Hey folks,
Inspected this home, new construction, SE beside meter with a 4-wire feed to the load side panel. The grounded and grounding conductors are both on the same bus in the load side panel, and multiple grounded conductors were installed in each lug. Can someone give me a IRC or NEC code reference for these violations. Thanks, Steven |
|
#2
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
NEC 408.21 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
The other is a bit trickier to quote but you can start at... 250.24 (A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article. (None of those exceptions would apply). It might be easier to just say "Neutrals may not be bonded to the grounding system anywhere but the Service Equipment.". No electrician should argue with that...No code needed. Last edited by rmoore; 5/3/06 at 5:02 PM.. |
|
#3
|
||||
|
||||
|
You might also include that the grounding conductors must be bonded to the load side panel.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I also don't see any bonding of the service panel-----anyone know if bonding via the meter base is acceptable?
|
|
#5
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the code references. I have got to get a NEC manual. Both panels are bonded. SE by use of bonding screw and the load side panel has a bonding clamp installed into a lug on the bus with Neutral/Grounds (wrong). These are typical findings in this builders homes. I had at least 21 deficiencies including at least 10 code violations which were mostly electrical.
|
|
#6
|
|||
|
|||
|
Please Note:
rain252 is a non-member guest and is in no way affiliated with InterNACHI or its members.
It also looks like the neutral conductor coming from the meter ought to be tagged white on its black insulation to identify it as the neutral.
|
|
#7
|
||||
|
||||
|
Quote:
Personally.....We always take the GEC to the Service Panel...on all homes..we ONLY change it in wintergreen IF the local AHJ demands it. lol........this looks like the mobile home feed thru's we use down here...If the image to the LEFT is the panel inside....and back to back it could be still 3 wire...all this is still considered outside of the building.... If it is changing over to 4 wire because the panel is remotly located furthur in that point of entrance then the GEC should leave from this panel shown( on the right )......thus the indoor panel become a 4 wire SUB....BUT based on this panel if the feed through at the bottom does not have a breaker to shut it off....and the panel inside is REMOTE....it would be wrong. Man.....you gotta forgive me tonight guys..I am beat...short handed and swamped....I am outta here for the night... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 5/3/06 at 7:36 PM.. |
|
#8
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just wanted to pass on to you all, that the Building Official was called to inspect these panels and informed the builder that these panels conformed to current building codes. There is no problemo!!!
|
|
#10
|
|||
|
|||
|
Quote:
If you write "it" up and recommend corrections by a qualified electrician "for enhanced safety" you do away with the code reference while still covering yourself. Just an idea. |
|
#11
|
||||
|
||||
|
Quote:
It may be that they were passed, but there is no code that allows for this installation. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Steven,
if you feel their is a major issue then by all means you can go over the local AHJ's head and go to the head building official and state your case....in terms of the images shown..... 1.) If the picture on the LEFT is the panel located within the house that is controlled by the MAIN breaker of the image shown in the picture to the right then the installation of the panel located in the image to the left is wrong... Variables: If the panel in the image to the left is DIRECTLY behind this and a 4 wire was run...BUT not seperated at the indoor panel as shown here then you have additional issues......so we wont go their. We really need to know the FULL story of this setup.....if the panel in the image to the LEFT is not controlled by the main breaker in the image to the right and is simply fed from the bottom and is a feed thru style then the inspector would be ok in his comments....but again depends on that main breaker....in the image to the right..... Conclussion- Based on the way the image on the right lOOKS to me...the panel shown on the right...SHOULD be the location of the GEC and GE for the system.....the fact the EC ran (4) wire from this panel to the panel image shown on the left inside....means it is a "remote distribution panel" and the grounds and neutrals should be separated as called for in the NEC. However...is their ANYTHING else in this setup you are not listing...... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#13
|
|||
|
|||
|
Please Note:
Steven Brewster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hey guys,
Update, talked to the builder last PM and discussed the panel issues. Reinspected the home this morning and the neutrals and grounding conductors have been separated in the load side panel and the boding clamp removed from the neutral bus. I was amazed that they did the right thing. Paul, the exterior panel (SE) has a 4 wire feed (approximately 30' of conductor) to the inside panel (sub or non service rated panel). Thanks for all of the input, and code references. |
|
#14
|
||||
|
||||
|
Steven,
Excellent.....See.......You look like a hero and MAYBE the electrician learned something....lol......glad they are not in my apprentice class as I would give them hell for 4 years..... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#15
|
||||
|
||||
|
I have seen many service equipment panels that are just plain wrong, but had just been passed by a local AHJ inspector.
That's why I don't bother citing code (and am, in this state, prohibited from doing so), I just point out national standards, like the NEC, but only as a national standard, as also mentioned in our state law. Inspected a new townhouse in a small local town. They had only accepted an old NEC and had many local variances to the NEC. No GFCI or AFCI protection. It was 'code' (according to the local AHJ) but was dangerous (or, at least, not as safe as modern standards would have it). Again, the client (and his lawyer) were confused. As usual, they believed that there was no higher standard than the village code. I explained the realityies of life (and politics) to them for about 20 minutes, and they finally got it. They decided that they did not want to buy a house where the builder had so little regard for their safety. A tough row to hoe, we have. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Where do I put the Aquarium? | mcyr | Structural Inspections | 3 | 11/6/07 4:05 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Sub or load side panels | mtimpani | Electrical Inspections | 9 | 1/25/06 10:23 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |