came across a loudly buzzing "load clipper" as was stated on the label. 2 circuits inside...1 attached to heat pump and the other to stove. 1 of the circuits looked like it was burned (electrically). Label said 30 amp max, circuit "must open" at 15 amps. I guess this is some sort of pre-historic gfci? Recommended an electrician take a look since the circuit was burned and was buzzing pretty good. insight?
|
|
#2
|
|||
|
|||
|
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#3
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Brian,
Is that a members only section? When I clicked on it, the box that says I don't have priviledges popped up. |
|
#4
|
|||
|
|||
|
DSCN1124.jpg
Sorry Scott. Electrical load controller, turns off one piece of equipment when power use goes up. Popular in the 1970's after the energy crisis. I always defer them. "Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#5
|
|||
|
|||
|
A "buzzing"sound coming from an enclosure containing a relay usually signifies a relay armature that is not closing completely due to things like rust, sticking mechanism, movement blocked by insect activity, etc. The result can be a burned load contact and eventually failure to compelte th circuit. No matter - the relay probably should be replaced.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
![]() |