Default Living room circuit

My mind is not working tonight...
Inspected a house built in 1966. Most of the electrical was great, but one outlet in living room was dead, then 2 others showed ok with the tester.

When I check an outlet, often, I press the GFCI test button, just to see if it does something. One time I found a living room with GFCI outlets all around...
Anyway, these other 2 outlets were OK, but with the trip button pressed, the middle light and the Red light came on, indicating the Hot/Neutral reversed - only when the GFCI trip button was pressed in.
What does this indicate? Please?



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/27/10, 9:41 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Living room circuit

It means nothing.
Reply With Quote
  #3  
Old 7/27/10, 9:53 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Living room circuit

Built in 1966....I bet two things...the living room did not have a ceiling light fixture and second, that "dead" outlet is on a wall switch so a lamp could be plugged into it and when someone enters the room they can turn on a light (lamp) at the wall switch. See it all the time especially in older homes from that era.

I plug a tester into the receptacle then try all the switches at the entrance areas until I find the one that operates the receptacle, identify it to the customers.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #4  
Old 7/27/10, 10:05 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: Living room circuit

Doug - that's the 1st thing I try - the outlet was dead - not controlled by the switch. There is a ceiling fixture. I am sure that at some time, some wiring work was done as the kitchen and baths have GFCI outlets.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #5  
Old 7/27/10, 10:09 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Living room circuit

Then it is still easy to write up and let the electrician "finger it out".



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #6  
Old 7/28/10, 9:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Living room circuit

Quote:
Originally Posted by acox View Post
Anyway, these other 2 outlets were OK, but with the trip button pressed, the middle light and the Red light came on, indicating the Hot/Neutral reversed - only when the GFCI trip button was pressed in.
What does this indicate? Please?
It indicates that your finger was on the "trip" button.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM
Smokes on AFI circuits lprinzi Electrical Inspections 9 7/6/06 9:12 PM


All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts