Default Location of main breaker in panel

Gentlemen,
At today's inspection I found a 100 amp Siemens main panel. I normally find the 100 amp main breaker located at the upper right-hand position. See the photograph that shows the main breaker has been mounted two positions lower than the top position. A single pole 20 amp breaker and an exposed opening exist where I normally find the main breaker. Is there an issue placing the main breaker in a location other than the top right. Thank you for your opinions
Attached Thumbnails
location-main-breaker-panel-img_0082.jpg   location-main-breaker-panel-img_0083.jpg   location-main-breaker-panel-img_0081.jpg  





Mark Raumikaitis, CMI, NH Lic #133
HomeCheck Professional Home Inspections LLC
Derry, NH
603-432-3211
Inspecting New Hampshire and Southern Maine
http://homecheckhomeinspections.com/

"Always think long term, do not be influenced by short term thinking or rewards."
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/12/13, 2:58 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,089
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Location of main breaker in panel

Since the panel cover is factory marked MAIN, IMO the CB shall occupy the top two slots. It also requires a screw or clip to hold it in place since it's back-fed.
Reply With Quote
  #3  
Old 1/12/13, 9:49 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,467
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Location of main breaker in panel

I agree with Robert.
Reply With Quote
  #4  
Old 1/12/13, 10:29 PM
ROBERT YOUNG, CMI's Avatar
ROBERT YOUNG, CMI ROBERT YOUNG, CMI is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal Quebec H4B2R8
Posts: 10,238
Send a message via Yahoo to ryoung7
Default Re: Location of main breaker in panel

Does the main breaker CB close the service or all breaker below it?
1) Was it an auxiliary panel?
2) The conductors look small for a 20 amp breaker IMO. 12 AWG is required.
Any photos further back?



Robert Young's Montreal Home Inspection Services Inc.
Home inspector Montreal - Montreal Home Inspector
"Putting information where you need it most, "in your hands!"
montreal-home-inspection-services.com
Reply With Quote
  #5  
Old 1/12/13, 10:40 PM
Mark Raumikaitis Mark Raumikaitis is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Fremont, NH
Posts: 459
Default Re: Location of main breaker in panel

Robert,
This a main panel not a sub panel
Breaker interrupts power to entire panel
20 amp breaker has #12...see the yellow insulation if you follow the wire





Mark Raumikaitis, CMI, NH Lic #133
HomeCheck Professional Home Inspections LLC
Derry, NH
603-432-3211
Inspecting New Hampshire and Southern Maine
http://homecheckhomeinspections.com/

"Always think long term, do not be influenced by short term thinking or rewards."
Reply With Quote
  #6  
Old 1/13/13, 1:14 AM
ROBERT YOUNG, CMI's Avatar
ROBERT YOUNG, CMI ROBERT YOUNG, CMI is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal Quebec H4B2R8
Posts: 10,238
Send a message via Yahoo to ryoung7
Default Re: Location of main breaker in panel

I have seen this before. Rightly or wrong I only wrote up what I could identify. You have an open knock out. I will also state that I would calibrate or measure the AWG. It look 14. Color means nothing to me after awhile. There is a thread, I forget where it is that has the neutral missing and most of the wiring is backwards. I think Chuck's thread.
Did you read the legend and go the the code for reference?
Here's something of interest.
Double Pole Service Disconnect The main breaker should be at the closest point to the service connection.

A panel can be installed top up or upside down. As long as the main CB or disconnect is nearest the connection on the bus.
So where is the top of the panel and the bottom.



Robert Young's Montreal Home Inspection Services Inc.
Home inspector Montreal - Montreal Home Inspector
"Putting information where you need it most, "in your hands!"
montreal-home-inspection-services.com
Reply With Quote
  #7  
Old 1/13/13, 12:53 PM
Chad Norlen, CPI's Avatar
Chad Norlen, CPI Chad Norlen, CPI is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: American Falls, ID
Posts: 351
Default Re: Location of main breaker in panel

Did you get a shot of the remaider of the label? I couldn't find the same label online, but this one indicates exactly where the backfed main breaker is to be located.



Chad Norlen

HVAC Journeyman - State of Idaho
EPA Certified Universal Technician
Reply With Quote
  #8  
Old 1/13/13, 12:59 PM
Mark Raumikaitis Mark Raumikaitis is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Fremont, NH
Posts: 459
Default Re: Location of main breaker in panel

Chad, Thank you for the diagram. I finished the report this morning and wrote it up as being in the incorrect position and recommended an electrician. I appreciate your research.





Mark Raumikaitis, CMI, NH Lic #133
HomeCheck Professional Home Inspections LLC
Derry, NH
603-432-3211
Inspecting New Hampshire and Southern Maine
http://homecheckhomeinspections.com/

"Always think long term, do not be influenced by short term thinking or rewards."
Reply With Quote
  #9  
Old 2/9/13, 7:01 PM
Thomas Hession's Avatar
Thomas Hession Thomas Hession is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: Pinellas Park, Fl.
Posts: 1,346
Default Re: Location of main breaker in panel

I believe this is related to this post...can someone explain it in slower terms.

Thanx in advance
Attached Thumbnails
location-main-breaker-panel-gedc0010.jpg  



Tom Hession
HHH Home Inspection Services LLC
Pinellas Park, Fl.
312-371-5076
http://www.inspectorpages.com/thession
http://www.pinellasinspector.com/
http://www.hhhhomeinspections@gmail.com

Home, Health, Happiness
Reply With Quote
  #10  
Old 2/9/13, 9:36 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,089
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Location of main breaker in panel

Thomas,
from the photo it appears that the panel was originally MLO or main lug only and they simply added a back-fed breaker (top left) as the MIAN. The back-fed CB requires a clip, bolt or some other device to keep it in place.
Reply With Quote
  #11  
Old 2/10/13, 8:17 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,467
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Location of main breaker in panel

I agree with Robert.
Reply With Quote
  #12  
Old 2/11/13, 10:14 AM
Thomas Hession's Avatar
Thomas Hession Thomas Hession is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: Pinellas Park, Fl.
Posts: 1,346
Default Re: Location of main breaker in panel

The clip is to prevent accidental removal....Yes

Anybody care to share a narrative.

Thanx in advance

Tom



Tom Hession
HHH Home Inspection Services LLC
Pinellas Park, Fl.
312-371-5076
http://www.inspectorpages.com/thession
http://www.pinellasinspector.com/
http://www.hhhhomeinspections@gmail.com

Home, Health, Happiness
Reply With Quote
  #13  
Old 2/11/13, 10:28 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,467
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Location of main breaker in panel

Tom, what do you think needs to be written up? The panel has a main breaker.
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/11/13, 11:27 AM
Thomas Hession's Avatar
Thomas Hession Thomas Hession is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: Pinellas Park, Fl.
Posts: 1,346
Default Re: Location of main breaker in panel

Needs clip....am i missing something. I said slowly.



Tom Hession
HHH Home Inspection Services LLC
Pinellas Park, Fl.
312-371-5076
http://www.inspectorpages.com/thession
http://www.pinellasinspector.com/
http://www.hhhhomeinspections@gmail.com

Home, Health, Happiness
Reply With Quote
  #15  
Old 2/11/13, 3:06 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,467
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Location of main breaker in panel

Not an HI, but if missing the hold down how about something like the required breaker holddown or breaker retention device is missing and should be installed.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel in Bathroom ederousse General Inspection Discussion 39 6/12/12 5:53 AM
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM

All times are GMT -4. The time now is 5:58 PM.
no new posts