/06, 12:15 PM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Paul, just to be clear, the GFCI does trip the receptacle itself. It just doesn't trip the weather cover! This sort of thing frightens me because it's something I wouldn't notice during a normal inspection.
Reply With Quote
  #9  
Old 10/21/06, 2:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Live weather cover

Jeff,

I have to ask.......when you say it wont trip the "weather cover" are you expecting the COVER itself to do something...lol.....now you are confusing me fella...lol..and I have been doing this for 20 years....lol

The cover itself should not do anything...thehe...ok....maybe you better just call me..540-607-0116 before i fly out to California....I hate flying !



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 10/23/06, 8:12 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Those non-contact testers can fool you, especially on older two wire systems. My tester lights up when I get within 6" of a receptacle in my house.
Also, keep in mind that when you trip the GFCI you still have power to the line side wiring and that may be what your tester is detecting.
Like any tester non-contacts should not be relied upon solely. Use a good voltage meter and use the 3 step test (1.Test a known live circuit to test the meter, 2.Test the circuit in question, 3.Test a known live circuit to re-test the meter) to verify that it is working properly.
Reply With Quote
  #11  
Old 10/23/06, 10:39 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Live weather cover

Steve,

I think he stated the GFCI is up stream and tripped.....I agree on the non-contact tester..always verify as some will even detect as low as 30 volts.....but I think the issue may be an improper wired GFCI upstream......I am sure Jeff will keep us posted.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 10/31/06, 6:59 PM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Hi guys. I was a long time in getting back on this thread; I'm sure you all thought I'd been electrocuted. Paul, I've been meaning to call you anyway; hopefully I'll get to it sometime this week.

I have used a multimeter on the circuit. The ground wire is what what conducting current. I knew the non-contact tester wasn't lying when I got shocked by touching the weather cover (nothing serious, obviously). The problem exists upstream of any GFCI and I discovered it on another circuit as well.

I should have been tipped off to the source of the problem when the circuit tester indicated a proper ground on a circuit I knew was not connected to earth via the panel. Both of these circuits are wired with 3-wire romex at the receptacles, but older 2-wire in hard-to-reach parts of the crawlspace and chase. Although I can't see all the wiring, my guess is that someone rigged up a makeshift ground which is somehow in contact with something live (12V doorbell circuit, maybe?)

Anyhow, since the GFCIs bestow some of the benefits of a true ground and the circuit wasn't really grounded anyhow, what I did for the short term was to just disconnect and isolate the ground wire from the upstream receptacle. Now it's running like an old-fashioned 2-wire circuit on a GFCI and I can touch the weather cover all I like.

I'd still like to figure out where the stray current is coming from, and someday I'll rewire everything back to the panel.
Reply With Quote
  #13  
Old 10/31/06, 10:38 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Jeff, maybe you have a bootleg ground on this circuit and you now have some neutral current on the grounding wire, which is in direct contact with the metal box.
Reply With Quote
  #14  
Old 10/31/06, 11:31 PM
jnicholson jnicholson is offline
New User
 
Join Date: Aug 2005
Location: Waynesboro, VA
Posts: 40
Please Note: jnicholson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Live weather cover

Yeah, the bootleg ground is what I've been suggesting. If it's tied to a neutral, however, I think it's a neutral on a different circuit.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Vinyl siding installation guide badair Exterior 18 3/27/07 6:38 PM
Weather head dmacy Electrical 3 2/8/06 8:19 AM


All times are GMT -4. The time now is 2:58 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts