Default Load side/reverse polarity?

A friend of mine just had a home inspection done on a rental property for his buyer. The inspector said all of the GFCI outlets have the load on the wrong side. My friend asked if they had reverse polarity. The inspector said no that he had to switch the load wires. What? This did not make sense to me. Does anyone know what the inspector was refering to?
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #2  
Old 4/2/09, 2:24 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Load side/reverse polarity?

GFI receptacles have 2 sets of terminals, LINE and LOAD. Line is for the incoming power, LOAD would be used to protect other receptacles downstream of the GFI receptacle.
Reply With Quote
  #3  
Old 4/2/09, 2:39 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Load side/reverse polarity?

From www.ecmweb.com :
Quote:
Line-load terminals. All GFCI receptacles have two sets of terminals having screws or wire leads. One set is typically identified as "LINE," the other as "LOAD," again as shown in Fig. 2. Conductors from the branch circuit overcurrent device are intended to be connected to the "LINE" terminals, and conductors feeding other downstream receptacles or loads (if intended to be protected) are connected to the set of terminals marked "LOAD."

Note that the receptacle outlets integral with the GFCI receptacle are on the load side of the current interrupting contacts and thus protected by the GFCI when properly wired. If the "LINE" conductors are connected to the "LOAD" terminals (essentially back-feeding the GFCI receptacle), then note that the integral receptacles are in the circuit before the current-interrupting contacts and are therefore not protected. If the GFCI is miswired and the "test" button is pushed, the 6mA differential current will still flow as before and the GFCI will trip, even though protection will not have been provided to the receptacles integral with the GFCI. Downstream receptacles, however, will be protected because they are on the protected side of the circuit-interrupting contacts. Therefore, it's important that you follow manufacturer's wiring instructions explicitly.
Reply With Quote
  #4  
Old 4/2/09, 2:59 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Load side/reverse polarity?

Quote:
Originally Posted by kmalone View Post
A friend of mine just had a home inspection done on a rental property for his buyer. The inspector said all of the GFCI outlets have the load on the wrong side. My friend asked if they had reverse polarity. The inspector said no that he had to switch the load wires. What? This did not make sense to me. Does anyone know what the inspector was refering to?

Do not confuse load wiring with the 'hot' conductors. As Michael stated, the line wires (coming in) were put into the load terminals (going out) and vice versa. Also, make sure that when the hots are switched around, that the neutrals are switched around, too (assuming they are also incorrect).

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #5  
Old 4/2/09, 4:26 PM
Kenneth R. Malone Kenneth R. Malone is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Sycamore, IL
Posts: 70
Default Re: Load side/reverse polarity?

Can this be detected with a simple 3 light testor or do you need an Ideal sure test? Thanks, Ken
Reply With Quote
  #6  
Old 4/2/09, 4:40 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Load side/reverse polarity?

Quote:
Originally Posted by kmalone View Post
Can this be detected with a simple 3 light testor or do you need an Ideal sure test? Thanks, Ken
It can be detected simply by pushing the GFCI test button. On an older GFCI, if it remains powered when tripped, line/load is reversed, or it is defective. On a newer GFCI, it will not function at all if line/load is reversed.
Reply With Quote
  #7  
Old 4/2/09, 5:38 PM
Kenneth R. Malone Kenneth R. Malone is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Sycamore, IL
Posts: 70
Default Re: Load side/reverse polarity?

Thanks guys...
Reply With Quote
  #8  
Old 4/4/09, 2:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Load side/reverse polarity?

Also lets not all forget to mention to our clients to test these GFCI devices on a monthly basis. Some older ones do fail in the closed position which creates a hazard they the consumer may not be aware of. I believe all GFCI devices produced after 2003-2004 UL 943 corrected this problem. However, their are still alot of the old ones still out their...some with SHOT MOV's as well and offer no functional protection at all.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
cut floor joice John E. Gibson, #2 General Inspection Discussion 16 9/25/08 9:45 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM


All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts